Best Of
Re: Now ya see why PVC on mod con flue is not a good idea
You can armchair quarterback your opinions and guesses as to the failure but without lab analysis you are still just grasping at straws. Was it installed per the mfrs. listed instructions as well as those of the PVC pipe mfr, the primer and the solvent cement? Was the pipe used within the approved applications by the pipe mfr? Was the pipe properly supported? Was it leak tested prior to use? Was the appliance inspected and tested including gas pressures, orifices, firing rate, MUA, intake air obstructions/ sizing/ pressures? Flue gas outlet temperatures? Any signs of overfiring in the unit or historical evidence such as tripped safeties? Was the heat exchanger ever replaced? Lot's of questions in a forensic investigation.
I don't like PVC for a number of reasons: The pipes out there were never listed for this use but specifically forbidden per most pipe mfrs. While the pipe itself might withstand short term temps upwards 170F, the solvent cement routinely fails at 140F or lower. I've never seen an HVAC tech properly cut, chamfer, deburr or join PVC for venting. Never. I see pipe cut with a Sawzall held with one hand and the pipe with the other. The end of the pipe resembles a hole saw with all its jagged edges. The end is never chamfered nor deburred and there is no way to tell externally once the joint is made. Meanwhile, inside, the rough joint plows the cement pushing a dam of it ahead while scraping cement from the outer walls. The result is a very weak, often leaky joint.
The pipe mfrs. expressly FORBID pressure testing with gas, such as done with gas piping. You can do a low pressure water test but how are you going to test the seal on a flush wall termination like a Bayvent? You would have to test with the pipe extended, tested, cut to length and attach AFTER the test. You might be able to rig a test ball in some cases. Also, on long runs through crawlspaces, you may get a few drips that harbinger a future failure yet not manifest during the test duration. You have to rely on one end of the pipe or another just as with gas pipe testing. That brings in the gauge resolution, test duration and allowable leakage. It has to be reasonable yet reflective of the conditions.
The UL 1738 test seems fairly reasonable and reliable. It is also repeatable.
Everything made by man can and will eventually fail. It's just a matter of when and at what cost.
Re: Now ya see why PVC on mod con flue is not a good idea
I am a bit curious on how you came to that conclusion. How can you know if it bottomed out or not by looking at the two photos? You certainly cannot judge this by the length of the primer.
Re: Torque Wrench
We had a rash of electric unit heaters burn up the terminals on the disconnects and/or contactors. I ended up getting a torque screwdriver for the replacements, no issues since then.
I wouldn't say I'm a true believer just yet, but the evidence is mounting so I use it when I can.
Re: Need help choosing between Comforto (Granby) and ThermoPride oil furnace
I don't know about Conforto. Thermopride is generally considered to be the best and most expensive oil furnace.
Your old one lasted 36 years that is a good run for an oil furnace. General rule of thumb is 20 years. You generally want as much return air as you can get it should not be restricted.
Re: J.P. Ward
The numbers just don't work to build factories in the US. Currently the labor department estimates 400,000 unfilled factory jobs in the US. They are looking for the same people as all the trades. Looks like we may be going in the wrong direction with entry level job workers these days. Farm workers, factory workers, construction labor, hospitality and food processors are leaving by the bus loads. A shiney new factory with no workers doesn't help much.
Modern factories to be accurate, fast and competitive will be automated. 65% of those jobs will require a degree. These are not low pay entry level jobs and wages. As such the cost of the product needs to cover those wages.
With a new pickup built in Mexico costing upwards 100 grand what would a truck 100% sourced and built in America cost?
Factory jobs, just like trade jobs, and farm jobs have a stigma of low wages, long hours, dirty, possibly unsafe conditions, etc. A major PR issue like our trade. How many people do you know applying for a factory job? Money motivates American workers these days, for the most part.
Farm land and factories are still being gobbled up by foreign investor group.
Uncertainty around tariffs, their %.
Raw material, partial assemblies will still come from across the globe, as the average US built car is 45% imported components.
Not a lot of discussion on how to over-come these obstacles?
There will be a lot of lip service and promises by manufacturers to build US factories, once they run the numbers on the costs involved to build a widget, even if the tax payers cover the cost of the factory build, in the US, not enough consumers are buyers. The stall is on.
China with its 1.4 billion people, a huge, low cost labor pool, started planing in the 1970s to become the worlds tool box and manufacturing powerhouse. They started with massive infrastructure investments.
Around here we barely have enough power to keep residential AC running on a hot day. Interstate grid lock every day. What happened to the 2018 focus on infrastructure improvements?
It starts with a realistic vision, then a pathway to get there. Our leaders, whichever party, just pinball from one problem to the next on a daily basis. Flavor of the day, what makes the headlines.
It would be nice to think someone, enough of us, are working in the background to get er done??
hot_rod
Re: Oil to propane, Kingston NY area - EDITED.
But, how many people actually get proper maintenance done?
It's the same basic principle that makes me favor probe-type low-water cutoffs on steam boilers as opposed to float-type. Folks tend to forget to blow the float-type ones down. Yes, probe units do need to be checked annually, but annually is not weekly.
ISTR @Mark Eatherton once ran a mod-con without maintaining it, just to see what would happen. Its efficiency dropped noticeably. I've forgotten how much, it's been quite a while.
Re: Oil to propane, Kingston NY area - EDITED.
I certainly have not forgotten. In fact, I support the decision to use CI due to the complexity of the mod-cons and the inability to find proper parts and service personnel.
I simply wish to prevent anyone from comparing a 92% mod-con to a 84% CI. This is not a fair comparison.
There are degreed engineers on this site that are doing exactly that and they do a disservice to all people who come here seeking advise.
I also wish for you to note that the mod-con will consume 869 Therms for the season vs. 1140 Therms for the CI boiler for the season on a house that uses 80M BTU for the season.
Figure $2.50 per therm and the annual savings is $677.00. An argument can be easily made that the mod-con can be maintained PROPERLY for less than this value, and, if maintained, it can last more than 10 years.
Re: New Propane Boiler Options
Thank you for the article you posted, @Kaos , these are all good things to explore. The example in that article presents a scenario requiring room air dehumidification when it was 90°F outside; this is much different scenario than operating a heat pump water heater in cold climates when outside air is cold and dry.
The ASHRAE article I referenced indicates that heating discharge air from a heat pump water heater is a possible solution as the air impacting a surface can cool it down below the dew point. This is not easy without an external source of heat. Although the discharge is localized, it is informative to see the following analysis on the impact of a heat pump water heater on a room the size of an entire home:
"The best-case scenario for installation in an enclosed space would be a closet the size of an entire house. …The HPWH would be able to extract about 6.2 kBTU of heat from the air (5.3 kBTU sensible + 0.9 kBTU latent). This is not enough heat for a single heating cycle in a typical 3 to 4-person household of this size. Furthermore, cooling indoor surfaces down near 45ºF for more than an hour, multiple times a day, carries a high risk of moisture damage and mold in most climate zones. If the air mass in a 1,625 ft² room does not contain enough energy to heat the water, neither will the air in a smaller room."
Roger
Roger
Re: New Propane Boiler Options
@Kaos , the controls have to be designed to allow stratification of the tank so that continuous cold water make up feeds the plate heat exchanger. The entire system has to be designed properly or you end up with lower performance and the boiler finishes hot which wastes energy (as it does with a conventional indirect tank and combo/instantaneous systems).
Regarding heat pump water heaters, the article indicates this is a common problem that has to be solved before widespread use of heat pump water heaters. This makes sense because the rooms (and outside walls) are chilled as part of normal operation. This introduces a new mold and condensation problem in the outside walls that did not exist before the heat pump water heater was installed. The authors identified the following issues:
- Inadequate heating capacity compared to advertised specifications.
- Real-world efficiency significantly lower than rated efficiency.
- Moisture-related damage and mold growth.
And believe the issues generally track back to two primary causes:
- Insufficient access to the thermal resources inside the building.
- Improper handling of cold exhaust air.
Roger
Roger
Re: New Propane Boiler Options
@Kaos , you’re spot on about micro zoning - it will keep the boiler idling and waste energy.
But the most efficient state for a boiler is when it’s off, so the best design is thermal purge so no energy is wasted at the end of each cycle. Properly designed indirect tanks with plate heat exchangers and thermal purge will exceed the efficiency of combi boiler water heating. Last month's ASHRAE journal also had an article that highlighted why heat pump water heaters have major issues (water damage and mold in enclosed spaces of outside walls due to cold discharge air), they operate at outputs and efficiencies far below their ratings (the rooms cool off and drop performance as there is no external heat source to feed it). Further, Vermont has relatively “cheap” residential electricity ($0.225/kWh recently) compared to the rest of New England, but that’s still $6/gal propane and $9/gal fuel oil equivalent so the cost to operate the heat pump water heater is more even without including the effective impact of running a small air conditioner in your home in the winter. Most of the boiler country in the US does not have comparatively inexpensive Canadian electricity prices found in some provinces you reference.
Roger
Roger