Replacing loop seal on my return?

Options

I have a wet loop seal/water seal right near the end of my steam main. The loop is leaking a bit and i think i should replace. Should i consider using a steam trap or just replace kind for kind?

steam4.jpg steam1.jpg steam3.jpg

Comments

  • Jamie Hall
    Jamie Hall Posts: 27,936

    Just replace it.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • Steamhead
    Steamhead Posts: 18,993

    Agreed. Why add moving parts? The Dead Men didn't need a trap there………..

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    mattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,268

    I agree don't mess up something that works. loop seals work well. If you replace piping below the water line copper is ok if it is easier.

    mattmia2
  • mattmia2
    mattmia2 Posts: 18,303

    the crossover trap is only a trap instead of fittngs because it needs to be able to vent air out of the main in to the return.

  • 109A_5
    109A_5 Posts: 4,699

    I'd just repair it. However if you get ambitious you could set up the bottom so it is more serviceable with better clean out capability.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Thanks all, very much appreciate. I will replace and try to make it more serviceable.

  • Steamhead
    Steamhead Posts: 18,993

    @kacrejamReturns , serviceability can be something as simple as a ball-valve boiler drain at the bottom, which would let you flush dirt out.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    PC7060Mad Dog_2kacrejamReturns
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,677
    edited September 18

    Replace. Like for like. If this was my job, I would definitely use copper. Won't accumulate sludge like steel and iron. Use brass in between the copper and the steel

    Mad Dog_2kacrejamReturns
  • Mad Dog_2
    Mad Dog_2 Posts: 8,753

    We always install a Gate Valve with a tee and 3/4" Boiler drain below the water line, whether its the Hartford Loop or a loop seal (install one on each leg) Its the best way to be able to blow out and Muddy Splunck that congeals at all the low points of a Steam system. We will use a ball valve in a pinch, but the Teflon ring inside them dont hold up long in the superhot steam condensate. Mad Dog

    There was an error displaying this embed.
    kacrejamReturns
  • Is it advisable to take apart the loop just to service it …I am pretty sure the two loops on my two pipe system have never been cleaned.

    Thanks.

    kacrejamReturns
  • Mad Dog_2
    Mad Dog_2 Posts: 8,753

    If you do them like this, you can power-flush 'em out down the road, and the mud and splunck have no chance to collect. Mad Dog

    kacrejamReturns
  • Jamie Hall
    Jamie Hall Posts: 27,936

    first place, there isn't that much condensate involved, and second place the condensate is basically distilled water. If you have mjor surging or a way overfilled boiler at some point, maybe…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,268

    Or just use two unions. You can take the whole thing off to clean it.

  • I needed to add a third union. Thought to share the horror of the sludge i found during replacement!!

    sludge1.jpg sludge2.jpg
    Mad Dog_2
  • 109A_5
    109A_5 Posts: 4,699
    edited October 4

    Now you see first hand why clean outs help with system performance. Although that is probably many many years of accumulation.

    Thanks for the pictures !!!

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Mad Dog_2
  • Is it advisable to take apart the loop just to service it …I am pretty sure the two loops on my two pipe system have never been cleaned. 

    Thanks.

  • Jamie Hall
    Jamie Hall Posts: 27,936

    If it's easy to do — nice unions or blowoff valves or somesuch, there's no harm. Otherwise… I wouldn't touch it unless I had a very good idea there as a real problem, like significant water hammer on that main…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,268

    That sludge would be completely normal for the amount of time the loop seal has been there. Probably the entire life of the heating system. You should only have to clean the piping below the boiler water line. There shouldn't be any sludge above the water line

    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Posts: 8,753

    Exactly Ed, thats why any chance I get and all new installations get Tees instead of elbows and a 3/4" Boiler drain. A gate valve if possible. This saves hours and hours on flushing and cleaning. Mad Dog

    EBEBRATT-Ed
  • Well this is what i did. Hopefully is better than before. There was indeed a lot of water hammer and essentially sludge all the way to the ceiling. btw, in the background you can see the sealed off old central "district" steam line supply.

    newwaterloop1.jpg
    Mad Dog_2
  • mattmia2
    mattmia2 Posts: 18,303

    make sure where those drips connect together is well below the water line or you can get steam or air flowing through them, closing a vent on a different main before it has finished venting or colliding with water and causing hammer.

    Mad Dog_2
  • mattmia2
    mattmia2 Posts: 18,303

    or is that a water seal between mains where it goes down then back up to a higher return?

  • Mad Dog_2
    Mad Dog_2 Posts: 8,753

    Looks great. As Mattmia says, check your system water level to keep the tees submerged. One other thing.... stick a plug is the bottom of each ball valve when you're all done. We dont wanna see Homeowners stacking boxes, exuberant dogs and curious kids inadvertently opening them. Mad Dog

    EBEBRATT-EdkacrejamReturnsmattmia2PC7060
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,268

    Nice Job.