Re: Snowmelt magician!
Call Therma-HEXX. The 11.5 “ wide hydronic ThermaPANEL was specifically designed for steps. It is capable of snowmelting 8” thick granite slabs, concrete, synthetic decking, Ipe, open grate systems, pedestal mounted surfaces and asphalt. The full size ThermaPANEL is used in everything from high rise ob decks, the North American Missile Defense System to driveways and interior radiant heating and cooling from the ceiling and floor. It is a very high output system.
www.therma-hexx.com
Re: Literature on Geothermal
"This is important, because our observations with my brother's field, a big 30x60 with 1800 feet of tubing in the 1800SF would cold soak pretty badly deep into the season. His soils were drier and less dense and not good conductors as @DCContrarian was talking about. We did not get much edge effect and that large contiguous field got below freezing by the end of the season."
Frozen soil is a much better insulator than unfrozen soil. If the soil freezes then the capacity of the field drops precipitously and it's pretty much game over.
Re: Radiant Floor Heating System – Is a 10°F Single Space - Same Zone Temperature Difference Acceptable?
Does the alcove probably has a high load? 3 outside walls? Lots of glass or doors that are low R-value.
Unless the alcove room can be doored off from the rest of the room, I don't see a 10° ambient being likely. Hot goes to cold, always. Unless there are some infiltration issues also?
The key number to check is floor surface temperature. , vs the load of that various areas. 2 btu/ sq ft for every degree difference between floor surface and ambient.
70° ambient with 80° surface= 20 btu/ sq ft. Oddly enough the cooler the air, the higher the floor output. So if the alcove is 60° and the floor 80 then 40 btu/ sq ft.
Plates over slab? How is that insulated below?
hot_rod
Re: Lochinvar burner cleaning
I not a big fan of either concentric exhaust or the cover with both pipes attached
I would like to see the vent out the roof, or the two pipes several feet apart if out the side wall
Your manual should have an entire chapter on venting procedures and locations
hot_rod
Re: 1966 heating oil tank
When you have a new tank installed, the sludge will be removed with the 59 year old tank. Then fresh fuel in the new tank. Nozzle, filter, strainer, combustion test, done. What the tank looks like on the outside is not what it looks like in the inside.
HVACNUT
Re: 1966 heating oil tank
You can get a plain steel tank like you have, or Granby sells a steel tank with a liner or you can get a Roth SS tank.
If it was mine and it shows no signs of leaking which your does not I would move the oil line into the top of the tank. Save up some money and make the switch in a year or two. Plan the install so the tank is below 1/4 full when you make the swap to make it easier. If you plan on staying in the house the longer warranty make sense although like most warrantys they look for ways not to pay