Options
wayneb301
wayneb301 Posts: 123

I need to disconnect the water heater. To make it easier to reconnect, I want to replace the vertical h and c tubings with flexible ones. What is a good point to cut the tubing and adapt to npt? These are 3/4 copper tubing.

Some sections are painted with white or silver coatings. What is the purpose of this coating?

IMG_20260614_145448.jpg
«1

Comments

  • mattmia2
    mattmia2 Posts: 18,100

    either they jus painted everything to make it brighter or there was a fire and the shellacked everything to seal in the odor.

  • wayneb301
    wayneb301 Posts: 123

    so the coating has no mystery. The available flexible s.s. tubing is 18 or 24 inch. What is an optimal point to cut?

    old_diy_guy
  • pecmsg
    pecmsg Posts: 7,549

    why flex?

    mattmia2
  • ChrisJ
    ChrisJ Posts: 17,675

    Because water heaters change in height and flex is quick and easy.

    Mine is hard piped, but you asked why.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    wayneb301GGross
  • hot_rod
    hot_rod Posts: 28,343

    use some coarse sand paper to clean the painted section and confirm it is copper

    Flex connector are available in a few different types and lengths. I prefer the copper

    In seismic areas inspectors want to see flex in water and gas

    IMG_2632.jpeg IMG_2631.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • pecmsg
    pecmsg Posts: 7,549

    If you can’t cut copper tubing maybe you should hire someone!

    Mad Dog_2
  • Larry Weingarten
    Larry Weingarten Posts: 4,194

    Hi, I used to prefer copper, but now I get corrugated stainless connectors. They are easier to work with and don't work harden like copper. I'm hoping you'll replace that valve with a ball valve at the same time. I like to use longer lines (like 24") and form a heat trap with the excess length. In this case I'd cur both lines low and make a 360 loop with the flex.

    Yours, Larry

    Alan (California Radiant) ForbesGGrossethicalpaul
  • mattmia2
    mattmia2 Posts: 18,100

    stainless does work harden. that is wat makes it hard to drill or cut, if you don't take enough of a cut the first pass it work hardens the surface and makes it hard to cut.

  • hot_rod
    hot_rod Posts: 28,343
    edited June 15

    A DIYer might go this solder less route. Sand the copper smooth, no nicks or deep scratches to get the best push connection.

    Maybe add a thermal expansion tanks also. Plumbing codes and tank warranties are starting to demand them.

    Screenshot 2026-06-14 at 5.45.16 PM.png Screenshot 2026-06-14 at 5.45.48 PM.png Screenshot 2026-06-14 at 5.48.53 PM.png

    Heat trapper nipples have been going int water heater tanks for probably 25 years or more.

    Screenshot 2026-06-14 at 5.51.01 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,100

    i hate those heat trap balls. my old water heater had them. every time the pressure in the municipal system would change or a fixture would shut off you'd hear this repeated clicking in the heat traps from the basement as the water sloshed in and out. i still imagine it every time i shut off a faucet or the toilet finishes filling even though i replaced that water heater 7 years ago.

  • hot_rod
    hot_rod Posts: 28,343

    some brands have a soft rubber flapper instead of the plastic ball

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingarten
  • wayneb301
    wayneb301 Posts: 123

    what value does the loop add? is it the same benefit for both the H and C?

    I've seen where the water pipe from the meter rises out of the floor, rather than taking off directly, it goes through a transposed U before going straight up again.

    image.png
  • hot_rod
    hot_rod Posts: 28,343

    Sometimes called

    a thermal trap. Intended to keep the hotter, lighter water from rising into the system. A few ways to accomplish that fuction.

    The special nipples of one of these options with a long flex tube.

    Screenshot 2026-06-15 at 6.44.13 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Larry Weingartenmattmia2
  • ChrisJ
    ChrisJ Posts: 17,675

    On a water meter it's to keep the meter horizontal.

    On a water heater, see what @hot_rod said.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ChrisJ
    ChrisJ Posts: 17,675

    I suspect Larry has found the copper ones tend to become brittle over time in use and will crack, where as the stainless ones do not.

    He's not drilling and tapping them, I'm sure of that.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Larry Weingartenethicalpaul
  • mattmia2
    mattmia2 Posts: 18,100

    that concerns me about stainless gas connectors especially ones to things that vibrate like dryers or some furnaces. i suppose brass is worse. maybe heavier wall copper?

  • ChrisJ
    ChrisJ Posts: 17,675

    Why does it concern you? What I got out of this was that it doesn't seem to happen with stainless.

    If a furnace or dryer is vibrating / shaking enough to fatigue a stainless appliance connector, there's some major issues going on there.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • wayneb301
    wayneb301 Posts: 123

    No, my plot is the city water. The location is the rear of the house, about 18' downstream of the water meter. The pipe from the meter goes under the slab all the way to the rear of the house, turns its way up and out of the slab, sending water to all floors. It's always cold water with no thermal to trap, why the detour?

