Best Of
Re: Tankless Coil Intermittent Hot Water
Welcome new steam homeowner. We were all in your shoes at one point.
Do yourself a favor and cut the lines to the coil, buy a standalone water heater and leave your boiler off in the summer.
There's no reason to tie your domestic hot water to that boiler.
Even a resistive electric water heater is only a few hundred dollars a year to run and if you want, you can get a heat pump water heater and have super cheap hot water with possible incentives from your local utility or state.
Re: Tankless Coil Intermittent Hot Water
As EPaul alludes, the boiler coils are not very efficient, are difficult to control and often clog with lime in many areas. You'll probably be happier with an indirect hot water tank, or separate tank hot water heater.
If you keep the hot water coil, it should (must) be plumbed with an automatic tempering valve to prevent it from delivering dangerously hot domestic water when the heating system is steaming. Many installers skipped the tempering valves or substituted a manual valve to save a few bucks. Especially with kids or elderly folks in the home, overheated hot water can cause serious injuries.
Re: Tankless Coil Intermittent Hot Water
under that cardboard are 3 screws, common, normally open, normally closed,
a volt meter across common, and NO, or NC, would tell you where your volts are going, listening closely will swinging the setting dial you should also hear a click,
Re: Tankless Coil Intermittent Hot Water
Yes. Sorry, I feel dumb assuming you had a closed hydronic system. 180° should be fine and the differential is at 5° so there shouldn't be an issue. Can you show the coil or water heater and piping? Is there a mixing valve?
HVACNUT
Re: Tankless Coil Intermittent Hot Water
um, yeah, but you're already set up around 180, (were) correct?
post a picture showing your sightglass, and the domestic coil and aquastat all in one,
water level in the boiler needs to cover the coil for good performance, let's see it
Re: Tankless Coil Intermittent Hot Water
Not dumb at all. Just need a bit more information. The aquastat is exactly what is required and you already have it. You have set it to 180°F and that will solve your problem. You can also see a small white dial on the right side near the bottom. It's set at 5°F. Increase this value to 15°F. This will prevent too much cycling of the boiler when the heat is not calling. I'm fairly sure you'll still be OK in the shower………….but, if not………….reduce it to 10°F.
Don't bother with any meters testing anything under the cardboard………..more work that you don't need.
You already have the anti-scald valve which is important with a steam boiler held at 180°F.
Re: Tankless Coil Intermittent Hot Water
Your boiler is steam so the L4006A is a low limit to run the boiler for domestic water. That is its only purpose. 130 is way to low. Set it at 160 and see how you do. If not enough hw you can go to 170.
If your water is hot when set to 160 after a few days you can creep it down a little till your short of hot water. Play with it until you get the right setting.
Your mixing valve could also be bad or tired. You can also replace the element in the mixing valve if the water temp adjustment doesn't fix it.
The L4006A is working as a low limit. It fires the burner if the water temp drops below the setting.
Re: Most conservative setting for barometric damper without a draft gauge?
From the field controls installation sheet;
Adjusting the control.
The burner must be running when the adjustment of the control is made.
The use of a draft gauge is required to set the overfire draft.
Set the over fire draft according to the appliance manufacturers instructions.
Set the control to maintain as low a draft as will give good combustion and meet the requirements for heat.
Turn the adjustment weight counter-clockwise too loosen, then slide in slot to the proper position and tighten.
The bracket is marked 2, 4, 6 and 8, which indicates draft settings of .02", .04", etc. (These are drafts adjacent to the control, Not overfire drafts)
Oil Burner Combustion Air And Overfire Draft Setting (inches of W.C.)
After the burner has operated for at least 5 to 10 minutes, take draft readings over the fire. For a domestic burner the over-fire draft should be .02-.03, although there are some makes of burners which require higher drafts. Follow the burner manufacturer installation instructions for proper settings. Ther must always be enough draft so that the burner does not puff back into the room at the moment it starts, and there should be no objectional smoke. CO2 and smoke readings must be taken to determine the proper adjustments.
========================================================================================
If you really want to ride herd on this you can purchase a Dwyer Mark II Manometer and a probe from Dwyer to monitor the draft on your oil boiler.
Re: Micoe Heat Pump - A Dead Loss
good eye!
yes the parts are common to both. These are just seeds and stems I have lying around the shop that I assemble for different demos or personal use.
The polymer media inside is also the same for dirt and air.
hot_rod