Replacing loop seal on my return?
I have a wet loop seal/water seal right near the end of my steam main. The loop is leaking a bit and i think i should replace. Should i consider using a steam trap or just replace kind for kind?
    Jamie Hall Posts: 27,832
    Just replace it.
    Steamhead Posts: 18,915
    Agreed. Why add moving parts? The Dead Men didn't need a trap there………..
    Semi-retired
    EBEBRATT-Ed Posts: 21,051
    I agree don't mess up something that works. loop seals work well. If you replace piping below the water line copper is ok if it is easier.
    mattmia2 Posts: 18,113
    the crossover trap is only a trap instead of fittngs because it needs to be able to vent air out of the main in to the return.
    109A_5 Posts: 4,524
    I'd just repair it. However if you get ambitious you could set up the bottom so it is more serviceable with better clean out capability.
  • Thanks all, very much appreciate. I will replace and try to make it more serviceable.
    @kacrejamReturns , serviceability can be something as simple as a ball-valve boiler drain at the bottom, which would let you flush dirt out.
    Semi-retired
    PC7060Mad Dog_2kacrejamReturns
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,661
    edited September 18
    Replace. Like for like. If this was my job, I would definitely use copper. Won't accumulate sludge like steel and iron. Use brass in between the copper and the steel
  • Mad Dog_2
    Mad Dog_2 Posts: 8,741
    We always install a Gate Valve with a tee and 3/4" Boiler drain below the water line, whether its the Hartford Loop or a loop seal (install one on each leg) Its the best way to be able to blow out and Muddy Splunck that congeals at all the low points of a Steam system. We will use a ball valve in a pinch, but the Teflon ring inside them dont hold up long in the superhot steam condensate. Mad Dog
    There was an error displaying this embed.
    kacrejamReturns
  • Is it advisable to take apart the loop just to service it …I am pretty sure the two loops on my two pipe system have never been cleaned.
    Thanks.
  • Mad Dog_2
    If you do them like this, you can power-flush 'em out down the road, and the mud and splunck have no chance to collect. Mad Dog
    kacrejamReturns
    first place, there isn't that much condensate involved, and second place the condensate is basically distilled water. If you have mjor surging or a way overfilled boiler at some point, maybe…
    Or just use two unions. You can take the whole thing off to clean it.
  • I needed to add a third union. Thought to share the horror of the sludge i found during replacement!!
    Mad Dog_2
    109A_5 Posts: 4,524
    edited October 4
    Now you see first hand why clean outs help with system performance. Although that is probably many many years of accumulation.
    Thanks for the pictures !!!
    Mad Dog_2