Best Of
Re: Beckett Oil Burner
I run into a lot more problems related to lack of maintenance and neglect than I do with actual part failures. And at least 90% of the time time I find a failed part it could have been diagnosed and replaced if proper maintenance and troubleshooting was performed.
Things like motors, pumps, couplings, igniters, cad cells usually don't go from working perfectly to not working at all without giving some signs of failing first. A good tech knows how to evaluate the condition of all of the parts of a burner. We don't swap parts out based on "this part is the most likely to fail".
Re: Steam Near Piping Equalizer, EFM S20 to SteamMax
"Why are you replacing the old boiler, is it leaking ?"
A VERY good question.
Re: How Do I Connect This Wire?
Yeah, I think it is a good idea as well.
Chapter 1. How to get a common wire to a Nest
Chapter 2. Taco Switching relay wiring
Chapter 3. How to flare oil line tubing
Chapter 4. All about TIGER LOOPS
@Larry Weingarten has a few books I am sure he could help you avoid some pitfalls
Re: Old fridge
CI does reduce noise but some insulation around the PVC can fix that.
For some strange reason Western, MA is usually ABS and Boston is usually PVC. but MA doesn't generally allow plastic in a commercial building.
Re: Boiler Heats House and Pool
Given the application, would perhaps a possibly too high delta T cause an inordinate amount of moisture on the combustion side of the vessel ? This causing the traditional issue of the by-products of combustionn ie ; sulphur, soot (unburned fuel), and ash adhering to that moisture ? In a extreme condition the weight of such impurities might have ill-effected the positioning of said burner tubes ? As with the preferred modern piping arrangements on the new smaller heat exchangers, maybe a primary, secondary loop piping set-up would alleviate the condition. And excuse this old timer but, isn't that one Grundfos circ pump installed in an incorrect position ? I'll believe so.
Re: 1950's Baseboard
Yes, infiltration is a guess without some type measurement like a blower door score. Both EdTheHeaterMan and bio_guy have good points. Ideally, you could use the heat load calculations and the fuel use calculations to produce the most educated guess that is closest to the true heat load.
Re: Rinnai i120sn condensing boiler flush
boilers work best when they have no leaks and never get the fluid changed unless there is something wrong with that fluid such as old or cooked glycol. You do however want to service the burner, typically annually or every other year. I like to do a burner service after the first heating season personally to make sure everything seems normal. Part of that service in my opinion should be cleaning the burner, flushing the condensate trap, checking the neutralizer if installed, checking the static fill pressure to make sure it is still in range (no leaks) visual inspection of the cabinet, visual inspection of the vent system, visual inspection of the piping system dynamic/static gas pressure checks and a combustion test making adjustments if needed. It looks like a lot of stuff but really cleaning the burner is what will take time, the rest is just making sure everything is still normal or in range, maybe an extra 45 minutes or so tops unless something is off.
Re: 1950's Baseboard
What Edthehearterman wrote about lots of radiation. Fortunately, lots of people are in a good position that way with increasing their insulation and air sealting their homes
I have a problem with some of the other advice. I don't see How can a load calculation can come closer to boiler capacity needed than a determination based on fuel use, boiler efficiency and heating degree days. There is, of course, the problem of calculating in the DHW and cooking contribution if the same fuel is used for those things. With an old house, expecially without an energy rating for the structure, infiltration is a guess. Insulation quality may also be a guess
Re: leaky sink trap connection
I do notice there is a big difference in the compression nuts I get from my plumbing supplier and HD .
Sloppy tolerances and too short threads equals problems snugging them up.