Re: Indoor Reset
Another Level
Between the "smart" boiler and "more and better sensors".
It's the boiler that learns how to adapt to the system to which it is connected. Ideally it learns how to keep everything (boiler and system) operating at peak efficiency. Such is relatively simple if the system has constant and proportional flow. It gets much more difficult with a barrage of digital inputs.
In that regard, modulating boilers are different. I believe that the Vitodens is the only one capable of learning in the way.
Fortunately it does NOT lock you out from being able to control the supply temperature--it learns to adapt to the temperature curve you set.
As I mentioned elsewhere, my Vitodens is learning to use the volume of the system as its buffer when demand is lower than low-end modulation. I suspected this would happen--in fact I reasoned that it must happen were this boiler to be "perfect". So far, it does appear perfect.
Interesting that the control unit displays not only current outside temperature, but "damped" outside temperature. (The damped temp is blank on mine.) I suspect that in Germany MANY more options are available and that you can install a 2nd outdoor temp sensor on the "hot side" of the structure instead of just the "cold side". The unit will then use the difference between the two to establish a damping factor that makes a corresponding adjustment in the supply target.
Anyone know if such a sensor is available HERE and can be installed in a system of type 000:000???
This is going to sound like a bizarre idea, but here goes anyway:
Say you have a proportional system with very low heat loss--not much greater than the low-end modulation rate of the boiler.
One approach to this problem would be to drive the system through a buffer and allow a wide variance in the buffer tank temperature between "charges" with heat.
As an alternative, why not install a well-insulated hot water tank in series with the system load. The burner WILL find all of that extra water. Even with extremely low loads, you should still get nice, long firing cycles.
Between the "smart" boiler and "more and better sensors".
It's the boiler that learns how to adapt to the system to which it is connected. Ideally it learns how to keep everything (boiler and system) operating at peak efficiency. Such is relatively simple if the system has constant and proportional flow. It gets much more difficult with a barrage of digital inputs.
In that regard, modulating boilers are different. I believe that the Vitodens is the only one capable of learning in the way.
Fortunately it does NOT lock you out from being able to control the supply temperature--it learns to adapt to the temperature curve you set.
As I mentioned elsewhere, my Vitodens is learning to use the volume of the system as its buffer when demand is lower than low-end modulation. I suspected this would happen--in fact I reasoned that it must happen were this boiler to be "perfect". So far, it does appear perfect.
Interesting that the control unit displays not only current outside temperature, but "damped" outside temperature. (The damped temp is blank on mine.) I suspect that in Germany MANY more options are available and that you can install a 2nd outdoor temp sensor on the "hot side" of the structure instead of just the "cold side". The unit will then use the difference between the two to establish a damping factor that makes a corresponding adjustment in the supply target.
Anyone know if such a sensor is available HERE and can be installed in a system of type 000:000???
This is going to sound like a bizarre idea, but here goes anyway:
Say you have a proportional system with very low heat loss--not much greater than the low-end modulation rate of the boiler.
One approach to this problem would be to drive the system through a buffer and allow a wide variance in the buffer tank temperature between "charges" with heat.
As an alternative, why not install a well-insulated hot water tank in series with the system load. The burner WILL find all of that extra water. Even with extremely low loads, you should still get nice, long firing cycles.
Re: Indoor Reset
Bob,
The Vitodens appears capable of what you say, yet it has no indoor temperature sensor. Only the outdoor sensor and whatever sensors are built in to the boiler itself. (Still not sure if it senses return temp or not by the way.)
Cloudy/rainy weather finally went away and days are significantly warmer with nights significantly cooler. Still not cold and the boiler is having to learn how to most effectively run in digital operation--remember it can't modulate down to nothing. Low end is about 22 mbh.
This is an old gravity system so there's LOTS of water in the mains. Also, the radiant floors are just connected to the mains with no form of control. Even with all of the TRVs satisfied, there is still a small amount of flow and small heating load from the radiant areas. Therefore there is always some circulation in both main pairs.
The old boiler (a simple standing pilot cast iron cube) was connected to mechanical outdoor reset and WWSD. Circulator constantly running except when stopped by WWSD. Once the house was maintaining heat, the boiler firing time became remarkably consistent--about 2 minutes, 20 seconds. Only the interval between firings would change with outside temp.
There is no low-loss header for the Vitodens and I speculated that it would turn the mains into a buffer. Guess what? It is.
While the Vitodens is still learning, it's a precocious kid that learns fast.
When outside conditions are such that lowest modulation is still too much heat, operation is really interesting:
After not firing for quite a period, the burner will come on at full fire. You can watch the actual supply temp rise rapidly. Within a few seconds, the burner shuts down. This repeats every few minutes for a few times. Then, the burner will come on and ramp down immediately. Actual supply temp is at the reset setpoint and it STAYS there for a very long time--easily 20 minutes! At the end of the cycle, the supply temp starts rising quite rapidly (after having stayed steady) and the burner shuts down.
Then the burner stays off for a long period and supply temp begins a very gradual decline.
My only explanation is that the boiler is learning to charge the buffer (e.g. all of that water in the mains) in a manner to allow the longest possible burn time with minimal target supply temperature overshoot or undershoot.
The Vitodens appears capable of what you say, yet it has no indoor temperature sensor. Only the outdoor sensor and whatever sensors are built in to the boiler itself. (Still not sure if it senses return temp or not by the way.)
Cloudy/rainy weather finally went away and days are significantly warmer with nights significantly cooler. Still not cold and the boiler is having to learn how to most effectively run in digital operation--remember it can't modulate down to nothing. Low end is about 22 mbh.
This is an old gravity system so there's LOTS of water in the mains. Also, the radiant floors are just connected to the mains with no form of control. Even with all of the TRVs satisfied, there is still a small amount of flow and small heating load from the radiant areas. Therefore there is always some circulation in both main pairs.
The old boiler (a simple standing pilot cast iron cube) was connected to mechanical outdoor reset and WWSD. Circulator constantly running except when stopped by WWSD. Once the house was maintaining heat, the boiler firing time became remarkably consistent--about 2 minutes, 20 seconds. Only the interval between firings would change with outside temp.
There is no low-loss header for the Vitodens and I speculated that it would turn the mains into a buffer. Guess what? It is.
While the Vitodens is still learning, it's a precocious kid that learns fast.
When outside conditions are such that lowest modulation is still too much heat, operation is really interesting:
After not firing for quite a period, the burner will come on at full fire. You can watch the actual supply temp rise rapidly. Within a few seconds, the burner shuts down. This repeats every few minutes for a few times. Then, the burner will come on and ramp down immediately. Actual supply temp is at the reset setpoint and it STAYS there for a very long time--easily 20 minutes! At the end of the cycle, the supply temp starts rising quite rapidly (after having stayed steady) and the burner shuts down.
Then the burner stays off for a long period and supply temp begins a very gradual decline.
My only explanation is that the boiler is learning to charge the buffer (e.g. all of that water in the mains) in a manner to allow the longest possible burn time with minimal target supply temperature overshoot or undershoot.
Re: Indoor Reset
Indoor Reset ( I like the name)
Paul,
Our company has a patent pending on a technology that will not likely be out until some time in 2005 or 2006 called Dynamic Demand Profiling. Essentially, we have found a way of calculating the precise heat loss of a structure from information available in virtually every heating system, without a multitude of sensors (indoor or outdoor). Our reset formula is based upon an algorithm that calculates the "Thermal Resistance" of the structure and accurately resets the Mean Delivered Water Temperature based on the current rate of heat loss.
Modulating the water temperature in theory will increase occupant comfort, but we see no evidence that it will incease system efficiency. We have, however, found that moduating the Differential based on the system's capacity to recover (BTU input vs BTU loss) is an effective way of increasing efficency through fewer but longer burn cycles (not a new idea).
The problem is that wide swings in delivered water temperatures (Differential) works against the occupant comfort objective of reset, so a comprimise must be made.
I don't know if this is what you were thinking about, but it is something that we are working on.
Bob Tonner
President
InfinityLab Inc.
www.infinitylab.com
Paul,
Our company has a patent pending on a technology that will not likely be out until some time in 2005 or 2006 called Dynamic Demand Profiling. Essentially, we have found a way of calculating the precise heat loss of a structure from information available in virtually every heating system, without a multitude of sensors (indoor or outdoor). Our reset formula is based upon an algorithm that calculates the "Thermal Resistance" of the structure and accurately resets the Mean Delivered Water Temperature based on the current rate of heat loss.
Modulating the water temperature in theory will increase occupant comfort, but we see no evidence that it will incease system efficiency. We have, however, found that moduating the Differential based on the system's capacity to recover (BTU input vs BTU loss) is an effective way of increasing efficency through fewer but longer burn cycles (not a new idea).
The problem is that wide swings in delivered water temperatures (Differential) works against the occupant comfort objective of reset, so a comprimise must be made.
I don't know if this is what you were thinking about, but it is something that we are working on.
Bob Tonner
President
InfinityLab Inc.
www.infinitylab.com
Re: Indoor Reset
Certainly hydronic control is much more advanced than typical forced hot air furnace control by a long measure. But with that being said, the approach your discussing above sounds somewhat similar to what Rheem/Ruud is doing with their Mod 90 furnace. The furnace modulates from 40% to 100% of capacity and uses an ECM blower that keeps the temp rise across the HX the same regardless of modulation level. They have a proprietary thermostat that has an additional signal (V terminal) to the furnace control board that tells the furnace what modulation level is needed. I believe the thermostat is measuring the rate of change of air temperature plus cycle data, and trying to use this information to infer the needed heat production to match the loss. As the system runs and you accumulate data on multiple furnace cycles it is suppose to get smarter with regard to this calculation.
1
Re: Importance of outdoor temp sensor for reset on Viessmann Vitodens B1KE-120 ?
ODR is the logic providing comfort and efficiency of the boiler. One way to see if you have the curve set correctly is to pick the heating zone with the highest heatloss….generally the great room. But your heatloss calcs will tell you that, highest btus/sqft. Do this on a cloudy day, to take solar gain out of the equation. Turn the thermostat up in that room to 80F and let the system run for a day. If the tstat achieves a higher setting than your desired set point(68F). You can turn down the slope and shift. I would start at 0 for shift. As said earlier in this thread you can run your house off a perfectly set reset curve without a tstat. At that point you are heating your home with the lowest possible supply water temp which in return provides a constant inside temp. The idea is call constant circulation which is the ultimate in comfort and efficiency.
Jeffrey
Re: Does thermal solar DHW make any economic sense for a 2-4 person home today?
Systems designed for families or multi family that served design loads for 5 years or so then with new owners or kids moving out, things change and 160 gallons of storage is very under utilized till something breaks and no one can be found to fix it. A kid plumber isolates it and it eventually gets removed. Payback never achieved. There is a tendency for solar designers to want all the fruit instead of just low hanging. They tend to over build as to never run out of hot water (perceived weakness) and much of the capacity is never used. Blunt is fine, I'm not engineering these things. I'm not saying there is never a good design use match up that lasts beyond payback. It's just not typical.
Teemok
1
Intrigued by NYC Retrofit Accelerator Diagram - How much is applicable to single family home?

Thanks to an advertisement from a particular bespoke radiator manufacturer, I stumbled upon this diagram from NYC's Retrofit Accelerator Program. I am curious how relevant this is to my single-family home vs. a NYC apartment.
This winter, after having water hammer problems due to a wet return being too high and two radiators not heating/slow to heat (still a problem that I just haven't devoted time to), my house was well-heated with only minor banging noise coming from the radiators and not the pipes - overall, the house was quite comfortable with only minor, manageable quirks like any other.
But I saw this picture linked in my email, I went down the rabbit hole in curiosity. Looking at the 5 things:
- Boiler Tune-Up: I get annual tune-ups, but to my understanding residential modulating steam boilers aren't really a thing - it would be quite nice if they were.
- Master Venting: Does installing a vent on the inlet (steam) pipe right before my third-floor radiator make sense? This is one of two radiators that really lag and doesn't seem to get as much heat as the others.
- Controls and Sensors: I've fully implemented this, with 11 of my 16 radiators having smart, connected valve controllers that open and close based on a set temperature. I also use the Netatmo boiler thermostat which controls the system and can even turn on my boiler to heat specific rooms,
- Orifice Plates: Does this make sense for me? As I haven't found any really good steam boiler mechanics in Western NY, I've become plenty handy and changing out valves and traps. Installing orifices themselves will be easy enough for me, but how do I go get orifice plates? It seems like an email to Tunstall with all of my radiator sizes is one way and I've scoured heating help and found a couple of sizing tables should I choose do it myself.
- TRVs: I have TRVs on 13 of 16 radiators, I don't have a TRV "master" radiator that is in the parlor with the thermostat. As this affects when the boiler turns on, I've throttled this screw valve down so my parlor heats at approximately the same rate as my bedroom (the room I want to maintain) and allows me to run my thermostat on "ECO" mode (radiator valves only turn on boiler with specific override) and along with hacking my Pressuretrol to a .1psi->1psi operating range reduces overall boiler cycles.
- Does installing a vent on the inlet (steam) pipe right before my third-floor radiator make sense? As near as I can tell the only air vents are at the end of my two steam supply runs in my basement. I should be able to install a tee with a vent on the inlet pipe fairly easily - I'll wait until the heating season is over so that in the worst case, I can break my pipe trying and then hire a contractor on a non-emergency basis.
- Does installing orifice plates make sense? I searched heating help and pursued 50 or so threads (including stumbling into one of mine) and it seems like it is always a good idea. Specifically, would it help with my sunroom, where the radiator heats up quickly, increases the temperature on the adjacent smart thermostat valve, and shuts off before the entire room gets hot?
- How do I acquire orifice plates? It looks like I can make them myself (one case of beer) or have them made by Tunstall, any other options?
KarlW
1
Re: Maximum PSI at home with water booster pump receiving 50 PSI from utility water main?
Check the screens on the washer hoses. Plugged screens will cause a pressure drop as it tries to fill
30 even 20 psi should be adequate
30 even 20 psi should be adequate
hot_rod
5
Re: Advice for replacing torn Flex with metal ducts
I've accessed small crawl spaces for repair / replacement work by cutting holes in the floor. Closets, under cabinets, and other discreet areas can help provide easier access. And if the finished flooring is carpeting, it's fairly simple to make & repair access holes.....
MikeL_2
1
Re: Question!
Sylvain said:
Of course this is only a pedagogic example; who would do that?
On the other side, a low Cv means more (pump) energy dissipated in the valve.
There is an optimum to be found. Installation cost/running cost.
How many zone on a single pump? One pump per zone? Which type of pump?
No - this is the actual heating system design in a multi-family building, which is a very good teaching example - because it is the optimum system design.
The in-floor heating system in the multi-family building in which I live has one single pump, to pump the floor-heating water to approximately 170 zone valves - about 8 zone valves per suite in 21 suites.
The single pump is a 3" ECM Smart-Pump that draws about 120 watts while maintaining a ∆P of 5 psig as it delivers warm floor-heating water to the entire building. As the zone-valves open and close, the Smart-Pump simply maintains the 5 pig differential pressure. Do not over-estimate the theoretical energy dissipated by the valve. Do add up the actual total pumping energy.
This single-pump heating system design provides the lowest installed-cost, and the lowest operating cost, compared to any multi-pump system you could envision. Why would you want to install 21 pumps - one per suite - or 170 pumps - one per zone ?
Of course this is only a pedagogic example; who would do that?
On the other side, a low Cv means more (pump) energy dissipated in the valve.
There is an optimum to be found. Installation cost/running cost.
How many zone on a single pump? One pump per zone? Which type of pump?
No - this is the actual heating system design in a multi-family building, which is a very good teaching example - because it is the optimum system design.
The in-floor heating system in the multi-family building in which I live has one single pump, to pump the floor-heating water to approximately 170 zone valves - about 8 zone valves per suite in 21 suites.
The single pump is a 3" ECM Smart-Pump that draws about 120 watts while maintaining a ∆P of 5 psig as it delivers warm floor-heating water to the entire building. As the zone-valves open and close, the Smart-Pump simply maintains the 5 pig differential pressure. Do not over-estimate the theoretical energy dissipated by the valve. Do add up the actual total pumping energy.
This single-pump heating system design provides the lowest installed-cost, and the lowest operating cost, compared to any multi-pump system you could envision. Why would you want to install 21 pumps - one per suite - or 170 pumps - one per zone ?