Re: A2W heat pump as primer for 4 bank hydrothermo ( 864,000 btu )
Thank you. It wouldn't surprise me that the heating system is oversized. Why would someone spend extra time to properly size a system and make less money off the deal. Throw 4x the gear at the solution, never have a not enough heat call back and make 4x the markup.
I'll review the heat loss article. The building is going to be modeled in CAD soon so I might be able to leverage that and throw it into LoopCAD and do the heat loss calculations there without too much work.
At this stage I'd just like a quick easy win. Throw something residential in for pre-heating if possible and save 10% pay back in 10-20 years is fine. Eventually the boiler needs replacement and it looks like high efficiency gas is likely to be the best choice given the heat loads. I had one quote just for the boiler of $52,000 and that is without installation. We'll likely run to failure for the existing heat plant - really I think until one of the 4 units dies I won't be serious about putting the work in to figure out a replacement plan. Yearly gas bill is ~$26,000.
My napkin numbers.
Going from the 80% to a 96% ( assume you only get 90% ) would save $2000 a year ( some of that gas is for the domestic ). $52k for the boiler assume optimistically $26k for install? would be a 39 year pay back which is too long. I like mechanicals but right now seems like doing things to decrease heat loss are going to be the biggest bang for buck.
Re: DIY Boiler Monitor Project -- Useful?
Great info! Clever data collection methods
6 minute run times are fairly short. Probably mild season loads?
With run time and off time.
6 minutes on, 11 minutes off, total elapsed time= 17 minutes
6/17= .352 run fraction 35.2%
So running about 80% cycle efficiency
I'd like to see the return up around 140F at shutdown. If you could get a CO2 reading you could determine if the boiler is still condensing when it shuts off. Or the flue is still sweating?
\
With a cast boiler you might bump the min. on the tekmar. Are you using a return sensor? You are limited on reset temperatures with a cast boiler might not do a wide reset with a cast boiler
Graphs from Modern Hydronic Heating & Cooling 4th edition
hot_rod
Re: To switch or not to propane
Thanks guys! All are leading me to put tank outside, tho the area is narrow. Will get quotes.
Re: In imminent danger of house freezing (Minnesota) - solutions?
Where in MN is this located, and why is a rental home sitting vacant? Would getting the heat on allow you to fill the vacancy and bring income in to cover the cost of the new system? Winterization is going to be the best option financially if it'll be unoccupied all winter anyway, but a simple boiler swap isn't a crazy expense and perhaps a small personal or equity loan would get you back going quickly…
Re: DIY Boiler Monitor Project -- Useful?
Here is something that will surely increase your journey of learning hydronic heating.
Look up the book or booklet by Bell & Gossett titled "Zoning Made Easy."
This book, in my humble opinion, is the best explanation of hydronics. It covers pretty much all of the bases and was written by the founder of this website @DanHolohan long before websites or personal computers were a thing.
I used this book when I was a Vocational Education Instructor years ago, and it was very well received as an addition to the curriculum. I still use it today as a reference guide. So, check it out. I'm sure you will be as pleased as I am. The book is excellent. Not to mention the many books offered on this website.
Intplm.
Re: New jersey BFP required without feeder?
it comes down to how the inspector classifies boiler water. If it is filled with potable water, no chemicals, that could be considered low hazard. The ASSE 1024 is for low hazard applications.
Mainly the inspector would be concerned about someone adding a cleaner or chemicals down the road.
Then a BFD with a higher hazard level might apply. Either a vented dual check, or an RPZ with test ports.
Lot of interpretation in accepting BFDs by AHJs. It is rare to see a code book site a specific BFD number.
hot_rod
Re: Heat exchanger between wood boiler and propane boiler?
Plate type HX are more efficient and less $$ compared to shell and tube.
More size availability also.
I could suggest some simple union fitting options to get to copper, pex or threaded pipe. Plate HX usually have nipples with a nice flat surface to take a fiber washer and union nut.
hot_rod
Re: A2W heat pump as primer for 4 bank hydrothermo ( 864,000 btu )
Assumption is that COP of 4 would mean 50% cost of the BTU from heat pump.
Swapping 864,000 BTUs over to an a2w heat pump would require more land space, more money and more electricity than the building currently has available. Ideally we'd start with something and see how it goes before 100% committing. Too often projects are contemplated in an all or nothing scenario resulting in nothing.
We have our domestic preheating with 3 HPWTs before final heating with a gas hot water tank. The proterra units are each 4200 BTU. The gas hwt is 385,000 BTU. While the HPWTs aren't providing a huge portion of the hot water it did enable us to reduce from 2x 385,000 BTU tanks to one and leave the redundant one as backup. The setup likely was overkill to start with but the hybrid solution has saved ~10% off the overall gas bill with minimal impact on the electric side.
In order to justify the project I'd want to see making the money for the installation back in 10-15 years (ignoring interest). I can't see a full swap ever paying back so a full swap point could only happen once the current hydrotherm hits end of life. 1985 cast iron - it might be around for another 25 years? The heat pump tech is still in flux so it is nice to start small and realize the improvements in the technology rather than bleed out on the cutting edge.
The HPWTs are an easy win as they are used year round whereas the boiler is only used Oct-April and I think the heat pumps will generally have a hard time heating water at 127F a lot higher before the boiler while maintaining a high COP.
My sense is that given the project requirements a heat pump can't work for this application but I thought I'd post and get a sense from the experts. Can assume 46F+ as air temperature during the majority of the heating season.
Re: In imminent danger of house freezing (Minnesota) - solutions?
Chances are the right guy could get it running. Sounds like the "TECH" that looked at it couldn't be bothered