Best Of
Re: Modern hot water radiators - what do I need?
The whole purpose of zoning is comfort control, possibly some small energy savings.
So it depends on how you plan on using the rooms. with variable use bedrooms it is nice to have the individual control. Bathroom control is nice for shoulder season, before the main house needs total heat.
At the very least leave options to easily add a zone control down the road.
A delta P type circulator is best for variable zoned systems.
hot_rod
Re: Modern hot water radiators - what do I need?
Do not use a MonoFlo® or diverter tee system with TRVs. And I would caution you with designing a MonoFlo® type system. It may not be as easy as it looks. You will need to understand the flow patterns and pressure drops of each radiator on the zone (loop). You need to then know how to use this selection chart in order to select the pipe sizes and appropriate tee fittings.
Re: How Do I Connect This Wire?
I like Ribs because the little red light tells you it's working.
Re: Plastic 3/4” service entrance on a brass adapter
so I’m not nuts? That’s a little sketchy? 😀
GW
Re: MM-2 Mastertrol and wiring Sensi Wifi touch thermostat to Zone 2
This is a 4 year old post. Better off to start a new one
Re: How Do I Connect This Wire?
If they go up that much a transformer and a RIB will work and nut much more work to install.
Wasn't there another relay like a RIB that had a transformer built into it? Someone posted it last year I think. But maybe the trans is to small for a Nest.
Re: Radiator removal
@Ghynes440 said: Thank you for all that info. I am actually getting it powder coated. There is a company that refinishes radiators near me and that is the process . The other side of the does union with a shut off valve, which was easy to get off. Instead of sweating fittings, I plan on renting a copper pipe crimper.
All good to get copper press fittings that will use a press tool. You should make arrangements to purchase the return bend union. Not sure if that make that in a 3/4" press fitting so you may need to get a 3/4" press x Male adaptor and thread on the 3/4" threaded union bend. Just putting it back as is, with no union, may not be the best idea if you plan on living there for a while.
.
Re: Repair or Replace Aging Heating System with Gas Conversion Gun?
Nothing wrong with replacing an oil burner with a gas power burner, especially on a boiler that is only 10 years old. When was the last time a gas tech cleaned and adjusted the power burner? You need a tech to clean and adjust it. Someone needs to make sure the boiler isn't leaking, it could be at 20 years but 30-50 years is more typical of that type of boiler. Someone needs to fix the leaks in that piping, the fresh water will damage the boiler over time. @EzzyT, @clammy, @JohnNY, and a few others are in your area.
like with an oil burner the boiler, the burner, and the vent all act together to control combustion, it isn't like most atmospheric boilers where the draft hood decouples the boiler from the vent. It needs to be set up y a tech with a combustion analyzer that knows how to use it. It could be that a part is failing on the power burner but that burner looks like it hasn't been touched by a tech in a long time so it should be cleaned and tested by a gas tech regardless of if there is bad part as well.