Re: Lochinvar boiler isn’t keeping up
While the 40 may not be enough I don't believe the controls are set properly. If you set the controls right and keep the tank at 135-140 and mix it down and be a little more selective in your water, use you might get by.
Re: Can you please critique this boiler setup that was installed in my house two wks ago
It stinks (since you asked).
Re: Can you please critique this boiler setup that was installed in my house two wks ago
From the Peerless manual. Note the takeoff from the header needs to be after the two riser connections to the header:
Re: Lochinvar boiler isn’t keeping up
this indicates the boiler pump turns off on dhw call
If it is in zone mode a primary loop pump would also run
hot_rod
Re: Lochinvar boiler isn’t keeping up
The boiler needs to be sized to the biggest load. In todays energy efficient homes, the DHW ends up being the biggest load often
So knowing what a homeowners expectations are will help with tank selection.
If a tub is used frequently I suggest more storage capacity compared to a larger boiler able to give you 4 gpm or more
Tank temperature could be elevated and mixed down
Operation above 140 will shorten tank life and precipitate more minerals
What did you have for DHW in your previous home?
hot_rod
Re: Lochinvar boiler isn’t keeping up
the tub is 66x34 free standing tub. It’s approximately 45 gallons at 3/4 full. Now writing down those numbers and knowing how large my indirect tank is, my tank doesn’t seem large enough at all.
Re: Lochinvar boiler isn’t keeping up
i have a similar setup to theirs but with a 20,000 btu/hr larger boiler and i can run it out of hot water with a long, adequate shower all by myself. if they want to fill a big tub or use 2 or more showers at once their capacity is way too small. they would need a huge electric to do it with electric because of its essentially nonexistent recovery rate compared to their consumption. that boiler can recover an 80 gallon tank in less than half an hour. electric would take about 130 minutes to recover 80 gallons.
Re: Lochinvar boiler isn’t keeping up
it is usually better to size the boiler to the heating load and get the needed dhw capacity with bigger indirect tank(s). if you get the capacity through boiler sizing then the boiler won't have sufficient turndown to match the heating load when it isn't at design conditions which will be most of the time.
Re: Lochinvar boiler isn’t keeping up
Hi, Another option could be to add a 40 gallon (or bigger) tank in series with the existing 40 and pipe it so both are heated by the boiler. It could be a lower cost way of solving part of the problem. Still seems DHW priority isn't figured out yet.
Yours, Larry