DIY Steam Boiler Install
Comments
-
What’s the correct length?
Edit: I found the correct length, but damn those are long!! https://www.engineeringtoolbox.com/npt-national-pipe-taper-threads-d_750.htmlNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Does anyone know why they piped my gas line so crazy? Is it because the installer was even lazier than me and just threw whatever pieces of pipe he had up there?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
He maybe did not want to cut and thread the larger size.....and just cleaned out his shop scraps with the short.
I am often less than 1/2 mile from installs and will do the threading in my shop on the bench vice.....if mis-measured and too long I might have done that also.....though would have put a tee with a plugged opening on the end of the first pipe to make it look like a plan......"that is for your water heater, dryer, range or grill".1 -
-
That sounds very likely! Luckily I don’t have any other service calls today so I can clean it up 😄
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Gas line done!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el3 -
-
@ChrisJ yes that gas valve is still allowed as per code.
@ethicalpaul how close is the draft hood and the flue pipe to the stairs?2 -
-
JUGHNE said:That gas stop valve must not be that old. The ones like that I have seen have a broken handle or will have soon....they were never exercised. If it operates smoothly it is better than the import ball valves most end up with.
I've been using full port. CSA rated ball valves recently. They aren't cheap tho.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
By plug valve do you mean a tapered plug with a slotted keyway in the plug (seems restrictive, but works).
Usually has a nut on the opposite side of the handle that can be loosened to allow turning....but more often is just forced with a pipe wrench breaking the handle off.
They can be taken apart, cleaned and regreased to work easy.
My guess is that is what it is.0 -
I looked through the valve and it appeared full port.I’ll measure the draft hood clearance @EzzyT thank you
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
JUGHNE said:By plug valve do you mean a tapered plug with a slotted keyway in the plug (seems restrictive, but works). Usually has a nut on the opposite side of the handle that can be loosened to allow turning....but more often is just forced with a pipe wrench breaking the handle off. They can be taken apart, cleaned and regreased to work easy. My guess is that is what it is.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
EzzyT said:@ChrisJ yes that gas valve is still allowed as per code.
@ethicalpaul how close is the draft hood and the flue pipe to the stairs?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
As long as the threads don't leak......................Usually the more threads engaged between the pipe and the fitting the better. I usually look inside the fitting to see if the pipes is close to the end of the fitting threads.
Unions always seem to make in further than other fittings which can screw with your measurements if in a tight spot1 -
-
Today I did the flue pipe and the electrical. Is it ok to put an emergency switch at the top of the stairs AND at the boiler? Before it was only at the boiler so I wired another one at the top of the stairwell in series.
I’m waiting on my control fittings and a couple more near boiler nipples but I can fire it up and do some skimming and test the controls.
It took awhile to clear the air out of the gas line but then 👍🏻NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
It’s clocking about 88.9k BTU (corrected) with a specification of 88.5 so that seems pretty good.From dead cold the Psycho Gard low water test kicked in before it started to steam but just barely so I think in the winter it will do its check mid-steam so I’ll be interested to see what that’s like
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Looks good Paul. I normally throw the cycle guards in the garage and replace them with a safe guard 450.ethicalpaul said:It’s clocking about 88.9k BTU (corrected) with a specification of 88.5 so that seems pretty good.
From dead cold the Psycho Gard low water test kicked in before it started to steam but just barely so I think in the winter it will do its check mid-steam so I’ll be interested to see what that’s like
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
-
Dave0176 said:
It’s clocking about 88.9k BTU (corrected) with a specification of 88.5 so that seems pretty good.
Looks good Paul. I normally throw the cycle guards in the garage and replace them with a safe guard 450.From dead cold the Psycho Gard low water test kicked in before it started to steam but just barely so I think in the winter it will do its check mid-steam so I’ll be interested to see what that’s like
He's probably going to keep it just because he knows I can't stand them.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Dave0176 said:
It’s clocking about 88.9k BTU (corrected) with a specification of 88.5 so that seems pretty good.
Looks good Paul. I normally throw the cycle guards in the garage and replace them with a safe guard 450.From dead cold the Psycho Gard low water test kicked in before it started to steam but just barely so I think in the winter it will do its check mid-steam so I’ll be interested to see what that’s likeNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
I’m awaiting arrival of a part for the second one. Should arrive tomorrow (good eye!)
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
I will be
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The first skimming session went fine. I threw some tsp in there and let it simmer for a while then skimmed for a couple hours. That peerless must have a lot of iron because it stayed hot for a long time.
today I received my last parts and finished attaching the second riser and the equalizer. And I did the control tree.
Wow, what an experience! At one point I was like 3/8” off in like three different places. But joints that seem tight can take another turn or two. And that boiler can be budged just slightly and then almost like magic that last union is suddenly lining right up!!
It’s really like an art—you get the urge to fight the pipes, to bend them to your will, but they don’t! Well ok a little they do, but only a little! But then you figure out a way to work with them and then they agree. Do you guys feel that feeling? I feel like I got just a taste of that experience from this project.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el4 -
It looks like a mad scientist’s lab on steam boilers lolDL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......2 -
ethicalpaul said:
But joints that seem tight can take another turn or two. And that boiler can be budged just slightly and then almost like magic that last union is suddenly lining right up!!
It’s really like an art—you get the urge to fight the pipes, to bend them to your will, but they don’t! Well ok a little they do, but only a little! But then you figure out a way to work with them and then they agree. Do you guys feel that feeling? I feel like I got just a taste of that experience from this project.” blockquote>
Paul I was told by an old timer quote “threaded pipe lies”
This is why we carry so many extra nipples and why I also have a nipple chuck.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......2 -
Thanks @Dave0176 that’s a great saying! I thought for sure I’d have to cut a 1-1/4 on the equalizer but it stopped lying finally!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
It’s no joke @EBEBRATT-Ed as you all know and I have learned!
I always use tape for the steam and water connections. One trick I tried is that when I needed to find two more turns on one particular joint, I removed the tape and went with my Blue Block. That got me the two turns just fine, but I found that joint leaking a little steam and oozing during my testing tonight.That stuff claims no cure time...what do you all think?
My mind reels at all the tricks I don’t know!NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
mattmia2 said:i think you need a bigger wrench...
I’ve never had a taped joint leak steam, even ones that were way looser than this one.Are doped joints known to have to be that much tighter than taped joints?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
No I’m not 100%. I’ll keep an eye on it and will redo the joint if it proves faulty. I’ll look hard for condensation drips on the next test run. Thanks @Danny Scully!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Most of my piping was done with Megaloc alone.
Going into the boiler and into my old mains got both tape and dope.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Is blue block rated for steam?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements