Re: Delay of boiler firing?
I usually put a strap-on aquastat on the outdoor boiler supply line and use it to interrupt the call to the gas boiler. As long as it senses that the outdoor boiler is hot, the gas won't fire. You may need a switching relay as well if you don't already have one- the gas boiler would not run the pump(s) without a thermostat call.
Re: Piped wrong
This looks like the installer of that boiler just copied the piping arrangement of the old coal boiler that was removed. Left riser to one main and the Right riser to the other main. And that may actually work for many years. I guessing without the equalizer, there is a check valve on the wet return somewhere.
But since you posted this in Chimneys and Flues, the first thing I looked at was the water heater and the gas boiler venting connection to the chimney. That looks fine too.
So they want a price for an replacement boiler without allowing you to calculate the radiation EDR? I would answer that TEXT with " A lot " but that could change when I do some calculations after the onsite inspection. Then it could change to "Reasonable". Let me know how you want me to proceed.
Re: heat pump manufacturers
Every compressor has a safe playing field. Installing guardrails (pressure switches) is a good thing. They are relatively trouble free and frequently alert to an issue before equipment damage occurs. They also protect the consumer from knuckleheads who fix every problem with a Freon jug.
That being said; I have no problem installing a straight AC without pressure switches on a tight budget.
I think the most insane thing a lot of manufacturers are doing, is using R454B when R32 is a readily availible option. The insanity blows my mind actually. 454B is a blend with a substantial glide. R32 is a straight blend and more efficient.
Re: Delay of boiler firing?
normally you'd pipe both boilers primary-secondary so the firing boiler would not heat the non-firing boiler.
Re: Delay of boiler firing?
This would work, but…
it strictly time. It doesn't know what the load is. It would be nice to work off temperature. Can you explain or show the wiring?
HVACNUT
Re: Delay of boiler firing?
Used oil, but if it's fuel oil or used oil, it's the same Beckett controls and gun so it doesn't matter.
The used oil works a bit different, but it's not important to this discussion.
nate379
Re: Am I crazy? Chimney company says you can reduce the flu.
there is also a table in the code that will say something similar to the table in the boiler instructions.
Re: Am I crazy? Chimney company says you can reduce the flu.
Don't know your location but in many areas "chimney sweeps" have to be licensed or certified or something.
I wouldn't get involved and it is good that you didn't recommend them.
It's the homeowner's issue and they should contact their building dept. I would go as far as sending the building dept the information, boiler size and input, chimney height etc and let them do their thing.
Maybe your state or location has a "consumer protection agency" that can help.
That chimney guy missed that day in school.
Re: Am I crazy? Chimney company says you can reduce the flu.
Even a 225K boiler needs a 7" diameter x 20' high vent. So, reducing from 8" to 7" might be OK but you have the right idea. That 5" is not going to work.
I would craft a letter with the statistics of the customer’s boiler and indicate that you do not believe that the 5" liner is adequate for the 225k input boiler (enclose the rating of the boiler) and send the letter by certified mail so you know that your customer received the letter. Give your recommendations in the letter and inform them not to operate the boiler until the problem is taken care of.
It should include statements like “I have made an inspection of this Make… Model number… Serial number… Boiler at this location and have determined that the carbon monoxide problem is a direct result of insufficient combustion air and/or inadequate venting. I recommend the customer have a competent chimney professional look at the venting system including the chimney and the combustion air requirements. After the work was completed by XYZ chimney company I was requested to inspect the problem again and discovered the work performed by that company has not solved the venting and combustion air problem . The 5“ chimney liner installed by XYZ Chimney company, may have actually worsened the problem."
You can also add that you said you are not a chimney man, you are a plumber and the venting system is not up to the specification that the plumber recommends, the manufacturer recommends, or the local authority having jurisdiction would approve.
"If you have any other problems with your heating system regarding carbon monoxide, please refer them to the XYZ chimney company, the local fire department, or the local authority having jurisdiction. As you can not create the needed venting and combustion air requirements within the job description of a plumber. You can only tell the other trades what the specifications and recommendations are for the equipment.” …Or something like that.