Best Of
Re: Air in oil lines - potential tank relocation
Is that a flap check valve on the return line?? WHY???
It would be worthwhile to reroute a new single oil line and place it in the ceiling of the basement routing it to the boiler and then have the plumber install a tiger loop air purger in your delivery line near the burner.
I would seriously consider replacing the 2 pipe system with a one pipe system using a tiger loop ultra air purger and a new oil burner.
Re: Help me calculate pressure drop!
If I added it right you have roughly 60' of pipe. With 140000 btuu you should have 1" all the way, thats the way it would be if piped properly.
you have 6.0"wc now at the meter and the boiler needs 5.0". I don't know if increasing the last 6' of pipe will help but it should.
You should also be combustion testing the boiler if you playing with the gas pressure.
Why are you increasing the firing rate ? Does the boiler heat the house now?
Re: Bit the bullet: bought an HTP UFT-100W on ebay
Fair price IMO. I was paying about $1800 for a 100W in 2019 when I stopped using them but as long as you don't have all low temp radiant or need any tech support, they're a pretty good boiler. As was mentioned above, I'd probably just install one with unions and keep the second for parts/spare rather than a cascaded system but you're welcome to do as you please.
Re: Can someone explain this hydronic loop heating.
@Lid431, saddle valves? For real? Complete with 1/4" tubing for easy bleeding? 🤪
HVACNUT
Re: Replacing cast iron radiator with smaller one
A kickspace heater, or any heater with a fan may just spread the airborne lint further into the home.
If anything some UltraFin below.
hot_rod
Re: OT: Underground Wiring Options
If your not going to have a charger run the larger PVC pipe and pull #12 for the 20 amp breaker. The new owner can pull the charger circuit or the sub panel. Only install what you need but you have left provisions for an upgrade if needed.
A garage can only have 1 circuit or 1 multiwire branch circuit. More than that and you open yourself up to ground rods, sub panels and more unneeded cost and issues you don't need if your not using the increased power.
Re: Boiler wiring tips
Step 1 Understand the basic electrical circuit. Source > Control > Load > Return path to source
This is a basic electrical circuit.
- Source = two 1.5 volt batteries
- Load = light bulb
- Control = manual switch
- Return path to source
Note that the load and control can be reversed. The load can be on the Source side or the Return Path side of the circuit.
From that basic understanding of electricity, you can build any analog electrical control circuit to operate a boiler.
Re: Boiler wiring tips
Go very slowly and know when you need to bring in help. It takes years to get really good. Mad Dog



