Best Of
Re: My Aquastat only has a high limit any reason why or should I put a low limit controller on.
this is desirable if you do not need to maintain boiler temp for your Domestic hot water such as in your case with your separate water heater.
By allowing your boiler to cool off more in between cycles you achieve longer run times during a call for heat which is more efficient than maintaining your boiler temp at say 140°F
Longer run times are better then short run times... (think highway driving vs city driving)
If the tech changed your aqua stat from a cold start to a non cold start then I would call them and ask them to install the correct control.
you will no doubt use some extra fuel by maintaining the boiler temp full time.
Re: Serviceable Hand Held shower Head
Maybe a spin down filter by a company named Rusco or others would help.
Re: Indirect water heater drywell overflowing?
it's leaking. determine the location of the leak, if you can replace the well that would be the preferred option, if that is not possible for whatever reason you would need to replace the tank. if you are the original owner you likely have a lifetime warranty so contacting tech support and explaining what is going on, they may have a better recommendation. triangle tube customer service may know a local dealer that can replace the well. Either way expect to pay for hired labor, and see with triangle tube what your warranty status is, check with whatever vendor you buy from that they are able to process the warranty with you so can be credited for parts if under warranty
Re: 1930's Hydronic System help understanding
Looks Ok. You may not need the check valve if there is one in the circ.
Re: Indirect water heater drywell overflowing?
Maybe the well is leaking water into the control.
Re: Refurbished radiator making bird noises. Not vent?
@AdmiralYoda Yeah completely agree. Annoying that it doesn’t “just work” but it would be REALLY annoying to disconnect, return, and roll the dice on another one.
It’s a nice looking radiator too, the matte black rustoleum bbq spray finish turned out pretty good.
Re: Condensate Piping- One Pipe
Steam can't move through a system that has air in it. The quicker you vent the air, the quicker the steam can move through the system.
The general rule is, Vent the Mains fast and the rads slow.
Re: Condensate Piping- One Pipe
You burn fuel the push the air out of the system. Steam may fill the main pipes faster, less burn time, less fuel. May help with balancing the mains too, for more even heating.
Re: Help with Goodman GSXC16 Error code 04
All this talk about the electric service is moot. The electric company fixed the problem and now we are just waiting on the warranty replacement parts. Other neighbors on the same underground service past my son's home also experienced electrical problems and their light dimming problems have also stopped. Many problems solved. Still getting error 04. Now we will see if the replacement board will correct that problem.
I'm just giving all here an update now that I believe that the issue will be corrected as soon as the PCB in replaced. I believe that some hard to solve problems here never reach a conclusion because once it is fixed, there is no need to post anything here and we all would like to know what happened. Did the problem get fixed? Did the the equipment get replaced? Did the wrong steam piping get repiped correctly? Did the house blow up? Did the OP die in the explosion? Just wanted everyone to know that I'm still alive!🤣
Stay tuned to this channel for more updates after station identification.