Re: New Steam Boiler Installed, Water Hammer, Prematurely Turns Off, Frustrated
Sorry to say but if they based the sizing off the old boiler that is probably wrong
Need more pictures of the piping up and around the boiler from about 10' away. Something tells me the piping isn't right.
The steam pressure should stop the boiler on a pressure rise at 1 1/2psi certainly not over 2 psi. The cut in should be as low as you can get it.
Re: Before you swap a component
Service techs in most cases will not clean contacts. You pay for a service call. If they clean contacts and get a call back who pays for the second call?
If you're working on your own equipment that is fine, but contractors will usually not want to do that and will replace the control if it is a simple swap.
Probably the most important issue is to make sure the controls are selected properly so the relays etc have ample capacity for the load they control.
Re: Residential boiler cycling again. House cold.
Don't worry about that. It's piped the way it's piped, and you can make it work the way it is.
The bypass is there to prevent too-cold water from returning to the boiler, which could cause thermal shock to the cast iron and risk cracking it (which almost never happens anymore) or could cool the boiler's exhaust gas too much, causing water vapor to condense in the exhaust stream, which can corrode the inside of the boiler.
So the mfr typically requires a bypass valve which returns some of the hot supply water back to the boiler, raising the temp of the return water.
I have two boilers where the mfr also required a bypass, but none was installed, and 30 years later the boilers are still fine. So the necessity for a bypass in some situations is debatable. The good news is that your installer did what the mfr required and installed one.
By closing the bypass valve, you force all the hot supply water to go out to your radiators, where you want it. And since your supply water is already getting fairly hot, it will still be fairly hot when it returns. I'm not an expert, but I think the rule of thumb is that as long as the return water temp gets up to 130 within 10 minutes of the boiler starting from cold, that's fine. My two boilers take even longer to reach 130 return (like 30 minutes) and as I said, they're still fine after 30 years.
To answer your question about the 0 psi, when the boiler gauge shows 0 psi, the boiler and all your pipes and radiators will still be full of water. The only thing that will have lost water is the expansion tank, because as you drain the boiler down, water from the pressurized expansion tank will be forced into the boiler to replace the water you drain, so the boiler and all the pipes and radiators will remain full. So by opening the boiler drain valve, you're actually draining the expansion tank, which is the ultimate goal.
Just follow Ed's instructions and all will be well. 😊

Re: Furnace playing games
" Im led to believe if my power goes out, upon turning back on, the R7284U will have to be reset manually. "
How or where was this inferred ?
Re: Cleaned out my sooted up boiler.
find a service provider you can trust.
your going to need one sooner or later!

Re: Cleaned out my sooted up boiler.
Based on what I've learned from being on this site for awhile and as a fellow homeowner, I think you want to figure out why it got sooted up like that.
Re: Cleaned out my sooted up boiler.
looks good is not troubleshooting
You need a combination analysis to tell!

Re: Steam Mains Insulate or not?
I am in the final stages of modification of my Coop steam system: Master venting, Fast venting and designing a boiler controller. The last thing that I am in the process of doing is insulating the mains wet returns and lower level [1st and 2nd floor in a 5 story building] risers. This will help achieve a better balance of heat. There are two apartments that have no radiators, they were all removed. These risers give off a good amount of heat in a room. Insulation in all cases [risers and mains] makes a big difference in steam transmission.
Re: Residential boiler cycling again. House cold.
I'm not a heating pro, just a homeowner/mechanical engineer with a similar expansion tank setup that had air management problems that I was able to fix after learning a lot from the helpful heating pros here.
No doubt they will have good advice for you. Meanwhile, I see a few obvious things:
- Boiler pressure gauge reads 30 psi at 140 degrees. Most residential boiler pressure relief valves are set to relieve at 30 psi, so you are perilously close to popping the relief if that gauge is correct. If your system was set up correctly, it shouldn't be above 20 psi or so at that temperature.
- You expansion tank setup is going to allow dissolved air to migrate from the tank back into the circulating water, where it will end up in your radiators and require regular bleeding. This can be fixed by replumbing the expansion tank with an Airtrol fitting, but that may not be your priority right now.
- If the 30 psi gauge is correct, it also means that your tank is probably waterlogged, ie too much water and not enough free volume left for the water to expand into. This can be remedied by draining some water out of the tank to free up more volume for expansion, but it does take a few specific steps to do correctly.
- The ease with which air from the expansion tank can migrate back into the circulating water, plus the apparent water-logging of the tank, all suggest air management problems that may be interfering with circulation.
Even if it turns out that the root cause of your problem is something else, your expansion tank/air management system could be improved if you want to not have to bleed your radiators regularly.

Re: Way overfired boiler
That is still a Vapor system, because the pipes were sized to operate at a few ounces pressure.
The Return Trap (where you added the sight glass) is actually a pressure-powered pump that operated when the boiler pressure got too high for the water to return by gravity. See chapter 15 of @DanHolohan 's excellent book "The Lost Art of Steam Heating" for a detailed explanation of this.
First thing to do is put the Vaporstat on. Then increase your venting. How long are your steam mains, and what pipe size?