Replacing loop seal on my return?
I have a wet loop seal/water seal right near the end of my steam main. The loop is leaking a bit and i think i should replace. Should i consider using a steam trap or just replace kind for kind?
Comments
-
-
Agreed. Why add moving parts? The Dead Men didn't need a trap there………..
Co-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
1 -
-
the crossover trap is only a trap instead of fittngs because it needs to be able to vent air out of the main in to the return.
0 -
I'd just repair it. However if you get ambitious you could set up the bottom so it is more serviceable with better clean out capability.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Thanks all, very much appreciate. I will replace and try to make it more serviceable.
0 -
@kacrejamReturns , serviceability can be something as simple as a ball-valve boiler drain at the bottom, which would let you flush dirt out.
Co-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
1