Well characteristics and well pumps
Hi, I think there are controls that sense when the current draw on the pump drops, meaning it's pulling air, and then activates a time delay to let the well recharge. Here's a link that gives a bit of a description: https://inspectapedia.com/plumbing/Pump_Protection_Switches.php Might something like that work for you?
Yours, Larry1 -
Some of the gadgets mentioned above may do it for you. However, a very simple float switch will also do it. Not just one of those flip-flop jobs, but there are switches made (come to think of it, that was some time ago...) including some ultrasonic ones which don't have to be in the well with a greater distance between off and on.
You should set them, whatever you use, so that there is at least a 5 minute off time between pump runs.
And a word of caution: if this is a submersible pump -- which at the depths you mention, I expect it is (by the way -- static at 260, pump at 260 just isn't right) -- it will have a short and unhappy life if it is allowed to run dry. They are water cooled -- but more to the point, water lubricated.
Now. If your well recharges at a steady 100 gallons per hour, you are doing it, and your pump, no favours by trying to get more water out of it. You and your well will both be much happier in the long run if you install a smaller pump better matched to the well, and let it run steadily. I know it's sometimes hard to accept, but in many years of playing with and drilling wells, I can assure you: if the steady yield is x -- in this case 100 gph -- you simply can't get more water out of it by pumping it harder. That never works. You have a well which will give you around 2400 gallons per day, and -- if pumped at a steady rate to give you that will probably do it for many years. Bluntly, if that's not enough for your irrigation scheme, you need another well, or a much deeper one (which may or may not have more yield) -- not a bigger pump.Br. Jamie, osb
A self sensing control would be my choice. Vary the pump speed to what the well can provide.
Most well levels vary from dry to wet season, or when others on the aquifer are also drawing heavily. As such, static level drops and pump performance also drops as the pump has a higher lift.
Pulling a lot of gpm can change other wells in the area, even miles away.
A neighbor put in a pond for livestock water, kept his well pump running for weeks to fill. Many of the neighbors, myself included had to drop our pumps lower to keep in water.
That seems like a tight range well at 280, pump at 260? Any well records available to show if it was tested when drilled?Bob "hot rod" Rohr
Well report says 300’, drilled 1994, yield test was 4.5gpm for one hour. Casing is 30’. I may have used the wrong term so I’ll list the facts as it is today.
Plumb bob measured well depth at 280’.
Pump hangs at 260’ down.
Water line after recharging all night is 20 below well top.
Old pump 1/2hp was delivering 2gpm and curve confirms that.
New 3/4hp gives 11gpm at rush, average 8.
Well runs dry at 360 gallons at average 8gpm.
I’ll buy the speed drive and set it to what delivers 4gpm. That will more than do what I need. I’m irrigating 1.3 acres and mostly lawn. I do half the zones one day and half the next. It takes just over 1000 gallons per day so I fill while the zones are running to add just a bit to what I could do. I just didn’t want to wait 8+ hours to fill the tank, that’s a lot of power to use too. The 1/2hp pump was just too small and the 3/4hp is too big clearly.
There is a clear bodied inline filter on the cistern fill from the well and I can easily tell when I’m getting low in the well because it gets darker when it’s low.
Since this is the first year we have owned this property we have no previous years or winter numbers to compare too and it’s not used in the winter anyway. Thanks for the input!Just a guy running some pipes.0 -
What are you watering that you need almost 400 gals a day?0
Good grief. We use around 200 gallons per day; 1 acre "locally grown" veggies and some horses.
Oh well.
On the power. The electricity cost of pumping 1,000 gallons of water at a slow, constant rate -- such as around 2 gpm -- will actually be less than pumping at a higher rate with a bigger pump for less time. Why? Because you are paying for the power to lift the water, and if you don't draw the well down so much you will use less power.
A well tested for 1 hour will not necessarily yield 4 gpm over any longer run. A true well test runs for at least 24 hours, and is often around half the one hour test.
I would point out that the colour change of the water indicates that yes, you are drawing down too far -- and, worse, indicates that you are overstressing that well.
Put the 1/2 horse pump back in, if you haven't junked it, and put a float switch on the cistern. Set the switch so that you some reasonable draw -- say 2 feet or so -- turn the thing on and let it go. Be happy with 2 gpm.
And welcome to country living. Water is your most precious resource; don't abuse it.Br. Jamie, osb
Way too much water usage!Jamie Hall said:Good grief.
And welcome to country living. Water is your most precious resource; don't abuse it.0 -
These don’t even show the side of the house on either side. All grass and beds. I have zero info on the domestic well. It’s behind the garage. Each zone gets 20 min every other day. Beds only 10 min. Remodel starts in the spring and we are adding a small ‘orchard’ of fruit trees so some grass goes. That’s Mt Hope bay across the street.
Well, one person’s waste is another person’s yard. It’s a nice area and a prominent street. It has to stay nice to maintain the home’s only real appeal at the moment. The whole property needs help and updating.pecmsg said:
Sorry but I cant justify wasting resources like that.
This summer has been extremely dry on the east end. I let my lawn go brown rather then waste all that water. It comes back when it finally rains, Only so much available on Long Island.Just a guy running some pipes.0 -
I had a similar issue recently with a rental property. To make it simple, I just installed a flow restrictor on the 1/2HP pump outlet to limit flow to 3 GPM. Easy peasy, $40, all done. No more sediment or dry well0
We live in a small town in RI now. The area we are in is maybe 10,000 population and we are out in the country a bit. Right on Mt Hope bay. My front porch looks at Fall River. I’m officially a New Englander now.hot_rod said:
Can or are you collecting rain water? I see Utah now allows a 2500 gallon tanks per home. With drip or root zone irrigation that would go a long ways for a vegetable garden.
I’ll have to do this tomorrow until I can get a pump speed control..GroundUp said:
Yep, I knew you are a back easterner now. We are actually trying to get back to UtahTimco said:We live in a small town in RI now. The area we are in is maybe 10,000 population and we are out in the country a bit. Right on Mt Hope bay. My front porch looks at Fall River. I’m officially a New Englander now.
hot_rod said:Can or are you collecting rain water? I see Utah now allows a 2500 gallon tanks per home. With drip or root zone irrigation that would go a long ways for a vegetable garden.
@Timco , I see radiators in the garage picAll Steamed Up, Inc.
Consulting0 -
There are many things I miss about Utah. We lived in SLC and we couldn’t take the mayor and city council’s agendas and the politics any longer. Crime is insane and property values are crazy. Add a growing homeless population to that and the smog and it was time to get out. We did very well on our place and the rentals.hot_rod said:
So what kind of heat does this place have?All Steamed Up, Inc.
Consulting0 -
Oil fired hot water. I’m changing to LP high efficiency with a backup oil system. Currently all copper fin BB but main floor will be warm floors and maybe some rads on 2nd floor. There’s also three AC zones.Steamhead said:
@Timco . Rhode Island? With that kind of water use I had assumed at least Kansas. There is no way you can justify irrigating on that level in New England -- except to keep up with the Joneses. I'm completely with @pecmsg on this one.
On the well. I've told you what you need to do. No sympathy if getting a speed control doesn't work.Br. Jamie, osb
Well,
Apparently it's typical for a golf course to use 300,000 gallons per day wasted on grass.
You need a flow control or put in the proper size of submersible pump. Just like with circulators they need properly matched to their load. Grundfos offers constant pressure systems but flow is not an option as far as I know. I vote to stop irrigating so much.Cost is what you spend , value is what you get.
cell # 413-841-6726
All points understood. I know what the yard needs to look like we want it to. I’m confident the speed control is the answer. For now I added a ball valve and choked it back to 5 gpm. Water stays perfectly clear. I appreciate your advise.Jamie Hall said:
On the well. I've told you what you need to do. No sympathy if getting a speed control doesn't work.Just a guy running some pipes.0 -
I had two options. 1/2hp @ 2gpm or 3/4hp @ 8gpm. I need about 4gpm. Not sure why so many are offended by irrigating 20 min every other day. I’m not keeping up with the Jones’s, I am the Jones’s when it comes to the yard. It’s important to me and I’ve spent cash on the jet pump and lawn this year.Charlie from wmass said:
So your point of view is, if the OP paid the government for a permit, it would magically change everything? But he's still using the same exact water, for the same exact thing. Literally nothing changes on his part.pecmsg said:
Golf courses are registered and permitted for there use.ChrisJ said:Well,
The OP's not a Golf Course
That's a bit strange.
