Re: Replacing 17 year old oil fired boiler/need help
You want either a cast iron 3 pass boiler, or a System 2000 by Energy Kinetics. Outdoor reset is useless on an oil fired system that isn't piped for it, with a buffer tank or high mass piping and emitters. Which you dont have. And oil fired boilers use an operating control that doesn't modulate, but fires to limit, whatever that limit may be.
You should have a heat loss calculation done, even though the smallest oil fired boiler is too big for most homes up to 3,000 sq. ft. if you consider a 75K BTU net. That gives you 25 BTU per sq. ft. For 95% of the heating season, that's too much. Unless you see sub zero temperatures often.
Honeywell, Hydrostat, and Beckett all have operating controls with economy settings that work well without using Outdoor Reset.
I don't recommend either of the boilers offered unless there's space or cost issues. They're both pin HX boilers. If space is the concern, Buderus offers a stackable G115 over their indirect water heater, and System 2000 offers the Frontier on a pedestal with their water heater underneath.
HVACNUT
Re: Replacing 17 year old oil fired boiler/need help
Those are decent but low end boilers, they are perfectly fine but not the most efficient. The more efficient boilers that are available in oil are Energy Kinetics, Viessman, and I think certain Peerless models. There may be a few more but the more efficient models have a multi pass HX design of one form or another. You might gain something like 5% to 10% over your old boiler assuming the old and new boilers are set up to not short cycle. If the old boiler was oversized or set up improperly you might gain more efficiency if you size the new boiler more closely to the loss of the house.
The modulating, condensing boilers are only available in gas so the most efficient boilers are not available in oil.
What kind of emitters do you have? Are they cast iron radiators or fin tube baseboard, or convector cabinets or radiant tubing or what?
Re: Furnace vibration
Depends on the type of blower. belt drive or direct drive? misalignment of the belt to sheave. improperly installed sheave. loose mounts, etc.
The classic is the wiring diagram or any papers falling into the squirrel cage.
Re: Furnace vibration
loose mounting, improper assembly of the new parts. loose set screws on the blower bent or damaged blower wheel, disintegrated resilient mounts.
Re: Furnace vibration
Nobody knows until you get to the job. Who know what the other tech did, he could have bent the motor shaft or damaged the blower. What was the original call that made him replace those parts.?
Re: Radiators make my apartment unbearable during winter
The system may be working as designed, it may just be a poor design. If there is no thermostat on your floor how would the system know when to stop heating the third floor ?
It would not surprise me if the seal in the valves were intentionally removed at some point.
Seems you may be stuck between a landlord that just does not care and the law that may just deal with minimum temperatures.
I think that's why the other folks offered other ban-aid type remedies. You are not the first to have this situation.
Re: Radiators make my apartment unbearable during winter
So let's proceed, with cautious optimism but realistic expectations. We are certainly happy to help you as much as we can!!
Re: Radiators make my apartment unbearable during winter
You mentioned two thermostats. Anyway to know which thermostat controls what? You mentioned one tenant on the third floor that's having similar issues. Would probably be somewhat helpful to know if other apartments are having similar issues.
Re: Radiators make my apartment unbearable during winter
The first part, of this last post, might be somewhat inaccurate. Thermostat only knows the temperature of its particular location. For example, if there are 10 rooms and the thermostat is in room number four, it only knows the temperature of room number four. Or in your case, if the thermostat is in the hallway, it only knows the temperature in the hallway and only reacts based on that temperature. Covering your particular radiators would have zero effect on the thermostat.