What am I doing wrong
circs like low much better
system is 107 {128}
flame 100%0 -
durring the day, I set the stat back I think 5 or 6 degrees
what your asking the house will be unable to live in comfotably
if your telling me to set the stat at 85.
you say play with the odr parameters Is that under outdoor reset?0 -
So long as the rads are getting the flow they need. That's fine. You said before the house was comfortable.0
can i turn down the valves of the radiator0
yes, the house has been comfortable, but the lowest we have had was 30, now
system is at 110 {128}
100%flame
the house is comfortable, just a little out of balance. The living room has always been a problem
I don't unstand why 185 to keep it at
it will be insane hot in here0 -
system 112 {128}
flame 100%
outside temp 32
inside at stat 700 -
what you are,shooting for is the reset curve doing all the work. You will never get it set optimally if the thermostat interrupts that setting process. You shift your reset curve so the water temp is just enough to off set the heat loss to what you feel is comfortable.0
Once that is done your golden, and the boiler will run optimally.0
I need it to stay on at 185 for a couple days? and no setbacks
I will be so uncomfortable for a few days
I'm happy at 71, your asking 850 -
what does it mean by shifting the reset curve. Is this something the boiler does on it's own, or I have to do something manually?
what do i do?0 -
If the temp climbs above 71 then then you need to shift the curve to a cooler supply temp. You may need to set the shift to -9 instead of 9 where you have it now.0
is the curve the {128} on the boiler?0
114 {128}
flame 100%
outside 32
inside0 -
I have to go walk my dog, will be back in 15 minutes0
Yes that is the target temp the boiler is trying to reach.0
The shift curve function allows you to tweak that number +18 to -17 degrees. So your at + 9 now you said right?0
he's walking the dog Gordy.0
Sigh0
If you absolutely must have a setback, we'll address the right way to do that -- after you have the ODR curve dialed in.0
I'm back
118 {128}
outside 32
inside 700 -
119 {128}
flame 100%
outside 32
stat 700 -
I changed the reset to -1
117 {117}
flame 83%
outside 32
inside is 700 -
118 {117}
flame 79%
outside 32
stat 700 -
should i set the odr lower than -1?0
Note the indoor and outdoor temps every hour or so for at least a day. The boiler should not shut off much, if at all. If the house overheats the thermostat will shut the boiler down.
Adjust the ODR curve and repeat.0 -
can i turn the temp down to something more comfortable than 85?
can i keep the heat at 71 all the time, instead of 85?0
117 {117}
flame 74%
outside 32
stat 700 -
the circs are on low0
If by "the heat" you mean the thermostat setting, no. We really do start with them set at 85°F or 90°F. That lets us zero in on the adjustments rapidly.
If the room gets over 71°F (and there's not a lot of sun shining in, a woodstove burning, etc.) then head for the boiler and start adjusting. You should be able to get within 2-3°F in a day or so, at which point you start looking for days with higher highs or lower lows so you can fine tune.0 -
what is a fine tuned boiler flame % is?0
117 {117}
flame 72%
outside 32
inside 700 -
the heat in the house is way out of balance
70 in bedroom0 -
Your low outdoor air setting is 180* IF you run out of shift adjustment you have some more yet drop that to say 160 170 then play with the shift again. NOT YET though see where what you have gets you.0
66 in living room (always cold room in house)
68 in kitchen
way out of balance, do not know what it is upstairs0 -
the flame is still at 72% and 117 {117}
obviously this is better, should it be better yet, than 72% for flame?0 -
The high mass of water and steel in your system is a giant flywheel. Think of the thermostat as a clutch. Think of the supply water temperature setting of the boiler as the throttle. ODR is the cruise control. The goal is to get the cruise control running the car at a constant speed without having to use the clutch.1
I have to work on the valves of the radiators, see if I can balance the system better than it is0
- 120 Geothermal