Heat Pump Refrigerant Uncertainty

Options
2»

Comments

  • charlie123
    charlie123 Member Posts: 38

    I just wanted to thank you guys for your input/ advice, i appreciate it!

  • hot_rod
    hot_rod Member Posts: 27,695

    with the info we have on your home and system, I’m not sure you're a good candidate for an A2whp? Just from a cost and return perspective if nothing else.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • charlie123
    charlie123 Member Posts: 38

    I've decided against A2W and ducted, I need the tank out now and they both sound too involved (and apparently A2W pretty much isn't done here at this time).

    I have someone coming Friday for an actual Manual-J and I'll get quotes on:

    a) A2A (I like the simplicity, the dealer says that a service contract will leave the cleaning to them (though I want to be sure about that), I'm hoping that by avoiding oversizing I'll be comfortable, and the cost should be lower that the 1st 2 above I think), or

    b) a new tank either with-or-without the New Yorker you mentioned. He's familiar with the unit.

    Hopefully I'm looking at this correctly, and if I do the boiler I have a procedure worked out that makes installation of the Midea window inverter AC pretty painless.

  • mattmia2
    mattmia2 Member Posts: 17,177

    i don't know if any of the mini split cassettes are going to solve the cool draft problem even if sized properly. the end consumer isn't the person buying most of them, it is mostly builders and developers and such so price is much higher up on the design criteria than comfort or durability. be very careful with "name brand". there are only a few manufacturers and a whole lot of stuff is just something they bought and slapped their name on.

  • charlie123
    charlie123 Member Posts: 38
    edited May 13

    I would be looking at the hyper-heat versions of Mitsubishi or Fujitsu so I think I'm dealing with the good stuff.

    I understand that the mini splits run at a very low output, so what you described makes sense, how even a slight draft could throw that out of whack/ compete with that airflow.

    I'm guessing that your home, like mine, isn't the tightest envelope, and as such, maybe not a good match for A2A? Or did you work on your home and seal/insulate, and you still don't like the A2A?

    Related question: do baseboard radiators often last far beyond the ~40 year lifespan I've heard of?

    I haven't done any maintenance beyond cleaning the outer cover, would hate to go for a new boiler and find that these also need to be replaced.

  • mattmia2
    mattmia2 Member Posts: 17,177
    edited May 13

    i don't know if there is good stuff, just less bad stuff.

    the air from the cassette is the draft, it isn't very warm so if it has enough velocity when it gets you for you to feel it, it will feel cold

    i would expect fin tube baseboard to last 100+ years unless you physically damage it or have a leak that is letting a lot of makeup water in to the system or have it very overpumped so you have erosion. it is a closed system and it is copper so it is pretty corrosion resistant to begin with and there is no continuous source of oxygen to corrode it.

    charlie123
  • ChrisJ
    ChrisJ Member Posts: 17,477

    We have an LG mini split in our office and never once has the air from it felt cold, even at 0F outside.

    For that matter, I don't think I've ever felt a mini split produce even remotely high velocity air.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • charlie123
    charlie123 Member Posts: 38
    edited May 14

    @EBEBRATT-Ed: one website shows the following as the punchlist for the annual oil service: would you say this is thorough or missing things?

    • New oil filter
    • New oil strainer
    • New burner nozzle
    • Clean and adjust electrodes
    • Clean oil lines
    • Check for proper flue discharge
    • Examine all electricals
    • Start up and run through of system

    *Note: If soot vac is required, additional charges will apply

  • Steamhead
    Steamhead Member Posts: 18,612

    They forgot to include a combustion test, which includes a smoke test. The smoke level should be zero. Burners made in the last 40 years or so should not make any smoke or soot, period. If they do, something is wrong.

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,371

    agree with @Steamhead

    But I don't agree that they should charge extra for cleaning the boiler of any soot.

    Why?

    Because if they screw up the burner adjustment then you have a problem a couple of months later then YOU have to pay for the cleaning.

    and as steamhead mentioned the combustion test is one of the most important things.

  • mattmia2
    mattmia2 Member Posts: 17,177

    isn't inspecting the combustion chamber and cleaning the blower on the burner in there along with cleaning the combustion chamber?

    that isn't a service contract, it is a fixed rate quote. a service contract has some risk that you may need to do more work sometimes. it is like the dealer that the service writer decided the problem with my car was alignment, charged me a lot to do an alignment and didn't fix the problem.

  • ChrisJ
    ChrisJ Member Posts: 17,477

    What is "clean oil lines" ?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 17,177

    if i read that again it looks more like some ai skimming rather than someone's service contract. some of that stuff is hard and unnecessary and other stuff is not how the trade would describe it and stuff that is more important and easier than the hard stuff in the list is missing

  • mattmia2
    mattmia2 Member Posts: 17,177

    testing the safeties is also missing there

  • ChrisJ
    ChrisJ Member Posts: 17,477

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,371

    The Op stated that his service company is in and out in 1/2 hour.

    They are basically doing a nozzle and a filter and that is all.

  • charlie123
    charlie123 Member Posts: 38

    I would say 1/2 hour is the norm, and that service list came from an hvac dealers website, thx.

  • charlie123
    charlie123 Member Posts: 38

    Hey, hoping you don't mind a few more questions.

    When a Biasi B-3 was consider in the past it was ruled out because it was too deep, would have to be oriented sideways and not sure that was an option.

    I'm wondering if part of the issue was due to the vent being on the back, but I also read that it uses 'atmospheric venting' (not sure what this is). I'm wondering if in general, boilers with rear vents can be easily adapted so that the vent comes out the top the way it does on my Utica? The NY'er appears to have a rear vent as well.

    Current rough measurements: are 7 1/4, 26, 35 (wall to boiler rear, wall to boiler front, wall to burner front, with ~42" between the front of the burner and a work bench.

    Thanks

  • Steamhead
    Steamhead Member Posts: 18,612

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • mattmia2
    mattmia2 Member Posts: 17,177

    there are lots of ci oil boilers out there, look around for one that will fit and has enough clearance for service and to not set things on fire

  • charlie123
    charlie123 Member Posts: 38

    Hopefully the New Yorker CI-HGS-74E that Steamhead mentioned can be adapted. One dealer wasn't inclined to install that (he likes Buderus, Veissman, etc) but when he realized it was a 3-pass he said he'd look into it.

  • winnie
    winnie Member Posts: 73

    IMHO the above is a key point for any sort of air to air installation.

    My house has both minisplits and steam oil heat. In regions of my house where I don't have direct air flow from the minisplit 'heads', I can't tell the difference, for example the hallway that is heated by whatever escapes from the bedroosm.

    But in regions right next to the airflow the difference in comfort is noticeable. The radiant heat from a steam radiator is very nice, the quality of the airflow from the 'head' is variable. Depending on the minisplit modulation level they can blow anything from nicely warm are to barely tepid air, and blowing tepid air in the winter is not a win.

    IMHO if you can design your system so that it doesn't directly blow tepid air on the room occupants in normal use, you will probably be fine with an air-air system.

    And to your original question about trying to suss out what refrigerant to use? I would not put much if any effort into that question. Use whatever equipment is currently available and put your mental effort into getting a good equipment size and layout (or put your mental effort into finding a contractor who will do so). Refrigerant is just too far down the list of things to optimize.

    -Jonathan

    hot_rodIronman
  • charlie123
    charlie123 Member Posts: 38

    Thanks Jonathan,

    It's being suggested that rather than installing multiple independent minisplits (which I believe is the most efficient), I should put in a ducted multi-split unit in my unconditioned attic.

    I had always heard that if you were going to locate an air handler in an unconditioned attic, it needs to be in a sealed and insulated box, but I'm being told that the ducts are already insulated.

    It would seem to me that, with the issue with tepid air that you all describe, having the unit further challenged by being in a very cold or hot attic would be a bad idea.

    Thanks again

  • winnie
    winnie Member Posts: 73

    IMHO do not put an air handler or ductwork in an unconditioned attic.

    Yes, the ducts are insulated, but they are not well insulated, and the installation has to be perfect to prevent air leaks from/to the attic.

    I have multiple independent minisplits, and I like the result. The downside is that I have 5 separate boxes outside of my house.

  • ChrisJ
    ChrisJ Member Posts: 17,477

    I installed most of my ductwork and air handler in an unconditioned attic.

    It was the best place, overall for my situation and all ductwork has R8 insulation. @winnie is correct that sealing all of the ductwork has to be good.

    Minisplits have their own set of issues as well though. Everything is a compromise.

    They work but keeping them clean is far from fun, especially with multiple heads to clean. It's also been my experience that they're less than great at dehumidifying. I'm sure someone will reply and say that's because they're oversized, but I'm not entirely buying that. I'm sure it aggravates the problem but they don't seem to run as cold as a window unit or split unit even on the lowest fan speed. They also never shut the fan off.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,177

    The mini splits can modulate but they probably do not do a great job of figuring out that they should modulate down and run longer cycles to get better dehumidification.

    GGross
  • pecmsg
    pecmsg Member Posts: 7,172

    minis suck at dehumidification at less then 60% load!

  • ChrisJ
    ChrisJ Member Posts: 17,477

    I currently have the one in our office set on fan #1. I always have it on manual fan speed.

    It still doesn't do great, I don't think they are programmed to run the evap cold enough.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ratio
    ratio Member Posts: 4,256

    I was told by Magic Mike (The world's best technician. Just ask him, he'll be happy to tell you about it!) that mini splits need to control the fan speed to operate at their best. It seemed reasonable, so I've been leaving them set on auto ever since.

  • ChrisJ
    ChrisJ Member Posts: 17,477

    I use auto in the winter, but in the summer I prefer to control this one.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • charlie123
    charlie123 Member Posts: 38
    edited May 21

    Starting to think that a new boiler and tank with window AC is the way to go. Not sure the heat-pumps are worth the bother.

    For those who need to clean wall-units (spraying coils and removing blower wheel, no pets), I'm wondering how often that's typically needed? I hear anything from every 6 months to a couple of years.

    If anyone knows of a low output, cast iron, triple-pass boiler with top venting where the burner only extends ~35" from the back wall, suggestions are welcome.

    The New Yorker CI-HGS-74E was recommended, not sure it converts to top-venting though.

    Thanks for the comments.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,371

    A lot of people rail against pin boilers but the same people still install them on their jobs. I see nothing wrong with them.

    The Weil McLain has been around for many years and seems to hold up pretty well.

    mattmia2
  • mattmia2
    mattmia2 Member Posts: 17,177

    look at the wm, peerless, dunkirk, and burnham catalogs for something the right shape to fit your space. don't forget there will be clearances needed to service the burner and clean the hx and may be clearances to combustibles on various sides.