Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

Oil to propane, Kingston NY area - EDITED.

Options
2»

Comments

  • joea99
    joea99 Posts: 142
  • ethicalpaul
    ethicalpaul Posts: 9,076

    Sounds good. Propane atmospheric should blow oil out of the water, no?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • hot_rod
    hot_rod Posts: 28,708

    Mod cons can give you some indication of their running conditions. They will accumulate running hours and in some cases running hours at various modulation rate. If you have a way to measure or meter the fuel, the number crunching is not so hard. BTU meters are also available, and in some cases billing is done based on BTU meter calculations.

    Obviously any properly tuned or maintained boiler should run most efficiently. Mis-sizing and mis-applied boilers are probably more common that not. Or heatinghelp.com would not exist :)

    Least we forget the building envelop and occupants use has the most to do with fuel consumption.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream