so you can close the service valves to isolate the condenser then you know if the leak is in the linset or evaporator or the condenser. there is usually a gasketed connection for the txv or a connecting tube with an orifice piston at the inlet of the evaporator. usually inside the casing. do you have specs o the test pressure? if you can increase it to maybe 200 psig or so you may be able to hear it.
Trane ac air handler
I have a Trane air handler TWH039P 150C1 from ‘92 that just handles AC and the fan continuously runs but the compressor will cycle off. If I hit the relay I can get it to turn off so I think it’s just the relay and not the timer board. Problem is I can’t find this relay and would greatly appreciate some advice on what a replacement would be. I’ve attached photos of the original relay.
Thank you!