heat loss from
living room 15565
bedroom 6065
kitchen 73510 -
the slanfin calculator gives what baseboard product should be put in each room
would this help knowing?0 -
No each rad manufactor has its own correction.0
-
thought i would put it out there
what can i do to help?
measure the radiators again?0 -
List the SF of each room. The heatloss for each room. We did this last year, and it seemed out of balance. I can't find that page.........yet. Many pages.0
-
i can figure out the square footage of each room, I have the slant fin right here0
-
Okay, and the heatloss.0
-
front hall 44 st 5496 heat loss
liv rm 266 sf 15565 hl0 -
Keep,it all in one post please.0
-
hall 24 sf 327 hl
dngrm 148.50 sf 6379 hl0 -
hall 24 sf 327 hl
mid hl 61.25 723 hl
masbed 156sf 6065 hl0 -
bath 42 sf 2353 hl
kitcn 231 sf 7351 hl0 -
sorry
office 99 sf 4266 hl
pr 25 sf 1271 hl
2 bed 121 sf 1360 hl
2nd floor
hall 63 sf 116 hl
bed 154 sf 6527 hl
kit 140 sf 5472 hl
bath 56 sf 2604 hl
dr 121 sf 3224 hl
livrm 192 sf 7499 hl0 -
anything else I can help with?0
-
by giving all the room sizes and loss, how will this help fining out how big of radiator I need for the living room?0
-
if this is going to cost me around 1,000 bucks, I can not afford it0
-
Probably double that if you want two of those nice vertical panels. Possibly half that if two commodity wall panels will do the job. In materials.0
-
I can not see myself spending 2 grand on radiators for that room0
-
what is commodity wall panels?0
-
We're not supposed to talk pricing here, but Myson publishes their list prices online and there are several retailers as well. The Select line (piped from the sides) is one of the least expensive options out there. The T6 line (piped from the bottom as are the Buderus rads and includes a TRV valve body) costs a little bit more. The vertical models are roughly twice as much.0
-
I am sorry, and I forgot when I was talking about prices.
Please forgive me.
I will look it up on the net, as your suggested.
Do I know what btus I am looking for? I imagine i need to know this, before looking at radiators
thanks
0 -
Mark,
A low tech solution would be to partially cover the radiators that are over performing. You could experiment by partially covering them with blankets.
There are limits to how far you can throttle down the flow in order to reduce output.
This might be a good solution for a guy with your carpentry skill set.
If needed, you could increase the water temps to get the living room up to temp.
Your posts would be easier to follow if you incorporated all your thoughts into one post. You can always edit the post if you need to add a detail.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
good morning carl
Hope you had a nice turkey day
all my radiators have valves, would it not be good, to close each of them a little, or would I be restricting flow to much?
would that hurt the efficiency of the system?0 -
There is nothing wrong with that approach, it just may not be enough. Those valves are not really designed for that so the sweet spot between too much flow and not enough flow may be difficult to find.
It sound like the reason the living room is under performing is that the rads are partially covered making the house imbalanced.
You options are:
Add radiation to living (expensive)
Reduce flow to other rooms (might work)
Partially cover other radiators .
Covering the radiators might be a simple as putting a plant shelf with an apron on top, reducing the convective flow.
I don't think you are under radiated as much as you are imbalanced (I am talking about the house . I am sure if you increased the boiler temps a bit the living would heat just fine, you would however be way too hot in the other rooms.
Carl
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Carl
This is the house i grew up in, the living room has always been the coldest room in the winter.
on the 1st floor, most of the radiators are behind a covering. except the bedroom and the office
Radiator boxes either my father made, or I made.
but the 2nd floor, none of the radiators boxed.
0 -
I did not know this.......about other radiators being boxed........0
-
-
Mark,
I would consider altering (making more holes) at some of the under performing rads and covering the over performing ones.
You could also add small computer fans to the radiator boxes in the living."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Carl
I have a small fan, larger than a computer fan behind the living room rads, and it is connected to an attic thermostat, so when the heat gets up there, the fan kicks in.
Since the water temp is much lower than before, I had too lower the thermostat temp
The living room is really the only bad room.
I have not been upstairs, but my tenant says it was comfortable, actually, last week, i saw his window open, and i saw $ coming out the window0 -
Are you able to confirm that you have adequate flow to the living room rads? What is the supply and return water temps to those radiators?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The valves are wide open on those radiators, i did not measure temps to them, unless the valves are broken and are in a semi closed position. The living room radiators are over the boiler room, they are the 1st radiators off the boiler.
to the touch, they are warm0 -
right now the circs are on medium, should i keep them that way, or increase them? and tweak the other radiators that are ideal temp0
-
Sorry Gordy, i didn't see your response until now
yes, most of the radiators are boxed on the 1st floor, the 2nd floor is not boxed at all.
2 radiators on the 1st floor are not boxed0 -
Mark I tried to correlate radiation to heat loss but some of your heat loss rooms are not labled according to what the room names for radiation are.0
-
-
Carl
I know that it's harder to give heat, with the covers on'
this is something that I should have said from the beginning
Gordy
I thought I got everything right, but it's possible I made a mistake, if you tell me wht rooms are in question, i will bring out the calculator again0 -
It is nearly impossible to compare the output of radiators mathematically based on surface area when some are covered with home made covers and some are not. You have thrown in a huge unknown.
I think it is down to trial and error..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
I understand now, but I didn't even think of it before, when I 1st showed up on this site.
Could it be possible, that the boiler will not heat my house properly at 0 degrees or minus 0?
I messed up, I totally see it now, I should have said something a long time ago0 -
Mark,
It is only a balancing issue. You have plenty of boiler to overcome the heat loss for the building. It is just difficult to calculate the difference in output with so many unknowns.
You can experiment with this by partially covering some of the rads and seeing how the balance changes."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
If it comes down to it not working with the boxes, I'll have to take them off0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements