Heat Pump Refrigerant Uncertainty
Comments
-
I just wanted to thank you guys for your input/ advice, i appreciate it!
0 -
with the info we have on your home and system, I’m not sure you're a good candidate for an A2whp? Just from a cost and return perspective if nothing else.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I've decided against A2W and ducted, I need the tank out now and they both sound too involved (and apparently A2W pretty much isn't done here at this time).
I have someone coming Friday for an actual Manual-J and I'll get quotes on:
a) A2A (I like the simplicity, the dealer says that a service contract will leave the cleaning to them (though I want to be sure about that), I'm hoping that by avoiding oversizing I'll be comfortable, and the cost should be lower that the 1st 2 above I think), or
b) a new tank either with-or-without the New Yorker you mentioned. He's familiar with the unit.
Hopefully I'm looking at this correctly, and if I do the boiler I have a procedure worked out that makes installation of the Midea window inverter AC pretty painless.
0 -
i don't know if any of the mini split cassettes are going to solve the cool draft problem even if sized properly. the end consumer isn't the person buying most of them, it is mostly builders and developers and such so price is much higher up on the design criteria than comfort or durability. be very careful with "name brand". there are only a few manufacturers and a whole lot of stuff is just something they bought and slapped their name on.
0 -
I would be looking at the hyper-heat versions of Mitsubishi or Fujitsu so I think I'm dealing with the good stuff.
I understand that the mini splits run at a very low output, so what you described makes sense, how even a slight draft could throw that out of whack/ compete with that airflow.
I'm guessing that your home, like mine, isn't the tightest envelope, and as such, maybe not a good match for A2A? Or did you work on your home and seal/insulate, and you still don't like the A2A?
Related question: do baseboard radiators often last far beyond the ~40 year lifespan I've heard of?
I haven't done any maintenance beyond cleaning the outer cover, would hate to go for a new boiler and find that these also need to be replaced.
0 -
i don't know if there is good stuff, just less bad stuff.
the air from the cassette is the draft, it isn't very warm so if it has enough velocity when it gets you for you to feel it, it will feel cold
i would expect fin tube baseboard to last 100+ years unless you physically damage it or have a leak that is letting a lot of makeup water in to the system or have it very overpumped so you have erosion. it is a closed system and it is copper so it is pretty corrosion resistant to begin with and there is no continuous source of oxygen to corrode it.
1 -
We have an LG mini split in our office and never once has the air from it felt cold, even at 0F outside.
For that matter, I don't think I've ever felt a mini split produce even remotely high velocity air.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@EBEBRATT-Ed: one website shows the following as the punchlist for the annual oil service: would you say this is thorough or missing things?
New oil filterNew oil strainerNew burner nozzleClean and adjust electrodesClean oil linesCheck for proper flue dischargeExamine all electricalsStart up and run through of system
*Note: If soot vac is required, additional charges will apply0 -
They forgot to include a combustion test, which includes a smoke test. The smoke level should be zero. Burners made in the last 40 years or so should not make any smoke or soot, period. If they do, something is wrong.
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
agree with @Steamhead
But I don't agree that they should charge extra for cleaning the boiler of any soot.
Why?
Because if they screw up the burner adjustment then you have a problem a couple of months later then YOU have to pay for the cleaning.
and as steamhead mentioned the combustion test is one of the most important things.
0 -
isn't inspecting the combustion chamber and cleaning the blower on the burner in there along with cleaning the combustion chamber?
that isn't a service contract, it is a fixed rate quote. a service contract has some risk that you may need to do more work sometimes. it is like the dealer that the service writer decided the problem with my car was alignment, charged me a lot to do an alignment and didn't fix the problem.
0 -
-
if i read that again it looks more like some ai skimming rather than someone's service contract. some of that stuff is hard and unnecessary and other stuff is not how the trade would describe it and stuff that is more important and easier than the hard stuff in the list is missing
0 -
testing the safeties is also missing there
0 -
Maybe that's under "Examine all electricals"
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The Op stated that his service company is in and out in 1/2 hour.
They are basically doing a nozzle and a filter and that is all.
0 -
I would say 1/2 hour is the norm, and that service list came from an hvac dealers website, thx.
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements