What am I doing wrong
I forgot one check the shift reset curve also.0
these are numbers I have for 1
OD low -5
OD high 64
SP low out 180
SR high out 70
ODSD 70
SHDN 1 10
Boost temp 25
boost time 2.000 -
on the menu, where will I find the shift reset curve, I don't remember seeing this0
I see it, I'll go downstairs again
shift reverse curve is set at 9
Ramp?0
ramp is disabled0
gordy
what should the reset curve be set at?
Set boost temp to 0 , and boost time to 0. Those are default.0
Then turn up the t stat see how boiler responds.0
Snow blowing ?0
Yes, it's snowing here0
Well?0
did what you said, and the flame went up to 100%, but, the system was very cold 82 degrees, I have it set back for a few hours
Your outdoor sensor is hooked to the right terminal?0
So the boiler is not bouncing off hi limit? Cycling you getting good condensate?0
system is 84 f and the flame is still 100%
the outside is hooked to the right terminals
condensate is flowing0 -
I don't understand bouncing off high limit0
next to the 87 f is {128 f}0
system is at 89 f {128}
flame 100%0 -
system is 90 (128}
100% flame0 -
system at 80 and on stand by, but stat is asking for heat0
system 91 {128)
100% flame, the boiler is running again0 -
system is at 93 {128}
100% flame0 -
system 95 [128}
flame 100%0 -
The temperature in parenthesis is the temperature it's trying to reach. Determined by your ODR.0
system 100 (128)
flame 100%
I changed the setting on the pumps but setting started to rise faster0 -
Don't mess with the circ. if your heating fine the pump is fine.0
Are you piped direct to the boiler, or P/s?0
direct0
when i turned the circs on low, it was heating faster
I had it on high, then turned it down, I'll put it back to high, if you think that is good
101 (128)
100% flame0 -
How is boiler piped??0
it likes low alot better it's up to 103 (128)
100% flame0 -
Has your thermostat been satisfied yet?0
it's piped for direct
no, not up to 71
was system was 104, changed to high, went down to 102 with in 3 sec,
flame still 100%0 -
So ~20 minutes to raise the water temp by 20°F?
More ODR, less thermostat, more comfort.0 -
I don't understand, your asking me to change the outside setting? to what?0
what does it mean more odr, less thermostat?
what should i be changing?0 -
I'm suggesting you turn the thermostat up to something like 85°F and leave it there. For the next few days, adjust only the ODR parameters until the house remains at a relatively stable indoor temp day & night, regardless of the outdoor temp.0
And don't setback, I believe you mentioned you had the heat turned down.0
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 162 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
