Air eliminator location
I am considering re-arranging the plumbing a bit in my setup. Every year in the fall or winter when i start using my heating system i need to purge the lines of air. Not a huge problem obviously but a bit of a pain since there is no drain in the basement near the boiler. The current configuration goes boiler supply —> circulator —> air eliminator —>zones—>return—> zone valves.
I am thinking of replumbing it and switching out the air eliminator to a spirovent air eliminator so the configuration would be boiler supply —> spirovent —> circulator (etc ).
I feel like the biggest issue is going to be supporting the circulator in the new location but i found threaded rod and floor supports that i think will do the job.
The big question to me, will this configuration make a differance? I keep hearing about "pumping away" and that a air eliminator should be close to the boiler yet before circulators and or pumps.
Comments
-
draw your proposed system. The best way to keep air eliminated permanently is to get rid of your leaks. air doesn't naturally form in the system, it gets in there from filling. On install the system is purged of air, then an inline air separator helps to remove the entrained air in the system, air vents appropriately located remove the trapped air that can be missed via purging. If air returns to the system it either was never fully removed, or has been introduced via makeup water (ie leaks)
0 -
Any air purger works best when you are pumping away from the expansion tank. The graphic below shows how the pump adds the pressure differential to the system, when pumping away
So boiler, air sep, expansion tank, pump.
Typically the expansion tank connects under the air purger. The fill system connects at the expansion tank also.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements