Would this be an issue to pipe this boiler like this with the equalizer on a 45.

«1

Comments

  • Jamie Hall
    Jamie Hall Posts: 27,975

    No — that will work fine. I'm not wild about a 90 degree bend in the header, but if there is enough pitch it should be OK.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • pedmec
    pedmec Posts: 1,488

    Why didn't you just pipe the equalizer on the other side of the boiler? or use the other riser coming out of the boiler to make the piping a little cleaner?

  • ethicalpaul
    ethicalpaul Posts: 9,076

    why the 90 degree dislike? It gives any water droplets another wall to slam into, no?

    I like the equalizer too fwiw

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Nothing wrong with the 45 in the equalizer as long as the pipe size meets the min. mfg. requirement. I'm more concerned about the 1st main takeoff from the header. It shouldn't be horizontal. Either 45 from or fully vertical.

    bburd
  • pedmec
    pedmec Posts: 1,488

    I don't mind the 90. it makes for a great chin up bar!

    ethicalpaulGGross
  • pedmec
    pedmec Posts: 1,488

    @Captain Who i think that's a coupling. you can see the horizontal line in the fitting. I was thinking the same until i saw the line.

    Captain Who
  • Would they void the warranty if the boiler is piped like this?

  • ethicalpaul
    ethicalpaul Posts: 9,076

    I don’t see anything that would void the warranty. What are you referring to?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Can you show a pic off the right-hand riser connects too? I agree the fitting on the header looks like a coupling instead of a tee.

    Other than that riser everything looks ok

  • 109A_5
    109A_5 Posts: 4,759
    edited February 17

    Is that a Tee at the Yellow arrow ? If not where does the pipe at the Orange arrow go ?

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • I dislike the bushings. They make reducing 90s that most manufacturers prefer. Also reducing from 3 to 1 1/2 at the end of the header? Rule of thumb, although probably not actually necessary, is only reducing 1 pipe size from header to equalizer.

  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    I am also not a fan of the bushings. But not such a big deal. That rule about reducing one pipe size is really counterintuitive and I don't agree. And neither do any of the boiler manufacturers. The larger the header, the less condensate you'll have, because velocity is reduced. So if anything, the bigger headers, should get smaller equalizers. But in reality, the only driving factor is really the boiler size.

  • ChrisJ
    ChrisJ Posts: 17,763

    Bushings seem to get a lot of dislike in general.

    Like all of those who say you cannot use them on gas piping. The only note I've seen is cast iron bushings shall not be used. The rest are fine along with street fittings, except some areas don't allow them in concealed locations.

    I am curious what that other pipe coming down in the backround is though. Looks like it's about 1 1/2" or 2" with a union?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680
    edited February 17

    The issue with bushings, is that in theory , and in practice, they can create a water dam. Reducing elbow, would give you better flow. But not a big deal, in strait vertical application.

    reggi
  • Again, I think you need to check the manual to make sure that equalizer is not smaller than the minimum recommended by the manufacturer.

    What is the Boiler model and size?

  • ethicalpaul
    ethicalpaul Posts: 9,076

    The larger the header, the less condensate you'll have, because velocity is reduced.

    I don’t follow this at all but regardless the size minimum on the EQ has nothing to do with condensate—we’re talking teaspoons.

    It’s about carryover

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • ChrisJ
    ChrisJ Posts: 17,763

    Some call for 1 1/4, others 1 1/2.

    That looks like an EG-30. So a single 2" riser, 2" header and 1 1/2" equalizer.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Grallert
    Grallert Posts: 1,237

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    We have all been taught, the higher the velocity, the more water gets carried out from the boiler. The lower the velocity, the less water gets carried out of the boiler. If you follow through with that equation, that means that the larger the boiler steam piping and header coming out of the boiler, the less water there will actually be in the header. Which means, the drain function of the equalizer, can be reduced.

    Captain Who
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    Here is the illustration from the manual on the left and I have made your piping arrangement on the right. I do not believe that your main rizer on the right side should be connected the way you did it. Red piping is not a good design.

    Screenshot 2026-02-17 at 9.34.14 AM.jpg

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Captain WhoCLamb
  • SMH. We need a sticky to tell people to give a few different view angles when submitting a photo. I didn't realize that was a Tee. A bullheaded Tee is a disaster in steam piping, when the steam flows in the other direction that it does here because it generates wet steam. In this case it is almost like another equalizer would be needed because you don't want the end of the header to be an elbow up into the main.

    CLamb
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    This might be a better design

    Screenshot 2026-02-17 at 9.34.14 AM.jpg

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Captain Who
  • ChrisJ
    ChrisJ Posts: 17,763

    I'd use the other tapping and plug the one that's currently being used.

    I'd also extend that left main over quite a bit so my equalizer is straight.

    Screenshot 2026-02-17 105154.png

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Captain Who
    Captain Who Posts: 883
    edited February 17

    @ChrisJ But that could get him in trouble with Weil McLain regarding warranty because the manual specifies that "Steam supply must be on the same end as controls"

    @jmerrill Make sure your equalizer is 1-1/2" min. because that is what is specified in the manual.

  • ChrisJ
    ChrisJ Posts: 17,763

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946

    @jmerrill could always go overboard like Paul did and use a double riser from the boiler into a drop header the there sill be plenty of room to put the two main risers into the header. Wouldn't that look nice?

    Screenshot 2026-02-17 at 11.29.48 AM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Posts: 18,399

    i'm not sure if that is a tee or if the tee is to the right of it and the tee happens to have a casting ridge in the bottom of it.

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,946
    edited February 17

    It is a Tee

    here is what I see behind that 3" header coming off of the riser.

    Screenshot 2026-02-17 at 12.40.58 PM.jpg

    What I see coming off of the 3" riser is from left to right: Yellow arrow is pointing to a 3" TEE < 3" pipe nipple < 3" coupling < 3" pipe nipple < 3" 90° elbow ^ 3" riser out of the boiler. The Tee in the header puts the steam in two directions ← → to get to to the different main risers. Not a good design!

    Here is the same photo with the hidden pipe covered by the header:

    Screenshot 2026-02-17 at 1.54.19 PM.png

    Untitled Image

    Without

    Screenshot 2026-02-17 at 1.54.19 PM.png

    With

    Untitled Image

    Without

    Untitled Image

    With

    Untitled Image

    Without

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • ethicalpaul
    ethicalpaul Posts: 9,076

    ahh thanks. Well that wouldn’t be condensate, that would be boiler water.

    And despite ridiculous attempts, I can’t get water to get carried out of my boiler due to piping problems—only due to water problems.

    A large header does not affect the velocity from the boiler through the supply but anyway thanks again for explaining what he was trying to say

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • STEAM DOCTOR
    STEAM DOCTOR Posts: 2,680

    My experience, is that residential steam boiler warranties are absolutely worthless. Have yet to see one be honored.

    ethicalpaulclammy
  • tcassano87
    tcassano87 Posts: 164
    IMG_1603.jpeg

    just my 2 cents, not sure if you have the space on that run for 2 tees but would look much cleaner. & can me please cover and protect the top of the boiler, it’s not a work bench lol

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Why scare the OP off? 100 people look at this and you get 100 ways to pipe it. Its done. Is it textbook? No will it work? Yes.

    mattmia2ethicalpaul
  • mattmia2
    mattmia2 Posts: 18,399

    if everything lines up just the wrong way and the tee is indeed in the corner that could cause some problems but it probably will be fine.

  • @jmerrill If you pitch the header downward towards the equalizer at 1" per 10 ft., then the section to the right of the Tee that feeds the main on the right will work as a counterflow header and the condensate will flow back wards towards the equalizer.

  • ethicalpaul
    ethicalpaul Posts: 9,076

    From my videos you can see that the amount of condensate in the header is minuscule—even uninsulated ones.

    And a lot of it gets re-evaporated by steam going by.

    Pitch on the header gets you nothing.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    Captain Who
  • Mucking the guy's thread up but try making this work without pitch

    chrome_2026-02-18_07-54-09.jpg
  • ethicalpaul
    ethicalpaul Posts: 9,076

    You were talking about the header, not the main.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    GGrossmattmia2
  • Captain Who
    Captain Who Posts: 883
    edited February 18

    Steam and Condensate don't give a rat's a whether they are in a pipe that humans call a header or a main. The diagram from peerless depicts the concept of proper pitch needed when steam and condensate flow in opposite directions, as will be the case in that stub extension of the OPs header (if he pitches it correctly), to the right of the Tee. Don't know how to explain it any more than that, except to say that anything he can do to keep condensate from being blown up into that main on the right will be a benefit. Basics matter most when things go wrong……

    PS (lol): Peerless says in the diagram "maximum header length 100 ft."

  • ChrisJ
    ChrisJ Posts: 17,763

    This is exhausting,.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Grallertmattmia2
  • Refuting the basics of steam piping knowledge passed down by the Dead Men certainly is…….