Oil to propane, Kingston NY area - EDITED.

Options
joea99
joea99 Member Posts: 107
edited June 27 in Gas Heating

I'm looking to convert/replace an oil hot water "boiler" (Burnham v8) with a propane unit.

I see my original text may not have been quite clear, so edits below:

The merits of oil vs propane aside, looking for input as to (efficient) reliable units and installers in my area. Cost, as always, is a consideration. Cost of the conversion/installation, not one fuel vs the other.

Not really inclined to approach any of the "Big Names" in the area as they are known to be quite pricey, compared to the more Mom and Pop shops. Charging for the privilege of a "service call" of quoting seems counterproductive. I've had some say they will come out, for the service fee, provide a quote, and deduct the fee if I go with their quote.

I'm inclined to believe "conversion" of existing unit (gun replacement) while cheapest up front, is very unlikely to be anywhere near as efficient as modern purpose built units.

I have an existing Takagi TK3 for domestic hot water.

I hope that helps.

«1

Comments

  • pecmsg
    pecmsg Member Posts: 6,246

    Unless you purchase a lot of LP Oil is generally cheaper.

    Mad Dog_2
  • joea99
    joea99 Member Posts: 107

    Fuel costs are not the deciding factor for me, as long as they are close. Also, I have to take into account the efficiency (90% or better for modern propane units), vs the 75% I have been able to get with the oil unit. The unit I have now was oversized and short cycles quite a lot.

    Already have propone on site for domestic HW and cooking.

  • Jamie Hall
    Jamie Hall Member Posts: 26,125

    It's your puppy on the fuel. Where I am, some 100 miles or so east of you, propane is two or three times as expensive as fuel oil, per BTU. Your mileage may vary, but do your math.

    Your Burnham V8 needs service if it's only putting out 75% by the instruments, by the way. It should be around 85%.

    The small shops can be very good. As always, the quality of the workmanship and stability of the shop for follow up service is what you are looking for.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    rick in Alaska
  • pecmsg
    pecmsg Member Posts: 6,246
    edited June 27

    put in the cost of oil and LP

    https://coalpail.com/fuel-comparison-calculator-home-heating

    LP at 95% and oil at 85.
    oil is cheaper!

  • HydronicMike
    HydronicMike Member Posts: 71

    ”Charging for the privilege of a service call…”?

    People should come out and do it for free? When you go to the doctor, you pay them basically a diagnostic fee. And usually you get a cursory look over, take some vitals and “I think it’s probably xxxx. Take this and if you don’t feel better in a week, come back” (and pay another diagnostic fee). Then they try something different, maybe send you for a test, you pay more. Then you get to see them again, and pay a fee, to get the results. And hopefully that solves your problem. A HVAC tech couldn’t get away with that, could they?

    A GOOD tech (emphasis on good) comes to you, with a vehicle they pay for, maintain and insure. With a full stock of tools and parts, they already paid for.

    Then they do a full diagnosis checking all the relative components and usually fix it then and there and they are done. And if called back, most won’t charge unless it’s a new problem.
    Modern oil done right almost always beats propane in price, reliability, and availability. You only get top efficiency if the equipment is sized properly, commissioned and condensing most of the time. Otherwise much less.

    EdTheHeaterMan
  • joea99
    joea99 Member Posts: 107

    TLDR.

    The "service call" in this case, is a fee for coming out to give me a quote, not to come out and actually perform some service.

    Do Contractors charge for quoting for a new Garage? Add on Bedroom? New roof?

    You want a shot at the business? And want to charge me for allowing you to quote?

    Thanks, but no thanks.

  • joea99
    joea99 Member Posts: 107

    Not when I put in realistic numbers for real world efficiency of my burner, expected efficiency of a modern gas unit, and the fuel cost in my area.

    Propane ends up cheaper.

    MaxMercyethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,128

    @joea99

    just realize you paying for quotes weather you know it or not. The ones that you think are doing it for free maybe do a half **** quote don't measure the radiation or do a heat loss so they oversize the equipment. Who pays ? You do with higher fuel costs and an oversized system. The ones that charge you may get the job right. You get what you pay for there is no free lunch. the person that is not charging you is just building his "lost time" into whatever jobs he gets so customers are still paying.

    A free quote is not necessarly a good quote or an accurate quote. if they find the job need more work because of an inadequate quote they will say its an unforseen thing and you pay the extra anyhow.

    HydronicMike
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,681
    edited June 27

    @HydronicMike has a good point there. However there are some larger companies that employ a salesman that works on a commission that often will provide a "Free Estimate" for new equipment. I was that salesman at one time for a few years working for a fuel dealer. If you wanted your heater fixed and you wanted a free estimate, I would show up for free and tell you how much you might spend on a replacement boiler or furnace. If you wanted me to tell you how much it would cost to fix the heater you had in your basement already, (even though I knew how) I was not properly dressed in my white shirt, tie and dress shoes… or equipped in my small salesman car with no tools or parts. So I would give you the free $X0,000.00 price for a new heater but your broken heater was still broken when I left.

    On the other hand, If you wanted a technician with all the training and a truck full of tools and parts to show up and fix your heater for under $1,000.00 because the nozzle was plugged, the you needed to pay for a service call. Then you would get the correct person for the job. They would have nozzles and filters and many other parts you might need.

    With my experience and if the customer was not being a PIA. I might suggest that the repairs will be worth the price of a service call to find out the cost, and you may even decide to have the technician do the repair while they are there, so you have heat tonight.

    The difference is the salesman gets paid a commission, and it there is no sale there is no pay. The technician on the other hand gets paid by the hour even if you tell him the repair is too expensive and ask him to leave without fixing the heater. So, if you want that guy to show up, you got to pay for his time along with all the time the support staff in the office gets paid for him to be able to get there.

    I used to call my minimum charge for showing up a "Diagnostic Fee". I'm gonna use really old pricing so not to break any "Discussing price" rules. My Diagnostic fee was $39.00. That minimum charge would get a fully insured technician with all his knowledge, training, and a truck full of tools and parts in front of your defective equipment. The would diagnose the problem and then fix it if it was a simple easy fix. If it needed parts or additional labor the tech would provicee a writen estimate for your approval befor any additional charge work was done. if you decided not to have the repairs completed, all you owe is the $39.00 and yopu get to keep the priced written report.

    That was pretty basic and most folks understood the rules. But every once in a while we would get the guy that called and said that he wasn't gonna need to pay for a diagnostic fee because he already diagnosed the problem and all he needed was a (Part XYZ) replaced.

    Screenshot 2025-06-27 at 5.51.52 PM.png

    I would use this old auto mechanic sign for inspiration: Then I told my customer service people that answered the phone to give the alternate price for the minimum charge to show up.

    If you don't want to pay the Diagnostic fee, then we have a Service truck house call that is $50.00 minimum charge, or you can come and pick up the service tech and drive him to your house for only $45.00 and save $5.00. Labor will be charged from the time the technician leaves the shop until you return them to the shop. You must also provide a paid lunch break and feed them when they are working on your equipment for more than 1.5 hours.

    If you wanted to save even more you can bring your heater to our shop and we will work on it for a minimum charge of $29.00 but you may need to leave it for a week or so, because all the technicians are on the road diagnosing and repairing other customer's problems.

    If the customer had a sense of humor, they usually elected to pay the $39.00 minimum charge. If the customer was just looking to cheat us out of our minimum fee then the call was usually terminated without scheduling the service visit.

    We usually got a return call after the customer found out the everyone else was charging a $50.00 minimum fee because the going service rate was $100.00/hr back then with a 1/2 hr minimum. At that time we used the $39.00 low ball number but charged a Flat Rate for repairs where the parts and labor were included in the cost of the repair. We marked up the parts and we had a higher than average labor rate, but no one ever knew it because we didn't post the labor rate. We just had a price book with flat rates for all the usual repairs. Our customers loved it because the price was quoted before the work was done so they were not worried how much the mystery repair bill might end up being at the end of the repair.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Steamhead
    Steamhead Member Posts: 17,879

    @joea99 , the efficiency of your current boiler is considerably lower than it should be. A possible reason is shown below:

    This one's a V-8, like yours:

    and

    I could go on, but you get the idea. These all tuned up at least 82% on the analyzer after being properly cleaned. The oil companies involved were not servicing them properly, if at all.

    We've since converted one of these to natural gas with a Carlin EZ-Gas burner.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,681

    @joea99. I recently had a bathroom remodel and the salesman from the contracting company showed up for free and said that the scope of the job was more involved than just a quick "Free Estimate" price like Bath Fitters™ or other nationally franchised over priced shower replacement companies might offer. I needed a complete tear out to the studs and rebuild with a shower that my wheelchair could roll into with no curb.

    The job would cost a minimum of $29,000.00 but in order for us to form an actual Quote with virtual imaging with renderings of all the walls fixtures and appliance. They could provide that comprehensive quote for $2,500.00 that will be applied to the total cost of the job. I agreed and gave them a check for $2,500.00

    If I didn't give them the $2,500.00 then they didn't need to spend hours selecting tile and wall colors and fixtures and other handicap accessible features. Then I would just need to go with some other less professional handyman where I needed to turn into the general contractor and bark out instructions on how they needed to do their job. I selected the professional job and the quote came out to $45,000.00 and the bathroom turned out perfect. Easy to get my wheelchair everywhere I needed to get in that bathroom

    I could have just had a replacement shower enclosure for 15,000 to 20,000 but the wheelchair would not fit everywhere. I might as well just do nothing if I was going to go that route.

    So there are contractors … especially general contractors that will provide you with an estimate for an addition to your home the will charge you for calculating the total cost of the addition. You wan a free estimate ther will use a ballpark using a price per square foot based on experience, but to get an engineer to draw up the blueprints and do the calculations, the will cost you big $$$ before you even get a price for the actual work.

    Or you can look for some old school ready to retire plumber to look over the job and quote you a price for his son to do it for him. They can compete with the One Hour, or Ben Franklin or Sparky national franchise when it comes to getting the equipment from the manufacturer's at low costs, and training classes for the workforce that will be walking on your carpets with shoe covers. As others have stated there is no free lunch.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,128
    edited June 27

    In the "wild west" of upstate NY who knows what you will get. I did some work in that area and was not impressed in the least. All the electrical i saw was terrible

  • joea99
    joea99 Member Posts: 107

    That's true, but paying for a quote is no guarantee of that either.

  • joea99
    joea99 Member Posts: 107

    Yes, good catch. That has bothered mw since it was installed. I've done all the work on it myself and just accepted that it was that way. But, if I don't opt to convert to propane, I will have someone, from this list probably, come out to have a go at it.

    How did the conversion work out? I was considering that for keeping costs down, but am a bit skeptical on the efficiency that could be obtained.

  • joea99
    joea99 Member Posts: 107

    I get that. I recently had a sunroom "kit" built for me and part of that deal was $3500 or so, design and engineering fee, full plans, "wet ink" stamps, ready to throw at the building inspector. Non refundable, if I chose not to have them build it, but I owned the plans.

    Seemed fair to me.

    EdTheHeaterMan
  • joea99
    joea99 Member Posts: 107

    There is that. One of the reasons I am asking here. I've had more than one unpleasant experience with a "contractor" that was suited to sweeping out barns. The link to contractors on this site shows them all to be 2 hours south of here, in the "Great Metro" area. Not practical I think.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,681

    Gas conversion burners are a good idea when there is natural gas available. With LP Gas, not so much but your area may be different than where I used to work in Southern NJ and the Greater Philadelphia area. If you purchase the fuel tank and you own it wether it is buried in your yard or above ground, you can shop the price for your LP Gas from one company to another. Just like you can shop for fuel oil dealers with the best deals. When you are using it just for cooking and DHW you probably didn't purchase your own tank so the LP Gas distributer owns your tank. that means that you can only get your gas form the company that owns the gas tank. Those companies charge a premium for filling that tank because you are actually paying a kind of rent to them for letting you use their tank. The rent is calculated in the higher LP gas per gallon price.

    If you are going to use that tank for the next yerar after you convert the heating to gas, you will need to use the higher price per gallon you are paying now for DHW and cooking. What is the number and what is the oil per gallon in your area, those prices will be on your latest metered delivery receipt. I have punched in some Kingston NY average prices numbers for today, but winter heating oil usually cost more in February then in June.

    The best part is the last number on the chart, I like to see how much it might cost Elon Musk to heat his home if he used 100 dollar bills to burn in his fireplace.

    This chart is from https://coalpail.com/fuel-comparison-calculator-home-heating where I have posted the current price of #2 heating oil burning in a Burnham boiler at about 83% efficiency, You should be able to get that form your Burnham. The LP gas in a new ModCon boiler at over 90% AFUE. and the Burnham with a Conversion burner installed. The cost per 100 million BTU of each fuel adjusted for the combustion efficiency leaves the LP Gas cost of operation higher than the oil burner operation in both cases.

    Screenshot 2025-06-27 at 8.38.59 PM.png

    To put things in prospective the average 3 bedroom in your area of NY State might use 100 million BTU of heating energy in about 1.5 winter seasons. To quote a recent auto advertisement: Your mileage may vary

    Oil can get as high as $5.99 per gallon in February, so try to purchase fuel in September, before the price jump and then again in December or early January. Try to refrain from purchasing in February if you can. You might be able to save if you get the boiler cleaned and the burner adjusted for optimum efficiency without making any soot or smoke number on the smoke spot test. Also installing a second 275 Gallon tank will help you purchase more fuel at lower cost to help you thru the most expensive fuel price season. I personally used a 550 Gallon tank and if I needed fuel in February, I purchased 100 Gallons, Once the price drops in April or May, I would top off the tank for the summer.

    I also repaired the Fuel Oil Dealer's heating and cooling equipment in his home and several rental properties. We had a deal, I would charge regular price for my service and he would charge regular price for fuel and we would barter the services rendered. It worked out great because I only had to pay cost for the full price services I did for him and he only paid cost for the full price oil he delivered. No one got cheated out of anything that way.

    You can bring up that calculator and put the real numbers you actually paid for LP Gas for the past year and Fuel Oil for the past year to see what is more cost effective based on what you actually paid.  

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Steamhead
    Steamhead Member Posts: 17,879

    Worked great. We've done a bunch of these and they match or sometimes exceed the numbers they got on oil.

    But you have to use the right burner. If a boiler was designed for a flame-retention oil burner, as yours is, the conversion burner must also be flame-retention. A Carlin EZ-Gas with the 9-slot diffuser head does well.

    Any burner must be tuned using a digital combustion analyzer. Anything less is guessing, which leads to inefficiency and possible safety issues.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • joea99
    joea99 Member Posts: 107

    Did you have to alter the exhaust flue and chimney? Or left as is? Seems like their overall fuel costs must have gone up significantly then?

  • Steamhead
    Steamhead Member Posts: 17,879

    The chimney and smoke pipe were working fine, but we had them inspected anyway. We did change the barometric to a double-swing type and added a blocked-flue safety switch, which Code requires.

    Since the cost per BTU of natural gas was lower than that of oil, and the boiler was clean, they saved money. I've forgotten the percentage though, it's been a while.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HydronicMike
    HydronicMike Member Posts: 71

    Ed when has oil ever got to $5.99? I’ve never seen it in almost 40 years in the Mid-Atlantic area.

  • hot_rod
    hot_rod Member Posts: 25,272

    Combustion efficiency is only part of the story. Cycle efficiency is an important number. The combustion could be 83% or higher and actual cycle efficiency dragging it down into the 70% range.

    Mod cons have a definitive edge as the can modulate to match an ever changing load, or micro zoning efficiency concerns.

    It takes some observation and calculation to get the cycle efficiency number. The run fraction is the number you want to record. How many minutes out of an elapsed time. Burner on for 10 minutes, off for 20, repeat over and over.

    Cycle efficiency would be the case for oil, LP or NG on a fixed firing non con boiler..

    10 minute run time is suggested minimum for a boiler to warm up,the combustion chamber and flue.

    This example shows an 86K input boiler, 60K design load.

    So in this case use 60% for oil on that Coalpail calculation.

    Oil boiler % efficiency.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • LRCCBJ
    LRCCBJ Member Posts: 1,043

    ^^^^^

    THIS

    Nobody gets 84% cycle efficiency on oil. NOBODY!

    THIS is why a mod-con can provide a fuel savings of 30%. It is constantly running at the require level to just MEET the heatloss of the building.

    Those that compare the combustion efficiency of a mod-con at, say, 92% with the combustion efficiency of a fixed output oil fired boiler at 84% and conclude that the mod-con will save them only 8% in fuel (as measured in BTU utilized for the season) are making a serious error!!

  • Steamhead
    Steamhead Member Posts: 17,879

    @LRCCBJ et al, don't forget that the mod-con might last 10 years or so, and parts availability has been an issue on older units. But a cast-iron boiler is good for at least 20 years, and we find many older examples that are still purring along, and parts availability is a non-issue. So it's a "pay-now-or-pay-later" scenario.

    What's in my house? Cast-iron.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Jamie Hall
    Jamie Hall Member Posts: 26,125

    How about we stop obsessing abut numerical efficiencies — which none of us can measure accurately, if at all, and worry about overall running and maintenance costs?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • joea99
    joea99 Member Posts: 107

    Mine short cycles a lot. 4 zones, which did not enter into discussions when I bought it. The "old timer" at the parts desk convinced my that "more is better, you don't want to be short on the coldest days".

    Never runs more than 5 minutes unless I am checking combustion.

  • Steamhead
    Steamhead Member Posts: 17,879

    @joea99 , what model V8? What burner is on it, and do you know what nozzle is in it?

    Is the aquastat relay on the boiler a HydroStat or AquaSmart? Post a pic if you're not sure………..

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • LRCCBJ
    LRCCBJ Member Posts: 1,043

    I certainly have not forgotten. In fact, I support the decision to use CI due to the complexity of the mod-cons and the inability to find proper parts and service personnel.

    I simply wish to prevent anyone from comparing a 92% mod-con to a 84% CI. This is not a fair comparison.

    There are degreed engineers on this site that are doing exactly that and they do a disservice to all people who come here seeking advise.

    I also wish for you to note that the mod-con will consume 869 Therms for the season vs. 1140 Therms for the CI boiler for the season on a house that uses 80M BTU for the season.

    Figure $2.50 per therm and the annual savings is $677.00. An argument can be easily made that the mod-con can be maintained PROPERLY for less than this value, and, if maintained, it can last more than 10 years.

    pecmsg
  • Steamhead
    Steamhead Member Posts: 17,879

    But, how many people actually get proper maintenance done?

    It's the same basic principle that makes me favor probe-type low-water cutoffs on steam boilers as opposed to float-type. Folks tend to forget to blow the float-type ones down. Yes, probe units do need to be checked annually, but annually is not weekly.

    ISTR @Mark Eatherton once ran a mod-con without maintaining it, just to see what would happen. Its efficiency dropped noticeably. I've forgotten how much, it's been quite a while.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    pecmsg
  • LRCCBJ
    LRCCBJ Member Posts: 1,043

    I would suspect about 15. :) That's the amount of mod-cons that should be sold per year. :)

  • joea99
    joea99 Member Posts: 107
    edited June 28

    Pictures attached. It does sometimes run for a while, as it is a "cold start" boiler, which perplexed the supplier when I complained that it did not maintain temperature in "standby". They got bought out by someone not long after that.

    Oh, forgot, Beckett AFG .85 B Delavan. It might be an A, I never remember till I look at the ones on the shelf.

    20250628_163531 (Medium).jpg 20250628_163829 (Medium).jpg 20250628_163844 (Medium).jpg
  • Steamhead
    Steamhead Member Posts: 17,879

    It's probably an 0.85 nozzle at 140 PSI. That would result in a firing rate of 1 GPH.

    The Beckett OEM Spec Guide specifies 60-degree nozzles for this model- some are hollow-cone (A) others solid (B). What nozzles do you have?

    Also that aquastat relay does not incorporate any energy-saving features such as a Beckett AquaSmart or Hydrolevel Hydrostat would have. If that were my boiler, I'd upgrade.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • joea99
    joea99 Member Posts: 107

    The pressure is set at 140. I checked it just last fall. I may have an 80 degree in there now, but have 60B's on the shelf. There was some difference of opinion on the angle.

    I was going to go lower on the firing rate, but, I think .85 is the lowest Beckett listed for that one.

    I'll check those aquastats.

  • joea99
    joea99 Member Posts: 107

    I looked over the blurbs on those aquastats, sounds reasonable, but are there real world data on realized savings?

  • HydronicMike
    HydronicMike Member Posts: 71
    edited June 28

    TLDR? in your case Too Lazy Didn’t Read? Funny you ask for advice then don’t read it. But you apparently did read it.

  • Steamhead
    Steamhead Member Posts: 17,879

    Beckett claims up to 20% for the AquaSmart:

    https://www.beckettcorp.com/product/aquasmart-120v-advanced-boiler-control-7610a/

    Hydrolevel doesn't claim a percentage, but here is their literature:

    https://hydrolevel.com/wp-content/uploads/2017/07/Fuel-Smart-HydroStat-Brochure-web.pdf

    To me, it just makes sense- if you don't need to get the boiler up to 180° to heat the house, why do so? Pretty much all new cast-iron boilers come with one of these controls.

    Since you have four zones, it is definitely possible for the boiler to heat up more than needed if only one zone calls. These controls would prevent that. And both can be upgraded to full outdoor reset if desired.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Kaos
    Kaos Member Posts: 668

    Another bit about the mythical 85% oil burner is the actual efficiency. Look at the post here of what the real efficiency is. Add on the bit above about cycling and the efficiency is way worst.

    A modcon with low return water temps will actually get you real mid 90's efficiency. Not hard to do if you have larger emitters and a good outdoor reset curve.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,681

    I was just using a statistic I found on the web for "Kingston county heating fuel prices". I'm not sure where the statistic was generated from but I can certainly understand it. Some fuel dealers sell fuel for higher prices than others. The price that the wholesaler charges plus the minimum margin on a given day may have topped off at something unreasonable but that dealer may not have purchased any wholesale fuel that day. But the bean counting mathematic nerd generates a price the gets posted as the recorded retail high price that day, maybe no one actually purchased fuel from them that day, the posting is still real. It could also be that someone ran out of oil on a Sunday and there was an extra charge added on for the Sunday special delivery. Another possibility, $4.899 per gallon plus the additional servicer fee to deliver on Sunday then send a service tech to prime the burner may have been all totaled up and then divided by the gallons delivered. That can easily be misinterpreted to be $5.99 per gallon.

    But I didn't verify that statistic from two other sources, so I guess i'm just not that good of a journalist. But… I never said I was a Journalist.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Jamie Hall
    Jamie Hall Member Posts: 26,125

    Fuel — of any kind — is more expensive in New York, but I wouldn't have thought it was that much more. Of course, I bulk buy (three properties, a total of 3,500 gallons). This year #2 was $3.09 per gallon in northwestern Connecticut (and it's a major dealer).

    The spot market, however, can be a lot higher… I've never seen it lower than bulk, though.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England