New Crown Steam Boiler
coolfx35
Member Posts: 77
So I have my Steam Boiler installed yesterday (Crown Steam Boiler with 172k BTU), replacing my old Burnham boiler. (170k BTU)
https://www.ambientfloorheat.com/products/crown-boiler-bsi-series-bermuda-model-bsi172-gas-steam-boiler
The installation went fine, took a day, 2-3 people, but last night when the tech left, i saw my Sight Glass was doing something really weird, 1st, it's dirty, 2nd, it fluctuates up and down, I recorded a video and uploaded it to youtube. Please let me know what you think the issue is.
https://www.youtube.com/watch?v=mVVTKy8nsLA
Last night, there were some pipe banging as well. I called back the tech, and he said he is coming tomorrow to take a look, maybe the boiler is dirty and needs some cleaning. It also stops and restarts every few minutes. is that normal? also making noises as if the low water cutoff kicks in and stop the boiler from running, then restarts when water came back, he said it's normal with new boiler now doing intermittent check (green light). I am concerned. This guy seems knowledgeable with steam, he said he did a lot of steam boilers and water heat boilers, and he did all my AC and water heater without issues.
I asked him if it's dangerous to use the heat today, he said no. but i turned it off anyway. It's kind of cold today. So I am using electric heat.
Any comments would be greatly appreciated.
https://www.youtube.com/watch?v=mVVTKy8nsLALast night, there were some pipe banging as well. I called back the tech, and he said he is coming tomorrow to take a look, maybe the boiler is dirty and needs some cleaning. It also stops and restarts every few minutes. is that normal? also making noises as if the low water cutoff kicks in and stop the boiler from running, then restarts when water came back, he said it's normal with new boiler now doing intermittent check (green light). I am concerned. This guy seems knowledgeable with steam, he said he did a lot of steam boilers and water heat boilers, and he did all my AC and water heater without issues.
New boilers need to be skimmed for hours until all/most of the oil is gone from the boiler0
he definitely didn't do that. I will make sure he does that tomorrow, but do you think it's dangerous to use the heat today? I don't want to crack the boiler if there's no water left.0
Yes skimming, this is standard procedure and they should have said it upfront and in response to you.
I hate to ask, did you call and get @EzzyT to do the work?
Also how was the new one sized?0 -
The grey box on the upper right....clear cover.....what are the numbers he set things at.
Just curious as he does a lot of steam.
This will not affect your problem for the moment.
Boiler needs skimmed.
Skimming might be mentioned in the book.
How about more pictures of the piping around the boiler?
Back up for the full view.0 -
I would keep the heat off. The surge seems to be extreme and could be emptying the boiler although the LWCO is working. You'll be pushing the oily water to your pipes and rads which can cause radiator vents to blow out the dirty water. Happened to me once. Not fun to clean dirty oily water
Don't let the pipes freeze though. Send us more pictures of the set up and the pros can let you know how to skim it yourself since it has to be done frequently.0 -
The "CycleGard" LWCO will stop the burner every 10 minutes to check the water level and allow foaming to settle. It's a piece of junk. Once the boiler is properly cleaned and skimmed, have your guy instal a "SafeGard" instead. Even if you have to pay extra for it. It won't stop the burner unless the boiler is actually low on water.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.3 -
They are referred around here as psychoguard.3
-1 -
Well they piped it wrong, copper is a no no, and the equalizer should have been off the end of the header where they plugged it.
Don't pay in full until they make it right. There is a picture right in the manual showing how it's to be done.
That definitely answers my question about calling @EzzyT2 -
Just noticed the relief valve isn't installed correctly either, should be vertical.0
relief valve is vertical...0
did you change it since this picture was taken?
what will happen if it's not vertical?0
You said he was coming back tomorrow?
You need to have the installation book in hand. It comes with the boiler. Might still be in the plastic bag lying around somewhere.
You can download the book for that model. (50-60 pages or so).
It will show piping diagrams and minimum sizes for that size.
It may or may not state no copper piping for steam above the water line. However it may discourage that practice.
Your old boiler was piped better than this and how long did it last?
