Best Of
Re: Help with hydronic piping to reduce hammer from circ pump
A properly adjusted pressure differential bypass on the discharge side of the pump should get rid of the water hammer.
Re: Flaring tools
I used the YJ style one for 30+ years. Still have it and like it.
About 2 years ago I switched to the NAVAC one. I like that better. And it’s easier to use in tight places.
Re: Gas hissing from water heater combustion air inlet area
Hi, One thing I don't see mentioned so far is the tubing connection at the pilot end of things. These can leak too. The Neanderthal (pre OSHA) approach would be to use a long fireplace match or similar, and move the flame past that fitting. If nothing lights, good. Placement of that connection is such that it would not necessarily be lit by the main burner firing. Also, I've seen leaks along the length of the pilot tube, so the entire length needs to be checked. The noise itself doesn't have to mean something is wrong, but as mentioned above, it could mean the pilot flame is too large.
Yours, Larry
Re: Gas hissing from water heater combustion air inlet area
Hi, As your unit has a flex connector for the main burner, you could remove the unit from the combustion chamber and hook it up, then test for leaks.
Yours, Larry
Re: Lochinvar WB80 not lighting, many new parts already. SOLVED
109A_5 - Yes, there are four wires going to the outlet sensor (#7 in drawing you posted) Yellow,Red,Orange, and Gray. You're right, the wiring diagrams are not very helpful in this case! That sensor only seems to throw a code if it's completely disconnected ("Sensor 1 Open") Even at the time this unit was built they could easily have provided better fault feedback - like the OBDII in cars. (by the way, where did you find that drawing/explantion? Have not seen that before, it would have helped troubleshooting)
Looking at the current track you laid out it's starting to make sense. I'm used to following the current tracks on old cars - no integrated circuit boards!
Hot_Rod - yep, I've been thinking about making up a whole new harness during the summer. Lochinvar has a part number for the cabinet wide harness, it's listed at $400, but nobody seems to have stock. Finding the correct connectors will be the challenge, but a good electrical parts catalog should list, they don't seem to be proprietary.
Alan - Thanks, being cold gives incentive! Living in a small mountain village we're limited on services available. The grounds were checked at the start, both in cabinet and the hardwire to house.
EBEBRATT-Ed - Thanks for the ideas, but hopefully this sensor is the problem and I won't have to keep chasing. Time will tell.
As usual, many thanks!
Re: Replace B&G 100 or use Taco 007 monoflo
I was called into a job years ago where my brother in laws father (in his 90s) was complaining that his addition on his house was cold. He had an old gas fired steam boiler with a tankless heater that heated the HW loop for the addition. There were 2 or three CI rads and they had piped a split loop 1" supply and 2 3/4 returns. (way overkill) He already had every local plumber look at this with no luck. They had monkeyed with this for years. They had taken the CI radiators out, put baseboard in and then put the CI radiators back in. I don't think it ever worked right. I think as his father got older he couldn't tolerate the lack of heat.
It had a Taco 110 circ.
After staring at this for a while feeling the pipes and bleeding the system I stood there looking at the tankless coil with it's 1/2" connections and pictured how much 1/2" tubing it took to make the tankless coil.
I upped the pump (forget what I put in) and it was fine.
I never missed when sizing a pump for a new job but going to an existing job that sort of works it gets in your head.
You have to step back , start from scratch gather some information and figure it out.
Re: top floors not getting that much heat
Your vents on each radiator may need attention, you may also have the pressure set too high
There are other causes. Can you post photos of your boiler in the basement so we can see the connecting pipes from the floor to the ceiling?
Re: Flaring tools
I think, if I remember right the clutch releases before the double flare is complete. I could be misremembering though.
