Best Of
Re: New-ish local boiler install
What happens at the ultimate end of the main? Unless it is pitched away from the end, the end of the main needs a steam trap or a drip to a wet return to drain the condensate out of the main.
The main could be vented through a crossover steam trap to the return, through an air vent, or the main could just vent through the emitters and their steam taps to the return. It looks like this is just a conventional 2 pipe system, it wasn't some sort of vapor system.
The return needs to have a vent somewhere (or be open)
Re: New-ish local boiler install
The takeoff for the mains and the equalizer are in the wrong order so any water is going to tend to get thrown in to the mains instead of draining down the equalizer. the pressure is too high. fix the near boiler piping in the off season but it should mostly work if the water quality is good so it isn't priming or surging.
my bet on the not heating would be that there are bad steam traps letting steam in to the returns and/or keeping it from venting. also look for connections that should be under the water line that aren't. at the higher pressure they will need to be far under the water line so turn the pressure down.
Re: Burnham Boiler - Aquastat Issue?
A boiler that size should have 2 high limits wired in series. 1 should be a L4006A and the manual reset control should be a L4006E (I believe that is the correct #)
You should have this fixed and the wiring check. Runaway boiler system is not good.
You aquastat in the picture set for 160 looks like it may be a strap on aquastat (strapped to a pipe). If that is the case that is not good the high limit should be an aqua stat with a well inserted in the boiler water.
Re: Burnham Boiler - Aquastat Issue?
Hello ElvisWashington,
The pressure part of the gauge may be broken.
Do both aquastats serve as a redundant boiler high limit ?
Aged pitted electrical contacts can stick closed.
Re: Help choosing a new boiler (part 2)
I know I will get disagreement, but you’re asking for opinions.
I would never do a combi, they are always a compromise IMHO.
I wouldn’t do an indirect either. Why run a boiler if you don’t need to? I’d do a heat pump water heater, in Canada, based on my limited knowledge, I would think this is the way to go. I fully appreciate the electric rates are regional. That is unless you need mountains of hot water for hours on end? The domestic hot water decision comes down to lifestyle, it’s not really a system decision. I’m betting none of the contractors have discussed lifestyle with you? They probably just want to provide you with something that no one, regardless of lifestyle, complains about. So, you will get recommendations based on people who take 45 minute showers at the hottest temp they can stand, for 3-4 people back to back.
For the heating side I’d get the smallest boiler available and have that put in. With your low load, I believe all of them will be oversized, so in my opinion it’s 100% about the lowest output, not the maximum, in your case. Considering you said no cast iron is allowed in your area.
Re: Help choosing a new boiler (part 2)
Combi boilers are made for apartments , you would find them in the kitchens in Europe where they also use radiators for heat , low temperature heat .. You have a basement with baseboard which is high temperature heat . A condensing boilers efficiency is peak at low temperature . Running it for baseboard the smaller savings gets eating up by the service , besides the aggravation of getting it running again up there with the great moose of the North way :)…. Go low as they allow you to go, as far as tech would be my recommendation …
Big Ed_4
Re: Help choosing a new boiler (part 2)
No, I mean a contractor that specializes in Hydronics. Most plumbers and HVAC contractors are clueless on hydronics.
You need to specifically look for and ask contractors if they’re trained and equipped to properly install and service mod/con boilers. Ask if they have a digital combustion analyzer and if they know how to use it.
There are only a small percentage of jobs where a combi is suitable and they require a lot more maintenance and repairs. Particularly where there’s poor water quality.
The fact that so many contractors push combi’s and Naviens only demonstrates their lack of hydronic expertise.
Ironman
Re: New-ish local boiler install
I added an edit. The piping diagram from the manual and a mock up of what is there. That boiler will flex at the riser tappings. You may catch it in time next summer, OR it may be too late. To be sure, that you get it right next summer, take all the sections apart and install all new "O"ring at all the section connections. you will also need new sealer and maybe new rope gaskets. Part numbers 592-800-010, 592-800-007 and 591-641-865.
You will need a set of o rings and rope gaskets for each section you take apart. OR… You can try to redo the piping without changing the O Rings and hope you get lucky.
Since you have low head room in that location, I strongly recommend a Drop Header in order to get necessary rise in all the vertical pipes. Here is an example of a drop header
Make a special note of three things.
- The header is lower AFTER the boiler risers go above 24" before the elbows turn to make a U turn back down to the Header.
- the system riser is not placed between the two boiler risers.
- The Hartford loop uses a close nipple (#16) that is connecting the equalizer (vertical pipe at the end of the header) at about 2" below the water line, to the wet return piping. Wet return means the return must drop below the boiler water line before it rises up the the close nipple (#16)
Good luck with this project.
Re: New-ish local boiler install
Read
The
Fu**ing
Manual
I agree, it’s like they want to do a poor job. Anyone, in any industry, that doesn’t read the manual, is automatically a hack in my world. I learned how important the manual is when I was a teen assembling my parents new propane grille. Missed part of one step and had to disassemble almost the entire grille because I couldn’t put the last part on. I also work for an OEM manufacturer of industrial HVAC and refrigeration equipment and I can tell you first hand, even on the multi million dollar installs of our equipment some “experienced” contractors screw it up, and screw it up HUGE. It’s sad when there is a manual that will make most of these mistakes, essentially, impossible.
For the OP, I’d start with a radiator survey. If one is going to touch anything you need to know how big the mistakes are. I’d bet money they didn’t size it correctly and on a two pipe that can be a much bigger problem. After that the entire boiler needs repiped. I’m not a two pipe expert, but there are definitely details of each system that need to be correct for it to function properly and that needs to be verified to see how extensive the repipe needs to be.