Re: Tankless Coil Intermittent Hot Water
Yes. Sorry, I feel dumb assuming you had a closed hydronic system. 180° should be fine and the differential is at 5° so there shouldn't be an issue. Can you show the coil or water heater and piping? Is there a mixing valve?
HVACNUT
Re: Tankless Coil Intermittent Hot Water
um, yeah, but you're already set up around 180, (were) correct?
post a picture showing your sightglass, and the domestic coil and aquastat all in one,
water level in the boiler needs to cover the coil for good performance, let's see it
Re: Tankless Coil Intermittent Hot Water
Not dumb at all. Just need a bit more information. The aquastat is exactly what is required and you already have it. You have set it to 180°F and that will solve your problem. You can also see a small white dial on the right side near the bottom. It's set at 5°F. Increase this value to 15°F. This will prevent too much cycling of the boiler when the heat is not calling. I'm fairly sure you'll still be OK in the shower………….but, if not………….reduce it to 10°F.
Don't bother with any meters testing anything under the cardboard………..more work that you don't need.
You already have the anti-scald valve which is important with a steam boiler held at 180°F.
Re: Tankless Coil Intermittent Hot Water
Your boiler is steam so the L4006A is a low limit to run the boiler for domestic water. That is its only purpose. 130 is way to low. Set it at 160 and see how you do. If not enough hw you can go to 170.
If your water is hot when set to 160 after a few days you can creep it down a little till your short of hot water. Play with it until you get the right setting.
Your mixing valve could also be bad or tired. You can also replace the element in the mixing valve if the water temp adjustment doesn't fix it.
The L4006A is working as a low limit. It fires the burner if the water temp drops below the setting.
Re: Most conservative setting for barometric damper without a draft gauge?
From the field controls installation sheet;
Adjusting the control.
The burner must be running when the adjustment of the control is made.
The use of a draft gauge is required to set the overfire draft.
Set the over fire draft according to the appliance manufacturers instructions.
Set the control to maintain as low a draft as will give good combustion and meet the requirements for heat.
Turn the adjustment weight counter-clockwise too loosen, then slide in slot to the proper position and tighten.
The bracket is marked 2, 4, 6 and 8, which indicates draft settings of .02", .04", etc. (These are drafts adjacent to the control, Not overfire drafts)
Oil Burner Combustion Air And Overfire Draft Setting (inches of W.C.)
After the burner has operated for at least 5 to 10 minutes, take draft readings over the fire. For a domestic burner the over-fire draft should be .02-.03, although there are some makes of burners which require higher drafts. Follow the burner manufacturer installation instructions for proper settings. Ther must always be enough draft so that the burner does not puff back into the room at the moment it starts, and there should be no objectional smoke. CO2 and smoke readings must be taken to determine the proper adjustments.
========================================================================================
If you really want to ride herd on this you can purchase a Dwyer Mark II Manometer and a probe from Dwyer to monitor the draft on your oil boiler.
Re: Micoe Heat Pump - A Dead Loss
good eye!
yes the parts are common to both. These are just seeds and stems I have lying around the shop that I assemble for different demos or personal use.
The polymer media inside is also the same for dirt and air.
hot_rod
Re: Balancing a large one pipe system
I'll be passing through the area this weekend if I can be of any assistance to you. Mad Dog
Re: Balancing a large one pipe system
Do your main vents first. How long are your mains, and what pipe size?
Re: Balancing a large one pipe system
From what can be seen in the pictures, the near boiler piping is incorrect and no where near enough main venting. That’s where I would start.
EzzyT