Weil-McLein CGM Series 8 HEADACHES
Manor24
Manor24 Member Posts: 19
edited January 2018 in Gas Heating
My old reliable Weil-McLain has been anything but this season.
We had heavy banging noises in the walls and so we called a local plumber to service the system. He installed new valves, expansion tanks (2), pressure relief valve and automatic vents, and purged the system. He told us it was a top-of-the-line system in great working order.
Everything seemed to be working great for a couple weeks and we started hearing noises again, sounded more like "kettling", opposed to banging. Called the plumber, he insisted there was air in the lines so he came to bleed them AGAIN... and AGAIN.
The noise never stopped so I asked my friend an "HVAC Specialist" to look at the boiler. For some reason he decided to close the automatic air vents. This is when the trouble kicked into high gear.
Later that night I heard what I sounded like a hurricane gushing through the walls. I went downstairs to check on the boiler and noticed the pressure oscillating like crazy. Thinking it okay because my buddy must've known what he was doing, I went back upstairs. A few hours later I heard the noise again and went to check the basement. This time I found a flooded boiler room filled with steam. I immediately turned the boiler off at the emergency switch.
Time to call the plumber again! This time since it was an emergency the owner of the company was dispatched. After looking at the boiler for a few minutes, he determined that it was not in the best condition and should be replaced, a far cry from what we were told just a few weeks earlier from his subordinate. When called out on this, he backpedaled and said he could replace the High Limit Control (Aquastat), but only if he could locate the part.
The next day he came by with a Honeywell Aquastat that he attempted to retrofit into the system because he said the system wasn't turning off at 180ºF as it was set to. (I have since found out after reading the owner's manual that the system is supposed to run at 210-240ºF. Some insight here would be appreciated.)
After all that, the pressure relief valve is still shooting out water and the system is tripping off. Every day I come home to a new puddle of water and have to reset the boiler via the Aquastat. Is there any hope for this thing or should I cut my losses and buy a new system?
«1
  • Gordy
    Gordy Member Posts: 9,546
    edited January 2018
    Your system is NOT suppose to run at 210-240 degrees. Water boils at 212 degrees, and this is not a steam system. If it is there's the problem. I can't believe that none of them didn't stay to make sure the boiler was shutting down on the high limit setting.
  • lchmb
    lchmb Member Posts: 2,997
    edited January 2018
    I'm surprised they couldnt locate the high limit controller (or something closer than what they did).. It is the small box top left in the boiler. the one with the wires cut off... It is an older boiler but should be repairable. I would also look at the circulator to make sure it's moving water...
    Manor24
  • Ironman
    Ironman Member Posts: 7,724
    You need to get a REAL hydronic pro out there immediately. Someone has disconnected the high limit safety and tried to replace it with a strap on aquastat above the boiler. I could understand that as a bandaid for a night time emergency, but it should have been immediately repaired correctly the next day.
    As Gordy pointed out: that's a hot water boiler, not steam. It should not be run above 190*. 180* is the normal high limit setting.
    The boiler is old, but probably repairable. Better pics from farther back of the boiler and near piping might help us see something else.
    Bob Boan
    Manor24Steve Minnich
    Jamie Hall Member Posts: 26,154
    The boiler probably survived the abuse. It's a good boiler, and Weil-McLains are tough. But the control system is a catastrophe, and the fact that the pressure is bounding around indicates that whoever is servicing it ... can't do it properly.
    Manor24
  • Manor24
    Took matters into our own hands and decided to go through the checklist in the owner’s manual... I think we found the problem...
    You guys were right about the plumber being clueless - turns out he left the manual feed valve OPEN.
    So we bled the system and closed the valve after fill, and (fingers crossed) we are good to go!
  • Gordy
    edited January 2018
    What is the system psi? Check when system is ambient temp., not while boiler, and radiation are hot.
  • Manor24
    System PSI is 24 (higher when hot). House is three stories and boiler is in the basement.
  • Ironman
    Should be 18 psi cold.
    Bob Boan
    PSI is a little high still, but not bad -- and if you're hot, you're hot. Sometimes we are our own best technicians, eh?
  • Gordy
    The expansion tank(s) come factory filled to 12 psi. They must be adjusted to the system pressure while not connected to the system.
    I'm assuming you have diaphragm tanks from your initial post.
  • JUGHNE
    JUGHNE Member Posts: 11,452
    It sounds like you just had 2 new expansion tanks installed.
    They should be pressurized to 18 PSI, cold, with no water pressure applied or removed from the system to check.
    It would be good if the were charged the same amount before install. (did he leave the old ones there....could be spares for the future....put air in them and if they hold for a couple days they would be good).
  • Manor24
    I'll take care of the expansion tanks tomorrow. Do you think these Maid-o-Mist #67 are adequate air vents?
  • misterikks
    misterikks Member Posts: 1
    Maid of mist are unlikely to last long but the air separator is piped too close to elbow . A common problem. So even a high quality valve wood have trouble.a spirovent would do wonders for air noises but then you get into repipe issues.
  • Tim McElwain
    Tim McElwain Member Posts: 4,656
    For your information the control system for that boiler is a obsolete White Rodgers system and is no longer available. It is a mercury pilot system, the pilot uses spark ignition from the white box shown in the picture. It is a 5059 control and is not made anymore.
