Replacing loop seal on my return?
I have a wet loop seal/water seal right near the end of my steam main. The loop is leaking a bit and i think i should replace. Should i consider using a steam trap or just replace kind for kind?
Comments
-
-
Agreed. Why add moving parts? The Dead Men didn't need a trap there………..
1 -
-
the crossover trap is only a trap instead of fittngs because it needs to be able to vent air out of the main in to the return.
0 -
I'd just repair it. However if you get ambitious you could set up the bottom so it is more serviceable with better clean out capability.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Thanks all, very much appreciate. I will replace and try to make it more serviceable.
0 -
@kacrejamReturns , serviceability can be something as simple as a ball-valve boiler drain at the bottom, which would let you flush dirt out.
3 -
-
We always install a Gate Valve with a tee and 3/4" Boiler drain below the water line, whether its the Hartford Loop or a loop seal (install one on each leg) Its the best way to be able to blow out and Muddy Splunck that congeals at all the low points of a Steam system. We will use a ball valve in a pinch, but the Teflon ring inside them dont hold up long in the superhot steam condensate. Mad Dog
1 -
Is it advisable to take apart the loop just to service it …I am pretty sure the two loops on my two pipe system have never been cleaned.
Thanks.
0 -
If you do them like this, you can power-flush 'em out down the road, and the mud and splunck have no chance to collect. Mad Dog
1 -
first place, there isn't that much condensate involved, and second place the condensate is basically distilled water. If you have mjor surging or a way overfilled boiler at some point, maybe…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Or just use two unions. You can take the whole thing off to clean it.
0 -
I needed to add a third union. Thought to share the horror of the sludge i found during replacement!!
1 -
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements