Another glitch on a steam install

Options
GW
GW Member Posts: 5,065

I was out this house today casing out air conditioning. The people just bought the home. A very nice home. I’m curious how this big old 9 section boiler wil gets its steam to the system

the header is supposed to be 3 inch, they bullheaded the 2 inch into one 2 inch connector, into the mains

IMG_9308.jpeg
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com

Comments

  • pecmsg
    pecmsg Member Posts: 6,290

    not your job

    Not your problem

    wuyuzizi000
  • Ironman
    Ironman Member Posts: 7,730

    It’s also piped wrong with the main tapped between the risers.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2wuyuzizi000
  • Jamie Hall
    Jamie Hall Member Posts: 26,183

    If it works without problems, it serves to show how forgiving steam can be…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    wuyuzizi000
  • mattmia2
    mattmia2 Member Posts: 13,502

    "works" can have a lot of meanings. I wonder how close the output of that boiler is to the actual connected edr

    wuyuzizi000Ironman
  • GW
    GW Member Posts: 5,065

    yes and yes. It seems like if I goof something up, the demons and vipers are biting at my heels. But when somebody else does a goofy job, everything works out just fine.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000IronmanEdTheHeaterMan
  • mattmia2
    mattmia2 Member Posts: 13,502

    Maybe you can figure out a way to tell them you know steam and if they have problems to call you.

    GWwuyuzizi000
  • mattmia2
    mattmia2 Member Posts: 13,502

    Are those risers bushed down at the outlets of the boiler?

    wuyuzizi000
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,240

    Can't see how the equalizer is tied in. @GW

    The hacks get away with it all the time. Anything over 2" black is a foreign object to them. I thought I was the only one. If I had installed it like that the boiler would have likely blown up on start up.

    GWIntplm.wuyuzizi000Ironman
  • ChrisJ
    ChrisJ Member Posts: 16,851

    Make sure they know you do steam.

    That way when it's leaking in the near future you'll get the call.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    GWmattmia2delcrossv
  • mattmia2
    mattmia2 Member Posts: 13,502
    edited July 23

    Looks like a reducer or bushing and tee at the end of the header to make sure no condensate or carryover goes in to the equalizer…

  • GW
    GW Member Posts: 5,065

    the header is full 2 inch, all the way to the 90 that drops to the equalizer. It’s turned 45 but it is not trapping any water.

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000
  • Steamhead
    Steamhead Member Posts: 17,892

    No. That's a Burnham V-89, and the outlets are tapped 2-inch.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2Intplm.wuyuzizi000
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,240

    It's butt ugly.

    wuyuzizi000delcrossvGW