Best Of
Re: My SteamPunk boiler
If you lost a gallon of water from vents etc during an extremely mild month, I'd start working on that as it's likely why your boiler rotted out.
Obviously weather is different all over, but I haven't added water since last March or so.
ChrisJ
Re: Question about ek1 wood boiler to dhw
Thank you for your question @masonnewb, and for your posts, @hot_rod .
Here is a drawing indicating how we would recommend wood boiler piping and wiring for a heating professional.
Roger
Roger
Re: Grateful for help recovering from rash changes to steam vent orifices!
After making sure main venting is sufficient I would start out thinking generally 4's for first floor, 5's for second and 6's for 3rd. Modify this by radiator size (and distance from main supply riser) such that small radiators on third floor drop to a 5, large or small radiators on second floor raise or lower to 6 and 4 and larger radiators on 1st floor bump up to 5's. This would be the starting point. Tune further with patience based upon room comfort level. In your own livable space on the third floor you could use adjustable valves like a Hoffman 1a to help your balancing. If using MoM vents you can also get a pack of orifices which essentially makes them adjustable.
Re: Issues with steam system after work completed
That plumber has absolutely no idea what he is doing. I'm sorry — really — that you are a few grand into the job, but don't even think abut trying to go on with him. There's an old saying: when you find yourself in a hole, stop digging.
It's a little hard to say from the description just what got messed up — but that wet return was essential to the operation of the system. I wonder where the water is going now…
And no, there is nothing you can add to the boiler to fix the problem.
All four of the guys mentioned above are known to me, and are dead honest and do quality work.
Re: Lwco shuts off when boiler overfilled?
Totally agree. And it is surprising how "little" overfill will do this. In many installations the pressure switch and the LWCO (and maybe other safeties) will be wired all in series (there are other way to do this, but this is very common indeed). So — I'd say everything worked the way it was supposed to work.
Re: What the heck is this? This
Unusual to see that on 1 pipe steam. Don't know how that would work. Several companies make pumping traps. Most of the larger trap manufacturers make pumping traps. $$$$.
Its only function is to pump condensate back to the boiler
Re: steam radiators are hissing loudly and spraying hot water/steam
Some pictures of the problematic vents ?
The actual water looks clean to me, the bottom 1/3 of the sight glass. The other junk upper 2/3 (probably rust) may have been there for a long time and accumulated over time. So when the boiler is boiling the water in the sight glass only deviates about 5mm or 0.2 inch and no other violent level changes.
The pigtail should be verified that it is not blocked.
Does the gauge ever move when " hissing very loudly and some are letting out so much steam that the room feels like a sauna "
Skim port if you choose to do a bit of skimming to see if there is any residual oil is still in the system.
Looks like a Hartford loop to me.
Re: steam radiators are hissing loudly and spraying hot water/steam
sediment would sink, i'm pretty sure that is oil in the sight glass which will cause surging which will throw liquid water in to the system which can get pushed out the vents. if the water bounces around while it is steaming we can tell you how to skim it to get rid of what i really think is oil.
the hissing may be bad or missing or severely undersized main vents
since it is cycling when you play with the pressuretrol settings I don't think the pigtail is clogged.
Re: DOE Heating Capacity Maximum
And in the situation here, you can see that the Megasteam MS288 has more than enough capacity (288 square feet vs. your 250) without doing any math at all — just reading the label…