Hopefully you did not pay in full.
it's a code violation,coolfx35 said:what will happen if it's not vertical?
junk builds up at the valve and seat, and at the stem,
either sealing it shut which is dangerous / bad,
or that same junk fouls the seat and valve when you test it annually / monthly, and that's a bad day also.
and it's a code violationknown to beat dead horses0 -
It's piped wrong. The equalizer MUST come off of the end of the header. No copper above the water line.
Also, both riser tappings should be utilized to prevent pulling water up, not just one.
Here's the manufacturer's diagram:
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Gentlemen I did not do this install someone else did and they do a very piss poor job. All incorrect as others have mentioned11
I was actually going to say I was impressed with how quick you got a new boiler at the start of heating season.
Get these things corrected and either skim the boiler yourself or have them do it, It takes a long time, and I'll bet you'll have both a quiet boiler and a steady water line.0 -
Why are they always messed up? I’m far from a plumber but the diagram is so clear! I know the job site can make things difficult but damn!!
how do I skim the boiler? instructions will be greatly appreciated.0
You need a port above the water line. It should show in the install book which one to use.
Your installer might know where it is and how to skim.0 -
you could remove t&p valve the way it is installed (incorrectly), crack fill water valve to trickle water in, let it trickle out nipple where t&p was, turn on boiler to heat it up every thirty minutes. keep water approx 180 degrees. the idea is to let machining oils float to top of water and trickle out. it can take 8 hrs or16 hrs. Painful but necessary.0
I think the reason he made the release valve horizontal was because the black pipe connecting to the equalizer is directly underneath of it.Ironman said:It's piped wrong. The equalizer MUST come off of the end of the header. No copper above the water line.
hmm... Can it be 45 degrees instead of vertical?
How much trouble would it have been to complete the gas line in black pipe. Doesn't any one carry a fitting bag anymore?0
you could fix that safety valve yourself with one more 90 and some tools,
take the copper off, unscrew it,
back the valve, and the 90 it's on, 1/4 turn counterclockwise,
(well take it out and redope it first,)
then screw your new 90 in where the copper was, and screw the copper back into that 90, done.
takes less time than it did for me to type this.
the header is a little more involved, equally important, and for any decent mechanic, that can read a manual, wouldn't take that much more time than the rest of this typing did.
Reading is fundamental.
(this isn't directed at you)
Besides the bad install, was the boiler sized correctly? 🤔🤔Homeowner, Entrepreneur, Mechanic, Electrician,
"The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci0 -
If that's a water alarm, I'd prefer to have it on the floor so I would know if there is a half inch of water instead of 4 inches.....just my 2¢.Homeowner, Entrepreneur, Mechanic, Electrician,
"The toes you step on today are connected to the butt you'll have to kiss tomorrow". ---Vincent "Buddy" Cianci1 -
I think it's suggested upstairs here somewhere,
instead of the 90 between the valve and boiler,
plumb in a Tee with the valve on top as I suggest above,
and add a valve and cap on the horizontal, this becomes your skim port.
Or post a better picture of that port behind the equalizer.known to beat dead horses0 -
Good eye, this one has 2 parts, the metal part that detects the water is on the ground. the one you pointed out is the alarm with battery.brandonf said:If that's a water alarm, I'd prefer to have it on the floor so I would know if there is a half inch of water instead of 4 inches.....just my 2¢.
It's pretty much the same as my last boiler, 172btu vs 170btu. i didn't have any issues with my last one. so I assuming I am close. He did count all the radiators and square footage of the house and decided on this one.brandonf said:Besides the bad install, was the boiler sized correctly? 🤔🤔
@coolfx35 unfortunately I’m not sure why you didn’t choose @EzzyT, or when you reached out to me you never responded back. Ezzy or I would have done this right but, it is what is.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
What a shame.
Another installer who can't read. I am sure it was a $$$thing. You get what you pay for. Especially with steam0 -
Coolfx 35, did you get a contract or proposal from this installer?
It would be interesting to see.....blank out any money reference if you decide to show it.0 -
No auto fill valve either?Bob Boan
you shouldnt need an autofill valve.0
I agree the equalizer has to be piped correctly, it's a shame because the work he did on the header was not bad -it just won't work right till that equalizer is piped right.
Looking at the manual it seems there is no choice but to use the PRV tapping to skim the boiler. Listen to what others have said about installing a T on that PRV tapping with the safety above and a horizontal pipe and cap to skim through.
3PSI gauge0
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam