What am I doing wrong
Comments
-
You might look at the Jaga radiators also. They have some with and "Enhanced Boost Feature" basically some small quiet muffin fans to force convection. They mount inside on top or under some of their rads and finned convectors. They dramatically increases output if you have space restrictions for adding rads.maybemark said:thanks kurt
how many btus should I be looking for?
Need to calculate the load carefully on a room like that, then get enough heat emitters to get the job done.
https://www.youtube.com/watch?v=gyZUkclqmYcBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I know I have the heat loss, i think i gave the radiator sizes to Gordy (I think), but why should he have kept them, I know i didn't
the heat loss on the living room is someplace above, I'll give it to you again
15,565 heat loss0 -
Living Room:
142.8 SF EDR. 21420 BTUS at 180* water
84.0 SF EDR 12600 BTUS
Hall
30 SF EDR 4500 BTUS
Dining RM
51 SF EDR 7650 BTUS
M.Bed
39 SF EDR 5850 BTUS
Bed 2
30 SF EDR 4500 BTUS
M.Bath
21 SF EDR 3150 BTUS
Kitchen
58.74 SF EDR 8811 BTUS
74.76 SF EDR 11214 BTUS Figured these at 20" tall
Office
48 SF EDR 7200 BTUS
Powder RM
17.5 SF EDR 2625 BTUS
2nd Floor
Kitchen
60 SF EDR 9000 BTUS
Bed 100.8 SF EDR 15120 BTUS
Dining
29.37 SF EDR 4405.5 BTUS
Living RM
60.62 SF EDR 9093 btus0 -
Might want to keep that with the boiler info Mark.0
-
Now do you have the heat loss yet? Put that with the boiler info to. You have double the radiation for the heat loss.0
-
Yes, if you have the heat loss calc for each of those rooms you can see how under-radiated the living room is compared with the other rooms. We can also get an ODR target temp for the house.0
-
Some where Kurt you did an Radiation to heat loss survey...........last year.0
-
I,seem to remember that it was not balanced obviously.0
-
-
May all the people that has helped me, and all the others that learned and read this post, hope all have a good turkey day
0 -
Your welcome Mark have some turkey, and relax. Just think if this rain were snow we would be up to almost 2' ,0
-
Gordy
No plans for me today, except icing my knee.
It rained early this morning, but not raining now
Eat some extra turkey for me0 -
both my sensor and my kitchen outdoor thermometer are the same 56 degrees0
-
the Jaga radiator looks pretty interesting. I didn't find any prices for them, but i did not look very hard
Anyone else have a panel radiator company in mind for me to check out?
I have 2 walls 30" wide and alot of height on both sides of the radiator box in the living room
I can invision a radiator on both side of that grill of the old radiator that is doing diddly for the living room
0 -
I suspect those bay window radiators may originally have been exposed, and so heated the room nicely.
I don't see your heat loss info here, but if you can provide those numbers for a few rooms we can help you figure out what you might need there.0 -
Runtal makes a nice low profile radiator."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Runtal was the name of the modern day radiator that i was trying to remember.
I've seen them on a job that i was doing maybe 10 years ago
thanks0 -
the vertical runtals look fine
how many btu's would i be looking for the living room?0 -
I can't seem to find an online source for the vertical runtals. I would like to get an idea how much they cost0
-
-
A properly sized radiator will also work better. Once you balance the system, the difference between room temps will drop significantly.0
-
Take the heat loss for the room and match it to the radiator. Since you are going to be running low water temps you will need to derate the radiators according to the manufactures data. If memory serves me, the runtal at 120 is a multiplier of roughly 0.4.
If you are keeping the existing rads, it is a bit more complicated. You need to look at the EDR of the existing compared to the heat loss."If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
Should I keep the radiators, or just turn them off?
they are doing a little good as far as heating the room, just not alot of good.
but, since it is helping some, and i think i remember it's better to be over radiant, for this system.
not sure what to do
0 -
In order to balance the system and maximize efficiency, you want all the rooms to be similarly over-radiated.
If you have the heat loss figures for the living room and a couple of others, we can get you close with a Runtal or Myson vertical panel radiator. I would supplement the existing rads and not turn them off. Bay windows are large heat sinks.0 -
Kurt
The living room is 15,565 heat loss0 -
Heat loss for some rooms that are heating well right now?
thanks~0 -
my bedroom 6279 i had to turn down the valve on the radiator
and now after several days, the kitchen is doing much better
7351 and office 4266
thanks kurt0 -
Living Room and Kitchen have two radiators each?0
-
yes, but the kitchen is open to my office, that would make 3 radiators. but even with the 3 radiators, the living room radiators are much larger0
-
right now, my kitchen is 71 f
and living room is 71
and bedroom is 73, and that room I turned the valve way down
I appears, the longer i am running the boiler it is getting more balanced (if that's at all possible)
also,
also, it's been unseasonably war the last few days. right now it's 58 outside0 -
Something isn't adding up quite right -- here are the BTU/ft² requirements I get for those rooms:
Living Room 15,565 BTU/hr from 226.8 ft² = 68.6 BTU/ft²
Kitchen 7,351 BTU/hr from 133.5 ft² = 55 BTU/ft²
MBDR 6,279 BTU/hr from 39 ft² = 161 BTU/ft²
0 -
Kurt,
I think the square footage numbers are the surface area of the rads rather than the floor.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Correct those numbers are sf of edr. Output Based on 180 swt.0
-
The living room has 13 foot ceilings the rest of the house is 8'6" ceiling, cubic footage is differnt0
-
Mark the sf of each room with the heatloss would help calculate btus per sf required for the room. Then you compare btus available from existing radiation. To btus needed from the heatloss0
-
Example:
If your radiator has an output of 15000 btus. The room it serves is 300 sf or 10x30 then that equates to 50 btus a sf.0 -
If the rooms heatloss is 25 btus a sf then you have twice the radiation needed to cover the load. So your swt goes down because the edr output is based on 180 swt,0
-
Correct, though I was actually looking at BTU per square foot of EDR in order to determine required water temps.0
-
I can get the sq footage, that's not a problem
doesn't the high ceiling in the living room have anything to do with heating that room properly?0 -
living room 266 sq ft
bedroom 156 sf
kitchen 231 sf0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements