What am I doing wrong
11213141618
  • Gordy
    Gordy Member Posts: 9,546
    So you could fudge your reset curve a little more. Unless you like the temps in all the other rooms. Forget about the living room for now.
  • Paul48
    Paul48 Member Posts: 4,469
    Four inch duct fan= $20.........
  • FranklinD
    FranklinD Member Posts: 399
    I wonder where that living room radiator falls in the piping scheme...our living room rad was always the coolest until I set my bumblebee circ to speed 2 (using the hydronic formula I should be using speed 1). I assume it's because my system (gravity) was designed for a long-burning coal fire in which all radiators would get hot eventually, not expecting them to all warm equally in 10-15 minutes.
    Anyway, boosting my flow another 3 gpm really helped with the living room. Then this year I freed up and re packed all the radiator valves, and spent a week fine tuning them all for what seems to be an ideal balance.
    If the mod/con is direct piped, I assume your options for pump speed may be limited. I'm not sure on that (I have cast iron and it doesn't care about minimum flow rates). But perhaps the radiator valve adjustments would help. It does take some time and patience is required, but it may be worth a shot.
    Best of luck!
    Ford Master Technician, "Tinkerer of Terror"
    Police & Fire Equipment Lead Mechanic, NW WI
    Lover of Old Homes & Gravity Hot Water Systems
  • Paul48
    For God's Sake........He has these radiators inside an insulated box!!!!!!!!!!!!!
  • maybemark
    maybemark Member Posts: 1,131
    Franklin
    The living room are the 1st 2 radiators off the boiler. It is direct piped. I am on med speed on my circs. when i as on low, I saw that the water was not getting to all the radiators.
    I do need to adjust the valves to try and get a closer balance.
    Paul
    That statement was a bit extreme. The box is not insulated at all.
    But, the box does have serious problems as far as transferring the heat out of the box
  • maybemark
    Gordy
    I imagine i can play with the curve a little, but, would it be better to play with the valves of the radiators, or, change the curve, because it is a little warm in the house. Correct me if I am wrong, if I play with the curve a little, would that make my living room even colder? or if i play with the valves, would that help warm up the living room a little bit
  • Gordy
    Balancing can get tedious. As you valve off warm rads that are to warm. That flow gets diverted to other rads in the system. since you have a constant speed circulator your flow rate will increase slightly as radiators get closed. It's a balancing act that may require going back to each radiator to readjust.
    SWEI
  • Gordy
    Trvs do this for you automatically. But it requires some bypass piping.
  • maybemark
    Gordy
    I don't have a problem going to each radiator a few times, rather than paying more money and more labor into this system, unless I really need too.
    If I turn down the valves, flow would be less? Can this be compensated by increasing the circs to hi, instead of medium as they are set at now?
  • Paul48
    No Mark.........That statement was not extreme, at all. The box is made of materials that insulate it. To suggest that adjusting flow rates can somehow change that fact, is akin to "throwing the baby out, with the bath water".
  • Gordy
    this may sound like a stupid question, but your absolutely certain both the living room rad valves are fully open, and I don't just mean the knob turned all the way open.
  • maybemark
    gordy
    Yes, the valves on the living room radiators are fully open.
    Paul, I'm not going to argue with you
  • Gordy
    Is the living room rads the first in the supply piping series? How many after that one before the return comes back to the boiler?
  • maybemark
    Yes, living room is #1. I think 7 or maybe 8 and this is only a guess are after the living room.
    Remember, my house is split with 2 mains and i am not sure
  • maybemark
    my office area is one of the last radiators and right now it's 71 back here
  • maybemark
    the living room is 65 right now
    my bedroom with the valve dialed down is 71
  • maybemark
    my house is too hot for me, I think 69 or 70 would be good
  • Gordy
    keep tuning.
  • maybemark
    the boiler?
    and what would you suggest I tune ?
  • SWEI
    SWEI Member Posts: 7,348
    Aren't the radiators piped as a parallel return? I don't recall mention of any series loops -- or did I miss something?
  • maybemark
    the system and set point are at 95, , the boiler water and set point was sensor is saying 41, which i think might be close
  • maybemark
    I have 5 main pipes in the basement, half the house has a 2" supply amd return, the other half has a supply and a return.
    the closer it gets to the back of the house, the mains get smaller
  • maybemark
    sorry, 4 main pipes
    each radiator has a supply and a return
  • Gordy
    Right Kurt I can't remember I would assume so. So Mark look at the first radiator in the basement mark the supply pipe from the main goes up to the rad, and the return from the rad goes down to the return main. That's parallel piped. I'm sure it is that.
  • Gordy
    If that is the case the trvs would not need bypasses. Makes things easier.
  • maybemark
    Gordy,and Kurt
    each radiator has it's own supply and return
    whay all of a sudden you think differently. Did I say something wrong?
  • Gordy
    edited November 2015
    I messed up Mark way back when I said the trvs would need bypasses. That is only true when rads are piped in series.
  • maybemark
    I never said they were in series, from the very begining, i said, the house is slit in half. 1 main supply and 1 main return, on both sides of the house
  • Gordy
    And I said I messed up.
  • maybemark
    as far as i know, all the radiators are this way, obviously, when they are in the walls I can not see the pipes and how they run
  • maybemark
    well, your not the only one that messed up, I never told anyone that most of the radiators have covers on them
  • Gordy
    The collective has given you the tools to rectify your problems. The rest is up to you whether or not you use them. This has been takin as far as it can be from my keyboard.
  • maybemark
    what is a trv?
    someone said, I would need to put them on the good radiators?
    why would this be better than playing with the valve, or curve?
  • maybemark
    Gordy
    thanks for all your help
  • Paul48
    The amount of labor, and or, price to have someone else install thermostatic radiator valves on all the good radiators, would be outrageous.
  • maybemark
    Paul
    why would that be suggested to me, if the cost would be extreme, why not just turn down the valves until i get it right?
  • Paul48
    Damned if I know Mark.
  • maybemark
    I'll try turning the good radiators down, and see what happends, if i do this, should i increase the circs to high? Or tune the boiler a little different?
  • Gordy
    Because it saves you from adjusting valves. the trv does it automatically. It holds the dialed temp of the room, and throttles the radiator flow automatically to keep the desired temp you set the trv to.
    Google them, and read up on how they work.
  • Paul48
    You may succeed in cooling the other rooms off. That will not change the fact, that you can't warm the living room. Maybe the guys that suggested TRV's missed the fact that you nixed the possibility of a repair costing $1000 a couple hundred posts back.