    Not that this has anything to do with your present problem but certainly for planning purposes. If it goes it will require an entire control system replacement including the gas valve. Weil McLain was offering a Hot Surface Ignition kit replacement. I will try to find the numbers for the kit replacement and post here.
    Gordy
    EBEBRATT-Ed Member Posts: 18,176
    What cracks me up is the owner of the plumbing business want's to replace the boiler. Why? He won't be able to work on the new one any better than the old one that he didn't have a clue about.
    The sad thing is (3) technicians looked at the job and didn't do crap. That's what scares me. Unqualified.
    And worse than that, there simple problems that you don't need to be a genius to fix
    GordyManor24
  • Manor24
    Swapped out the Maid-o-Mist #67 for Taco #400 and pressurized the expansion tanks to 18-19PSI. So far the system is running much better. Will post any updates later if there are (or hopefully are not) any problems.
    Steamhead Member Posts: 17,886
    Sure about that, Tim? R.E. Michel still shows the 5059-23 and -134 still available...................
    Consulting
  • Tim McElwain
    Steamhead that may be the case or even E-Bay but here locally we can't get replacements at any of the supply houses.
  • Manor24
    Came home and found the boiler off again with no apparent symptoms. Could be too much pressure?
    As requested, here are more pictures of the system with specs on the components...
  • neilc
    neilc Member Posts: 3,028
    OP
    you're having to reset the strap on manual reset high limit, strapped to the pipe above the boiler, cause the operating limit / temperature control, the one with the 2 clipped wires under the cover, isn't doing its job. This control needs to be wired back in and work.
    You have nothing there monitoring pressure, or to stop or disable the boiler by pressure. The boiler pressure is controlled by the fill valve and the expansion tank(s), and then in worst case scenario, by the pressure safety relief valve.
    Has that been discharging?
    You should put your zipcode into the Find a Contractor at the top of the page.
    known to beat dead horses
  • Manor24
    Yes, the relief valve has been triggering at 30PSI. The pressure builds so quickly once it reaches 20PSI. Cold it's running around 10 now... :|
  • Gordy
    edited January 2018
    Did you check the expansion tanks pressure isolated from system? It was brought up to do, and you said you were going to do it.
    Zman
  • neilc
    you need that operating limit !
    with the manual set to 240 you're making steam, and there's your pressure.
    Understand, that red button is the dooms day safety.
    it should be set lower, like 200, once you get the operating limit repaired.
    Right now your banging off at 240 and that's too high.
  • neilc
    You're probably tripping on high temp when only one or 2 zones call, and the boiler can't shed the heat it's making.
    I would lock all those zone valves open and maximize flow right now until you get the operating control dealt with.
    dial that high limit down to 210 and see if it will hold there with everything open
  • Manor24
    Hi Gordy, I pressurized the tanks to 18PSI like you had suggested.
    neilc, The Aquastat is actually set to 130º, which corresponds to 180º (measured offset of 50ºF).
  • Gordy
    so of system is set to 18, and X tanks are filled properly that only leaves a run away boiler if you are still popping the relief valve. Is relief valve new?
    You need to get this fixed asap! The aquastat.
  • neilc
    yeah, sorry , I was concentrating on the high limit reset tab,
    isn't that dialed over to 240?
    It is that red button your resetting, right?
    your hitting the manual reset high limit, (?)
  • Gordy
    It's set at 130.
  • neilc
    i see the pointer tab at 130.
    what's the metal tab at 12:01 oclock ?
    I see that at 250
  • neilc
    I'll admit I missed the 130 operating,
    I was keyed in on the manual reset, and it's temp,
    Was that tripped?
    then I also have to ask,
    what's the differential set to?
    and isn't 130 too low a cut out?
    (i still think we're making steam at 250)
  • Manor24
    Are we sure this isn't a steam boiler?
  • Gordy
    edited January 2018
    I hope not with an air removal device, and a circulator. A lot of boilers are rated for steam, or hot water.
    Question for the OP what is the differential dial on the back of the aquastat set at?
  • Manor24
    I don't think my Aquastat has a differential; if it does, I haven't been able to find it. It doesn't look like the OEM has one either? https://www.supplyhouse.com/Weil-McLain-510-312-250-Operating-Temperature-Control-All-Sizes?gclid=EAIaIQobChMIu87Y9cXW2AIVk0wNCh2JhgMnEAQYASABEgKDaPD_BwE
  • JUGHNE
    Did you unscrew the tanks from the system, then check for the 18 PSI for the air bladder?
  • Gordy
    That link is not the one in the picture. The one in the last set of pictures is a strap on aquastat.
  • Manor24
    The differential is 50 degrees based on activity...
    The link was is the OEM High Limit Control (not operational)
  • Gordy
    Sooooo,the strap on is the controlling device?
    Manor24
  • Manor24
    Yup, probably going to need to swap that out. I know we can't discuss specifics, but if I told you what he charged me for that disaster you'd fall out of your chair
  • Manor24
    Yes, but should they still be at 18 when my system now is running at 10-12?
  • Gordy
    Just so you understand the job of the aquastat is to turn the burner off at its set high limit usually 190, or lower depending. Then relight the burner at low limit, or set differential usually 30-50degrees usually no lower than 140 so flue gas does not condense. It is also a saftey feature to prevent the boiler from over heating the system water past the boiling point.
    My stance on this is you need to get someone to fix this ASAP, and not the person who has been working on it.
    Steve Minnich