Equalizer
Would this be an issue to pipe this boiler like this with the equalizer on a 45.
    Jamie Hall Member Posts: 27,167
    No — that will work fine. I'm not wild about a 90 degree bend in the header, but if there is enough pitch it should be OK.
  • pedmec
    pedmec Member Posts: 1,299
    Why didn't you just pipe the equalizer on the other side of the boiler? or use the other riser coming out of the boiler to make the piping a little cleaner?
    ethicalpaul Member Posts: 8,579
    why the 90 degree dislike? It gives any water droplets another wall to slam into, no?
    I like the equalizer too fwiw
  • Captain Who
    Captain Who Member Posts: 700
    Nothing wrong with the 45 in the equalizer as long as the pipe size meets the min. mfg. requirement. I'm more concerned about the 1st main takeoff from the header. It shouldn't be horizontal. Either 45 from or fully vertical.
    bburd
  • pedmec
    I don't mind the 90. it makes for a great chin up bar!
    ethicalpaulGGross
  • pedmec
    @Captain Who i think that's a coupling. you can see the horizontal line in the fitting. I was thinking the same until i saw the line.
    Captain Who
  • jmerrill
    jmerrill Member Posts: 3
    Would they void the warranty if the boiler is piped like this?
    I don’t see anything that would void the warranty. What are you referring to?
    EBEBRATT-Ed Member Posts: 20,018
    Can you show a pic off the right-hand riser connects too? I agree the fitting on the header looks like a coupling instead of a tee.
    Other than that riser everything looks ok
    109A_5 Member Posts: 3,822
    edited 6:37AM
    Is that a Tee at the Yellow arrow ? If not where does the pipe at the Orange arrow go ?
  • 4GenPlumber
    4GenPlumber Member Posts: 90
    I dislike the bushings. They make reducing 90s that most manufacturers prefer. Also reducing from 3 to 1 1/2 at the end of the header? Rule of thumb, although probably not actually necessary, is only reducing 1 pipe size from header to equalizer.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,569
    I am also not a fan of the bushings. But not such a big deal. That rule about reducing one pipe size is really counterintuitive and I don't agree. And neither do any of the boiler manufacturers. The larger the header, the less condensate you'll have, because velocity is reduced. So if anything, the bigger headers, should get smaller equalizers. But in reality, the only driving factor is really the boiler size.
  • ChrisJ
    ChrisJ Member Posts: 17,240
    Bushings seem to get a lot of dislike in general.
    Like all of those who say you cannot use them on gas piping. The only note I've seen is cast iron bushings shall not be used. The rest are fine along with street fittings, except some areas don't allow them in concealed locations.
    I am curious what that other pipe coming down in the backround is though. Looks like it's about 1 1/2" or 2" with a union?
  • STEAM DOCTOR
    edited 2:12PM
    The issue with bushings, is that in theory , and in practice, they can create a water dam. Reducing elbow, would give you better flow. But not a big deal, in strait vertical application.
  • Captain Who
    Again, I think you need to check the manual to make sure that equalizer is not smaller than the minimum recommended by the manufacturer.
    What is the Boiler model and size?
    I don’t follow this at all but regardless the size minimum on the EQ has nothing to do with condensate—we’re talking teaspoons.
    It’s about carryover
  • ChrisJ
    Some call for 1 1/4, others 1 1/2.
    That looks like an EG-30. So a single 2" riser, 2" header and 1 1/2" equalizer.
  • Grallert
    Grallert Member Posts: 1,094
  • STEAM DOCTOR
    We have all been taught, the higher the velocity, the more water gets carried out from the boiler. The lower the velocity, the less water gets carried out of the boiler. If you follow through with that equation, that means that the larger the boiler steam piping and header coming out of the boiler, the less water there will actually be in the header. Which means, the drain function of the equalizer, can be reduced.
    Captain Who
    EdTheHeaterMan Member Posts: 11,915
    Here is the illustration from the manual on the left and I have made your piping arrangement on the right. I do not believe that your main rizer on the right side should be connected the way you did it. Red piping is not a good design.
    Captain Who
  • Captain Who
    SMH. We need a sticky to tell people to give a few different view angles when submitting a photo. I didn't realize that was a Tee. A bullheaded Tee is a disaster in steam piping, when the steam flows in the other direction that it does here because it generates wet steam. In this case it is almost like another equalizer would be needed because you don't want the end of the header to be an elbow up into the main.
    This might be a better design
    Captain Who