Another glitch on a steam install
GW
GW Member Posts: 5,184
I was out this house today casing out air conditioning. The people just bought the home. A very nice home. I’m curious how this big old 9 section boiler wil gets its steam to the system
the header is supposed to be 3 inch, they bullheaded the 2 inch into one 2 inch connector, into the mains
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    pecmsg Member Posts: 7,039
    not your job
    Not your problem
    wuyuzizi000
  • Ironman
    Ironman Member Posts: 7,903
    It’s also piped wrong with the main tapped between the risers.
    Bob Boan
    mattmia2wuyuzizi000
    Jamie Hall Member Posts: 27,319
    If it works without problems, it serves to show how forgiving steam can be…
    wuyuzizi000CLamb
    mattmia2 Member Posts: 16,673
    "works" can have a lot of meanings. I wonder how close the output of that boiler is to the actual connected edr
    wuyuzizi000Ironman
  • GW
    yes and yes. It seems like if I goof something up, the demons and vipers are biting at my heels. But when somebody else does a goofy job, everything works out just fine.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000IronmanEdTheHeaterMan
    Maybe you can figure out a way to tell them you know steam and if they have problems to call you.
    GWwuyuzizi000
    Are those risers bushed down at the outlets of the boiler?
    wuyuzizi000
    EBEBRATT-Ed Member Posts: 20,145
    Can't see how the equalizer is tied in. @GW
    The hacks get away with it all the time. Anything over 2" black is a foreign object to them. I thought I was the only one. If I had installed it like that the boiler would have likely blown up on start up.
    GWIntplm.wuyuzizi000Ironman
  • ChrisJ
    ChrisJ Member Posts: 17,350
    Make sure they know you do steam.
    That way when it's leaking in the near future you'll get the call.
    GWmattmia2delcrossv
    edited July 2025
    Looks like a reducer or bushing and tee at the end of the header to make sure no condensate or carryover goes in to the equalizer…
  • GW
    the header is full 2 inch, all the way to the 90 that drops to the equalizer. It’s turned 45 but it is not trapping any water.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000
    Steamhead Member Posts: 18,467
    No. That's a Burnham V-89, and the outlets are tapped 2-inch.
    Consulting
    mattmia2Intplm.wuyuzizi000
    It's butt ugly.
    wuyuzizi000delcrossvGW