Re: What options do I have with this steam two-pipe system?
Add a balancing valve or orifice plate with the trv so it doesn't heat fully even when the trv opens fully to throttle things a bit.
1
Re: Replacement Aquastat Unit
I've replaced the older milivolt aquastats with modern digital aquastats by adding a RIBU1C relay to the burner terminals.
Re: Rusty NEW MoM main vents
Hello @Jim_X,
Maybe this will help.
Deep Dive Into Gorton #2 Main Steam Vent Construction & Failure Modes
https://youtu.be/s-g0YSu8Bbo
Gorton #2 Main Steam Vent With Nothing To Hide
https://youtu.be/LeYDZvD7NmI
Gorton / Maid-o-Mist Single Pipe Steam Radiator Air Vents
https://youtu.be/0ugIrg9bquk
Maybe this will help.
Deep Dive Into Gorton #2 Main Steam Vent Construction & Failure Modes
https://youtu.be/s-g0YSu8BboGorton #2 Main Steam Vent With Nothing To Hide
https://youtu.be/LeYDZvD7NmIGorton / Maid-o-Mist Single Pipe Steam Radiator Air Vents
https://youtu.be/0ugIrg9bquk2
Honeywell Power-pile VS8187A1203
Hi All,
My boiler is starting intermittently. I traced the issue to a loose PP terminal on the power pile. I replaced the terminal on the wire end, but seems the terminal is loose in the terminal strip, as is the entire terminal strip loose to the unit. Are these power pile's serviceable (maybe an internal solder joint broke?)? Are these valves still available, or is there a suitable replacement that anyone know of?
Thanks Much!
JP - Winnipeg, MB Can
My boiler is starting intermittently. I traced the issue to a loose PP terminal on the power pile. I replaced the terminal on the wire end, but seems the terminal is loose in the terminal strip, as is the entire terminal strip loose to the unit. Are these power pile's serviceable (maybe an internal solder joint broke?)? Are these valves still available, or is there a suitable replacement that anyone know of?
Thanks Much!
JP - Winnipeg, MB Can
1
Re: Well that isn't going to work (outdoor unit iced over)
So, what was there 1st?
if the heater exhaust than the condensing unit gets moved. I’d the A/C then the heater exhaust gets moved.
The boiler exhuast was put in first. I'll likely move the AC Compressor around the corner this upcoming summer to avoid problems.
For anyone wondering about performance, I did kick the heat pumps in for the bedrooms which uses a different compressor (same model/size properly located) and even at -15F it's keeping up in the bedrooms. I suspect it's not very effecient at these temps so I'll kick the hydronic heat back on shortly but I do want to move to a air to water heat pump for the hydronic eventually (2-5 year), so it was worth seeing how they performed on design days...
iced98lx
2
Re: Hauling A Furnace In The Back Of A Pick-up Truck
kinda comes to a point that , if installed, it must idle all winter season, can't be used to just warm the shop on a random weekend , or work day,
you still have the same condensate concerns freezing up,
but you knew that, , , ,
you still have the same condensate concerns freezing up,
but you knew that, , , ,
1
Re: Hand held ultrasonic flow meter? Water differential pressure gauges/ Hydronic manometers?
Testo 550 are rated for r-718, probably most others are also. get a selection of different gauges depending on the pressures.
Probably find these cheap at pawn shops, CL, FB marketplace, e-bay, etc.
From HVAC-talk
Probably find these cheap at pawn shops, CL, FB marketplace, e-bay, etc.
From HVAC-talk
hot_rod
1
Re: Leaking air vents on steam baseboard raditors and banging noise in pipes
A "C" vent is a fast vent and that type of convector is usually happiest with lower vent rates because of all the condensate the convector produces. Are the other convectors venting at that same rate?I need to do more research on convectors to better understand you feedback
You can get vent kits that come with a vent and 5 different vent orifices for that single vent, this lets you dial in the correct venting rate.
Generally you want to vent the mains slowly and the radiators slowly. Keep in mind this is a heating system and it has to be balanced so it comes up to heat at about the same time.
Bob
Re: Radiant Heating Pump pulling power, 0 GPM output. Advice Appreciated
Here is a better illustration of @hot_rod"s diagram. This shows the radiant floor tubing not in the picture. The instructions are the same. Close valve at the circulator pump (#3). Attach the hose from the water heater darin to #2 purge valve. let the water out at #1 purge valve.
Once that is all done, close the valve #1 first.
Then close the valve at the bottom of the water heater second.
Next close the valve #2
Now open valve #3
Check the pressure gauge. if the water pressure is over 50 PSI (or 115 feet) lower the pressure to about 20 PSI or so by letting some water out of valve #1. Then you should be good to go for the rest of the winter. .

By the way.. you still need a relief valve and other components on that heating system closed loop, if it has the heat exchanger coil inside the tank. Please let us know the model number so I can determine if you have the Combi Core® or not.
Once that is all done, close the valve #1 first.
Then close the valve at the bottom of the water heater second.
Next close the valve #2
Now open valve #3
Check the pressure gauge. if the water pressure is over 50 PSI (or 115 feet) lower the pressure to about 20 PSI or so by letting some water out of valve #1. Then you should be good to go for the rest of the winter. .

By the way.. you still need a relief valve and other components on that heating system closed loop, if it has the heat exchanger coil inside the tank. Please let us know the model number so I can determine if you have the Combi Core® or not.