  • wayneb301
    wayneb301 Posts: 123

    Any comments on the SS flex hose? I think inside of the braided outer layer is some rubber hose.

    https://www.homedepot.com/pep/Everbilt-3-4-in-FIP-x-3-4-in-FIP-x-24-in-Stainless-Steel-Water-Heater-Supply-Line-EBBC-07-24a/206527409?

    image.png
  • mattmia2
    mattmia2 Posts: 18,100

    you're taking like 10# of clothes, picking it up, and dropping it, there is going to be some vibration. since the gas connector is usually in a loop to allow the appliance to be pulled out, there isn't much support to that loop so it is very easy for it to resonate with the vibration from the dryer. the connector is pretty thin and the work hardeing makes it more brittle.

    i know brass hardens with age, try using a compression ferrule that has been sitting around for a decade without annealing it first, i wonder if stainless and copper do the same.(i realize stainless encompasses a wide variety of different alloys)

  • Larry Weingarten
    Larry Weingarten Posts: 4,194

    Hi, A thermal or heat trap would only be used above the water heater to prevent heat loss into the piping. I was responding to the photos of your water heater and it's piping. 😉

    Yours, Larry

  • ChrisJ
    ChrisJ Posts: 17,675

    Besides my opinion that's it's not a problem, I'll add in how many gas leaks and explosions you hear about from work hardening appliance connectors……

    It's not an issue my friend.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • hot_rod
    hot_rod Posts: 28,343

    The copper ones seem to work harden when you try to bend them multiple times, even new ones.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • wayneb301
    wayneb301 Posts: 123
    edited June 16

    Here is an exhaust s.s. pipe that failed after a year's sunlight and then a few bents a month ago -

    Screenshot_2026-06-16-19-52-41-36_40deb401b9ffe8e1df2f1cc5ba480b12.jpg

    So I want to avoid that and use this type of hose shown below:

    image.png

    Both have similar price. Anyone can comment on the preference?

  • mattmia2
    mattmia2 Posts: 18,100

    the plastic inside the braded one is likely to eventually fail due to degradation of the plastic, the stainless will only fail if you make it fatigue and break

    Larry WeingartenIntplm.
  • mattmia2
    mattmia2 Posts: 18,100

    my preference is copper tube and fittings.

    Mad Dog_2
  • Larry Weingarten
    Larry Weingarten Posts: 4,194

    Hi, In addition to what @mattmia2 said about the braided connectors, they have flow restrixtion at both ends and the lining has been known to degrade and lose little bits of itself.
    Yours, Larry

    Intplm.
  • hot_rod
    hot_rod Posts: 28,343

    With the stainless braided WH connectors, the inner lining, depending on the brand, is either EPDM hose or a reinforced PVC core. Either should hold up to the harshest of water conditions.

    I doubt the outer braid is water tight, it is the protection for the thermoplastic or rubber core.

    I agree the fittings on the ends reduces flow somewhat.

    The copper flex flow well and are as durable as the rigid copper tubing in many buildings.

    Most plumbers would replace the flex connectors with a tank replacement. Not often do they line up as WH dimensions change.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • wayneb301
    wayneb301 Posts: 123

    Tank replacement means copper or PEX tubing that is rigid?

  • ChrisJ
    ChrisJ Posts: 17,675
    edited June 17

    My interpretation of braided hoses is the metal braiding is there just to prevent a catastrophic blowout of the hose which used to happen on washing machine hoses. Not too long ago all washing machine hoses were just rubber.

    It won't stop leaks.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • wayneb301
    wayneb301 Posts: 123

    Cutting the copper will leave about 3' horizontal 3/4 pipe unsupported. On the cold inlet it would be about 4' copper left unsupported. There is no rigid fixed structure nearby to clamp these pipes. Although the code allows unsupported section under 6', is it better to provide some support?

    IMG_20260905_150855.jpg
  • mattmia2
    mattmia2 Posts: 18,100
    edited September 5

    you could use clevis hangers and threaded rod or hanger iron but unless the new part is a lot more than you have now or there will be something like a circulator or expansion tank hanging off of it, I wouldn't worry about it.

    wayneb301
  • hot_rod
    hot_rod Posts: 28,343
    IMG_3234.png

    a piece of 1x or 2x4 from the joist above, and a 2 hole copper strap is another simple option

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ChrisJ
    ChrisJ Posts: 17,675

    Depends.

    Every 10 years seems common. But you knew that.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Posts: 7,549

    I’ll still solder with unions.

  • ChrisJ
    ChrisJ Posts: 17,675

    Really the best installation would be welded stainless pipe. It wouldn't have galvanic issues with the tank either.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Posts: 7,549

    I prefer Titanium on fish tanks

  • PC7060
    PC7060 Posts: 1,957
    FLIR0171.jpeg

    Heat trap thermal circulation by creating high / low spots where hot and cold water naturally will stop.

    wayneb301