Options

I have a wet loop seal/water seal right near the end of my steam main. The loop is leaking a bit and i think i should replace. Should i consider using a steam trap or just replace kind for kind?

steam4.jpg steam1.jpg steam3.jpg

Comments

  • Jamie Hall
    Jamie Hall Posts: 27,832

    Just replace it.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • Steamhead
    Steamhead Posts: 18,915

    Agreed. Why add moving parts? The Dead Men didn't need a trap there………..

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,051

    I agree don't mess up something that works. loop seals work well. If you replace piping below the water line copper is ok if it is easier.

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,116

    the crossover trap is only a trap instead of fittngs because it needs to be able to vent air out of the main in to the return.

  • 109A_5
    109A_5 Posts: 4,524

    I'd just repair it. However if you get ambitious you could set up the bottom so it is more serviceable with better clean out capability.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Thanks all, very much appreciate. I will replace and try to make it more serviceable.

  • Steamhead
    Steamhead Posts: 18,915

    @kacrejamReturns , serviceability can be something as simple as a ball-valve boiler drain at the bottom, which would let you flush dirt out.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    PC7060Mad Dog_2kacrejamReturns
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,661
    edited September 18

    Replace. Like for like. If this was my job, I would definitely use copper. Won't accumulate sludge like steel and iron. Use brass in between the copper and the steel

    Mad Dog_2kacrejamReturns
  • Mad Dog_2
    Mad Dog_2 Posts: 8,741

    We always install a Gate Valve with a tee and 3/4" Boiler drain below the water line, whether its the Hartford Loop or a loop seal (install one on each leg) Its the best way to be able to blow out and Muddy Splunck that congeals at all the low points of a Steam system. We will use a ball valve in a pinch, but the Teflon ring inside them dont hold up long in the superhot steam condensate. Mad Dog

    There was an error displaying this embed.
    kacrejamReturns
  • Is it advisable to take apart the loop just to service it …I am pretty sure the two loops on my two pipe system have never been cleaned.

    Thanks.

  • Mad Dog_2
    Mad Dog_2 Posts: 8,741

    If you do them like this, you can power-flush 'em out down the road, and the mud and splunck have no chance to collect. Mad Dog

    kacrejamReturns
  • Jamie Hall
    Jamie Hall Posts: 27,832

    first place, there isn't that much condensate involved, and second place the condensate is basically distilled water. If you have mjor surging or a way overfilled boiler at some point, maybe…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,051

    Or just use two unions. You can take the whole thing off to clean it.

  • I needed to add a third union. Thought to share the horror of the sludge i found during replacement!!

    sludge1.jpg sludge2.jpg
    Mad Dog_2
  • 109A_5
    109A_5 Posts: 4,524
    edited October 4

    Now you see first hand why clean outs help with system performance. Although that is probably many many years of accumulation.

    Thanks for the pictures !!!

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Mad Dog_2