Anyone ever see an arrangement like this?

IMG_1397.jpeg IMG_1396.jpeg
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.
PC7060kcoppmattmia2Alan (California Radiant) ForbesHydronicMikeIntplm.Steve Minnich

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    that isn't even the brand that home depot carries

    IronmanIntplm.Steve Minnich
  • mattmia2
    mattmia2 Posts: 18,399

    what's the flo check for? i don't see any evidence that they are making dhw with that boiler.

  • hot_rod
    hot_rod Posts: 28,699

    A tank for each one of the little people to the left, to watch over?

    I did see a bunch of #30 on their side on a unistrut cradle once.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGrossIronmanJoannie
  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    Old gravity system? Probably lots of expansion/water volume. As strange as it looks, easier to source #30's, then 60's or larger, when replace time comes. Lots of supply place, don't carry anything larger than #30.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    " If the relief valve blows add another tank"

    I do like the 1/2" copper supply to return bypass

    The ball valve handles removed to prevent balance tampering.

    0-30 psi ASME tanks are not required. Maybe that is why they used multiples of the cheaper tanks

    Only 1 circulator so no need for a flow check. "We put those on every job but I don't know why"

    Ironman
  • ratio
    ratio Posts: 4,344

    That's the staged-admittance configuration. Charge each one a few lbs higher than the next & when one is full the next one takes over.

  • hot_rod
    hot_rod Posts: 28,699

    4- # 30 Extrol= 10 gallon acceptance $252

    1- EX 90= 11.3 gallon acceptance $224.

    The # 30 are easy to find, not so much with the larger sizes

    Also the #30 and # 60 are the same 2.5 acceptance. You get a larger air space with the # 60

    IMG_2520.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2GGrossIronman
  • Mad Dog_2
    Mad Dog_2 Posts: 8,755

    I've hung double tanks in a pinch, but 4??? Looks like a Bunch of bananas 🍌 😆 . Mad Dog

    PC7060GGrossIronmanIntplm.
  • HydronicMike
    HydronicMike Posts: 471

    The flo check could’ve been there because they used to have a coil. Or the boiler maintains temperature.

  • GGross
    GGross Posts: 2,104
    edited May 20

    This seems like as good a place as any to share amtrols sizing tools! It's not rocket science, and if it is you made a big mistake!

    https://www.amtrol.com/resources-rewards/selection-tools/

    IronmanAlan (California Radiant) Forbes
  • Ironman
    Ironman Posts: 7,975

    The local RE Michel stocks a floor #30 and can get up to a 90 in a day or two. That’s where I get them. But I also doubt that they would have had four these #30’s on the shelf.

    I wonder if they started with one and then kept adding them until the relief valve stopped releasing.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Intplm.mattmia2EBEBRATT-EdHydronicMike
  • Ironman
    Ironman Posts: 7,975

    The only problem is if it’s an old gravity system, then you have to calculate the water volume in the system. You can’t use the quick sizing chart. Most technicians don’t know how to do that.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2
  • GGross
    GGross Posts: 2,104
    edited May 20

    out of curiosity when you mention a floor mounted number 30 tank are you talking about a floor mounted tank similar to an ex30 or an SX-30V? I only ask because I have seen contractors in my shop ask for a floor mounted number 30, looking for a 4.4 gallon-ish tank and they get the SX-30V which is 14 gallons (similar to EX90) and end up paying more than they should.

    I am surprised the local supply house doesn't have 4 on the shelf! even with Amtrol prioritizing shipments to big box stores we still have around 50 or so in each branch here.

    GroundUp
  • Ironman
    Ironman Posts: 7,975
    edited May 20

    An SX30.

    RE Michel branches get a supply truck from their distribution center twice a week, so the bean counters don’t want to leave a lot of things on the shelves of the branches that doesn’t move quickly.

    There’s a fair amount of hydronic work around here, but this is definitely not boiler country like the North East.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    GGrossHydronicMike
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,328

    The only one I remember is that 6" pipe holds about 1.5 gallons /foot.

    i was never one for the 'quick pick charts". I always wanted to calculate my own stuff. I don't like figuring pipe and fitting resistance by multiplying x 1.5 for fittings either.

    Mad Dog_2
  • PC7060
    PC7060 Posts: 1,980

    I cheat, drain down the system and read the before and after on the water meter! Normally have to because there’s typically no isolation valves on those old system.

    IronmanpumpcontrolguySTONECREEKSERVICES
  • mattmia2
    mattmia2 Posts: 18,399

    you can probably be off by about 30% and still pick the right tank, especially if you don't cut it too close to 30 psig in your calculation. You would have to be closer if your structure is 4+ stories.

    Ironmanpumpcontrolguy
  • GroundUp
    GroundUp Posts: 2,573

    @Ironman dang, even with trucks coming in every few days it still seems like 4 gallon tanks would be a pretty common item. But then again I very seldom visit a local supply house so maybe mine have slim pickings as well, which would resonate because I regularly have local plumbing/HVAC guys coming to me for tanks, pumps, valves, flanges, etc. It's been many years since I had less than 5 of anything on the shelf; ironically enough I just took delivery of a pallet of expansion tanks yesterday with 40 #15 and 15 #30.

    With that said, this 4 pack seems to have done its job since those tanks are upward of 20 years old

  • HomerJSmith
    HomerJSmith Posts: 2,837

    When the bladder psi is 4#, you need a lot of #30s.

  • johnnyb
    johnnyb Posts: 3

    you guys that commented should do stand up comedy.

  • leonz
    leonz Posts: 1,994
    edited June 16

    Seeing that Rube Goldberg mess certainly makes me happy that I have a single 15 gallon Bell & Gossett steel compression tank hanging in the ceiling of my laundry room and assures me again I was sane in following Mr. Holohans advice in his wonderful books; Classic Hydronics, Pumping Away and How Come using a pump module for my coal stoker boilers "air management" system.

  • JimP
    JimP Posts: 118

    It’s neat to see so much threaded pipe. Usually see a lot of copper on an installation like this that isn’t too old. The flow control valve might be needed to stop gravity flow from higher points in the building. There are three returns so maybe one or two come from higher up in the building. The lack of isolation valves for service is unfortunate and that 1/2” bypass probably does very little.

  • mattmia2
    mattmia2 Posts: 18,399

    they probably didn't know they could use copper

    PC7060
  • Alan (California Radiant) Forbes
    edited June 23
    IMG_1923.jpeg

    Saw this yesterday on a job we installed in 2000. Another contractor added it onto the return piping from a radiator system.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    mattmia2rick in Alaska
  • Steamhead
    Steamhead Posts: 19,007

    Cue the "Twilight Zone" theme………………