So someone believes I need a permit to pull up to 1500 gallons a day from my own well? I’ve not been given any documents restricting what I can pull and I have never been billed. I don’t even think there are restrictions to adding 5 wells if I pay to have them drilled.pecmsg said:
The OP's not a Golf CourseJust a guy running some pipes.0 -
We have 2.2 acres. Mostly planted in fescue?? or Buffalo grass.
Once started no water at all. Green now because of rain. Another 2 weeks it may be browning.
My theory is the more water the more mowing needed.
Also weaker root system near the surface.
Whatever mix of grass we have has to go down deep to stay alive. This is how prairie grasses survived here.
Drip hose for anything that needs more than rain.1 -
@Timco . It might pay you to check with your local health department, if the well is not known to be permitted. Most districts in New England require a permit for an active well. It's usually not a big problem (though if you are connected to public water it is a big problem), but helps everyone to keep track of -- and not overuse -- what is in truth a limited resource.Br. Jamie, osb
I enjoy the yard work. I mow weekly all year and do it myself. I keep it as perfect as I can.JUGHNE said:
Drip hose for anything that needs more than rain.Just a guy running some pipes.0 -
The health department division of wells sent me my well record for the irrigation well. The domestic well was drilled just before there were any requirements and I was told to contact a well company if we have any issues. When I spoke to them they made no comment about permits or ongoing permitting or documents or inspections. Water was tested just before we bought. High iron but we soften. New England is lacking in several things but I don’t think ground water is one of them.Jamie Hall said:
> @ChrisJ said:
> (Quote)
No my point is the golf course is regulated. They can only pump X amount of gallons a year.
You’re the one that brought up a Golf Course0 -
> @Timco said:
> So someone believes I need a permit to pull up to 1500 gallons a day from my own well? I’ve not been given any documents restricting what I can pull and I have never been billed. I don’t even think there are restrictions to adding 5 wells if I pay to have them drilled. (Quote)
In certain jurisdictions yes water is considered a mineral just like gold silver and lead.
In Colorado you need to contact whoever owns the water rights to put a well on your property0 -
like ground up said install a flow limiter after the presure switch and relif valve not on the pump outlet in case it clogs they make them stainless with a changeable rubber restrictor is this a jet pump or submersible if its a sub put on a pump tech. in ct they required me to install a water meter on a private well to see how much water was be discharged to the septic system in a church0
There’s just a small difference between west of the Rockies and East. I have no specific water rights and there are no limits.pecmsg said:
In Colorado you need to contact whoever owns the water rights to put a well on your propertyJust a guy running some pipes.0 -
> @Timco said:
> There’s just a small difference between west of the Rockies and East. I have no specific water rights and there are no limits. (Quote)
True but why wast it...........because you can?
We’re handcuffed with energy regulations yet you can waste 1mil BTU’s Heating your pool with zero government regulation, is it right NO but it’s legal?0 -
Define waste! My lawn being watered and me using 1200-1500 gal per day is not having any adverse effect on anyone lol. I can see you’re an anti-lawner type but I have over an acre of green lawn and I’m not ashamed to keep it that way. Do you think that the aquifer I pull from is one sealed pool that will run dry sometime? You won’t shame me into letting my lawn go brown. To me that’s the hillbilly approach. Too lazy to mow weekly? Don’t have any pride in your home’s appearance? Well water is not an issue in southern RI. Now if I can just find that speed controller online. That’s why I started this thread, not to fight about what constitutes waste.pecmsg said:
We’re handcuffed with energy regulations yet you can waste 1mil BTU’s Heating your pool with zero government regulation, is it right NO but it’s legal?Just a guy running some pipes.1
- 110 Chimneys & Flues
- 982 Plumbing
- 387 Solar