Re: sunrad steam radiator close to boiler gurgles clicks & is annoying
You said it's not surging during operation and yet the level is dropping 3"? That is surging. Cue "Black Water" by the Doobie Brothers
The surging water might not be getting all the way up to the radiator, but the sound of it might be going there. It might only be surging up to the header (which it is a nice header, by the way)
Re: Steam Sizing Question.. what would you choose?
299,000 input and 285,000, are effectively the same boiler. We're talking about an approximate difference of 12,000 BTU output difference between the two boilers. On a system that size, that is negligible and will never be noticed. If you are comfortable with the 299, then you should be equally comfortable with the 285. IMO
Re: Drip drip . .
The drain valve should obviously be closed. The ball valve should be at least be half way open. It tempers the hot water entering the water heater.
HVACNUT
Re: Rehashing the old Williamson vs Weil McLain comparison, and new boiler specs
Agree, if indeed there is more vertical space and we would have to assume water of same purity shouldn't boil any more violently (vertical displacement) in a bigger boiler than a smaller one then this could be some of the explanation.
Re: Rehashing the old Williamson vs Weil McLain comparison, and new boiler specs
The closer the top of the water is to the steam tappings, the more likely it'll be to pull water up into them.
I could only guess the larger boilers have more distance between the top of the block and the normal water level.
ChrisJ
Re: sunrad steam radiator close to boiler gurgles clicks & is annoying
Check the piping for pitch. Maybe something changed with the boiler swap. Is the rad hooked up 1 pipe or two pipe?
Did they skim the boiler and is the water level steady while steaming?
Need more pics of the boiler piping.
Re: Can you please critique this boiler setup that was installed in my house two wks ago
5 section boiler calls for 2 2" risers or 1 3" riser. As others have mentioned its piped wrong but the fix is easy.
Remove the 2" riser that is between the building supply and the equalizer and cap the boiler and the tee.
Remove the other 2" riser and install a 3" riser. Easy to go back to the flange and make it a three elbow swing joint with 3 90s
Re: Can you please critique this boiler setup that was installed in my house two wks ago
and @EdTheHeaterMan even patched the hole in the boiler jacket!!
Re: Can you please critique this boiler setup that was installed in my house two wks ago
It says 2 weeks, no?
ChrisJ