near toilet floor constantly wet
azward
azward Member Posts: 20
the bathroom floor behind the toilet is constantly wet along the tile joints. what could be leaking?
  • HomerJSmith
    HomerJSmith Member Posts: 2,762
    More pictures all around toilet.
    mattmia2 Member Posts: 16,167
    it could be the seal to the closet flange or it could be the tank to bowel gasket or the washers on the tank bolts. or the supply line. or something in the wall. you need to get back there and look at where it is coming from.
    Jamie Hall Member Posts: 27,088
    There's a commonly overlooked source: condensation. If the relative humidity is high enough — unlikely in the winter, but not impossible — condensation can form on the tank from the cold water coming in and then drip down on the floor. I've had that happen.
    mattmia2ethicalpaul
    in winter the incoming water is the coldest so if you get a warm day or otherwise suddenly get a lot of humidity, the water is still cold but the humidity shoots up any at least here you get the most sweating of the tank in the winter and early spring
  • ChrisJ
    ChrisJ Member Posts: 17,194
    Specific Men / Boys using the toilet a lot?
    HomerJSmithazward
  • pumpcontrolguy
    pumpcontrolguy Member Posts: 17
    I've replaced many dozens of toilets in a former life. Seeing that moisture pattern and assuming you already ruled out the supply line leaking
    -Tank to bowl ring gasket or bolt gaskets leaking
    -condensation around tank dripping down, generally more common in summer in spaces without AC
    -leaking wax ring and water seeping under tiles but coming up through grout joints
    bjohnhyRTW
  • Grallert
    Grallert Member Posts: 1,083
    Is the house on a slab? Looks like an under floor leak. It looks dry around the toilet .
  • Intplm.
    Intplm. Member Posts: 2,948
    @azward "What could be leaking?"
    The packing nut on the service valve.
    The closet riser/supply tube suppling water to the toilet.
    The tank to bowl bolts are loose.
    The tank to bowl washers used with the same bolts are worn out.
    The flush valve spud gasket between the tank and bowl.
    Condensation build up on the toilet.
    The thoughts above can commonly be checked visually.
    Below are not usually visible.
    The next is the wax gasket that cannot be seen between the floor and the toilet.
    Rarely the toilet could be cracked. I mention this here because a crack is not always visible.
    If any of the above are not found, a rebuild with the above parts should eliminate the leak.
    As what @HomerJSmith says above. "More pictures all-around."
  • ChrisJ
    @azward take pictures of the underside of the tank where it bolts to the bowl. Take pictures of both sides, clearly showing the bolts sticking out.
  • HomerJSmith
    edited February 3
    Do the wet finger test. What's the wet finger test, you ask? Run a dry finger under the tank where it meets the bowel. If your finger comes up wet, you're honing in on the source of your concern.
    pecmsg Member Posts: 6,961
    connection from the storage tank to the toilet
    Water inlet
    You need to look under the tank
  • azward
    Thanks all your inputs.
    Will take more photos around the toilet.
    The humidity stays around 36% so it's not too wet. Will do the finger test.
  • ChrisJ
    edited February 5
    36% at 70F is a dew point of around 40, so even really cold water probably wouldn't cause much if any condensation.
    I'd take pictures with my phone my self. I don't like reaching under toilets blindly. 😉
    mattmia2bjohnhy
  • pumpcontrolguy
    A piece of paper towel works great in areas you can't see well, it's immediately obvious if you've hit moisture with it
    mattmia2HomerJSmithPC7060
  • PC7060
    PC7060 Member Posts: 1,765
    agree although I use toilet papers, readily available and show wet spots quicker.