Best Of
Re: The "equalizer" is mis-named. It does nothing to equalize anything.
I see at least three things or three benefits of the equalizer.
A drip for the header, especially for a drop header. In which case you could call it a drip.
The Hartford loop needs it to work correctly, by providing a vacuum break. Otherwise the boiler's water could just get siphoned out with a wet return leak.
Providing multiple access points to the wet return to the steam side of things allowing gravity to keep the water level more constant throughout the wet return system.
A 'False Water Line' setup uses an additional equalizer to work correctly.
Re: The "equalizer" is mis-named. It does nothing to equalize anything.
Ed my good friend ( @EBEBRATT-Ed I have to specify because there are 3 eds in this thread!) , no one in this thread ever said not to have an equalizer. The only point of it was that it does act to equalize pressure in order to keep water in the boiler while it's running. It makes a nice header drip which I believe the real old books called it.
Re: Wirsbo return manifold leak
I think tightening the black caps, clockwise, turns flow down then off. It pushes the pin and washer, #2 & 5 against the bottom seat.
If you loosen or remove the black cap that valve port will be wide open.
The top of the cap is also a tool that fits over the stem when you remove them. It slides over the valve stem to either adjust, or maybe remove the packing to disassemble and clean the valve.
This is a different brand, but that are all similar insides.

Re: Wirsbo return manifold leak
it looks like a Dahl mini ball valve with an air bleeder
You can turn the silver handle 1/4 turn and replace the white air vent
Wire brush the assembly first to see were it threads apart.
That white vent is probably a hydroscopic type and they have a life expectancy
In all honesty I would just turn off the silver valve and forget about it. Unless the system has been opened up recently, it should be air free and the vent is no longer needed
It is more of a start up vent, when the system is first filled
Be aware old valves can easily break if they have corroded badly , it is a gamble

Re: Heating recommendation for Jackson, WY
Radiant ceilings and or walls is a nice clean, quiet, unobtrusive option. Typically run 110 supply or lower.
I have seen radiant walls with the tube around the bottom 3’ of the wall with a wood wainscot over the tube. No need to worry about picture hangers getting to the tube, with tube down low🫣
If it is a super insulated low heat load, I would not go with a radiant slab, it will rarely feel warm.

Re: [Solved] Taco VT2218 Rattling Sound
That boiler, as per the installation manual should have a full size bypass or primary secondary piping.
The table #1 shows the minimum flow, I doubt that pump, flowing through a 3/4 zone will get you anywhere close to the 14 gpm min. Much less the 18 gpm suggested “normal” rate. Maybe just crank it to its highest speed, although the noise is another issue. There is a reason you keep eating circulators.
In addition I think the boiler oversized by a bit. A heatload calc on three home would determine that. Adding up all the heat emitters is another way to check the boiler output match up.
I think you are headed towards a repipe, maybe even a smaller boiler, although cranking down the red know should lower the boiler firing. Look inside as you adjust, does the flame size decrease? The label on the boiler shows a low end firing of 78,750 btu/hr

Re: [Solved] Taco VT2218 Rattling Sound
My initial thought is you have air in the pipes that hasn't been purged out. How long has it been doing this?
Try taking out the ifc from the circulator if it's in place. Integral flow check valve. That could be vibrating causing the noise.
" On some zones, as you'll see in the video, the pump runs at around 58 watts while pushing only ~6GPM. Does this mean that the pump is undersized?" Not necessarily undersized. Is 6gpm enough to heat that zone. My experience with this 2218 is it runs full power 58 -65 watts until the delta is satisfied and then it backs off significantly to 7-11 watts until Delta exceeds parameters then it goes back to full power. There is not much for middle ground.
Re: Calling Peerless 63-series Owners: A Venting Mystery
@109A_5 " If your boiler runs once an hour that's 24 minutes a day that you are not paying to burn fuel to push air out through a restrictive venting system."
My boiler runs once every two hours on a cold day… and the heat is not wasted. As I found out, the steam goes significantly farther up the risers when I'm using the installed vents.
@ethicalpaul "..a #1 is too small for 80 feet of main"
Agreed, but it's a #1 Maid-o-Mist (or whatever they call the only main vent they sell) + a Gorton #2. It was going to be TWO Gortons but one arrived broken and I ran with just the one for a while.
The size of the main is irrelevant. What matters is how quickly steam can be made to heat it up, and whether the air can be evacuated quickly enough so the process is not impeded.
My next step will be to downfire the boiler from 125 to 88 MBTU and see how that works. I will report in my DIY thread.

Re: System 2000, nearly double the cost of Weil McLain, is it worth it?
On hot water I like to use primary secondary all the time if I can.
Its just my opinion.
Todays boiler in my opinion are not as robust as the older stuff.
Todays boiler hold less water
I like the idea of keeping the heat exchanger happy so the boiler will last as long as possible.
Having a dedicated circ to just do the boiler and near boiler piping makes sense to me. You will always have the correct flow through the hx no matter what is going on elsewhere in the system. Although Pri/sec is not a substitute for low return temp protection in most cases it will provide that as well
Re: System 2000, nearly double the cost of Weil McLain, is it worth it?
We put a System 2000 in an older house with mediocre insulation. It is also our hot water supply.
The summer savings were jaw-dropping. Also, the basement was cooler, so reduced AC cost. This is not applicable to you as you are running electric hot water.
Our winter savings is high too, maybe closer to 50%. But we replaced a WW2 boiler that was failing. And added a fresh air intake. And added 2 zones so can keep the upstairs cooler.
I would highly recommend the fresh air intake. More efficient. And makes the house less drafty. And runs quieter.
»»That 2-year pay-back period quoted is not possible, especially if you are replacing a newish boiler and running electric water.