I plan on replacing my 97 year old furnace with a Weil-McLain AquaBalance Heat-Only Wall Mount Gas Boiler. My option is 65,000 97000 or a125000 BTU unit. After a quick calculation I should need a 93000 BTU unit. Just how close do I have to be to the 93000 for thing to work right?
383-100-045 - Weil-McLain 383-100-045 - AB-120H AquaBalance Heat-Only Wall Mount Gas Boiler, 97,000 BTU (NG)
    Is 93,000 btu/hr the heat loss of the house that you calculated? Since it is a modulating boiler it can fire at a lower rate much of the time. I would go with the 97,000 btu/hr output model though the actual output may be a little less depending on what type of emitters you have and how well they deal with low temp water. Are you heating DHW with it or just space heating?
  • scatgo
    scatgo Posts: 102
    Just space heating with cast iron radiators.
    hot_rod Posts: 28,706
    A 97,000 input will be around an 84,000 output, derate for efficiency.
    If you trust the load calc, go with the 125, it will turndown about the same.
    it is 97,000 output, but that is in a lab test. how close it comes to that will depend on how cool you can run the ci radiators and get the design output. if the house is 2 story that calculator is way off because it will be guessing about 2x the roof area you actually have.
    That is a pretty simplistic load calculator. I would run another load calc to tighten up that number.
    What size is the existing boiler?
  • GGross
    GGross Posts: 2,104
    that calculator gives me a load of 103,554 BTU/hr. My boiler is an 85k mod/con and when I checked up on it this past winter when it was -15f outside it satisfied a call for heat in less than 10 minutes. That calculator is pretty far off, that being said a 125k with a 10:1 turndown is going to be fine, I just don't think your actual load is anywhere near what SH suggests.
    mattmia2ethicalpaul
    EdTheHeaterMan Posts: 12,948
    This question is better asked in private with your significant other.
    As far as the boiler size is concerned…
    If you do the load calculation based on I=B=R form 1504WH or ACCA Manual J, you will find a much lower requirement. I have a feeling that you will be able to use the WM AB-80H with a 65,000 NET output, and have the most efficient setup. If you don't want to go to the trouble of an actual Load Calculation for your home where you measure the actual amount of doors, walls, windows, ceilings and floors, then you will be guessing that you have something less that 97,000 NET and I would choose the WM AB-120 with the 97,000
    NET output. Either way, the boiler will only use the amount of BTUs required to heat the home and rarely fire more than actual load requirements. Where you will waste fuel is at the low end when you only need 6000, BTU on a spring evening and the turndown ratio only goes to 9700 BTU so the boiler will cycle on and off to provide the lower BTU requirement.
    scatgo
  • I recommend the process detailed in this article for sizing based on actual fuel usage:
    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
  • I need to tread lightly here. Some of my comments have been removed in the past and I don't want to get banned. I think I did this one properly.
    old_diy_guy
  • GGross
    GGross Posts: 2,104
    Need to start a mailing list for your spicy jokes. 'Ed Young: Too Hot For The Wall"
    EdTheHeaterManmattmia2
  • ZackR
    ZackR Posts: 30
    That is what I did and was able to size down my boiler and save approx. 8% on my gas usage. 2 heating seasons so far and no problems keeping things warm in the winter.
  • The Steam Whisperer
    The Steam Whisperer Posts: 1,328
    I've used a method like this for decades and it works quite well. However, some of thier assumptions are quite off.
    Heat loss of a structure is not close to linear. Heat movement through most materials is nearly linear at typical design temperatures. However, air leakage rates increase nonlinearly, so heat loss accelerates as it gets colder. The old ASHRAE charts show the design air leakage rate of a medium "tight" construction as 0.6 air changes per hour when its 50F outdoors. At 0F , the number of air changes per hour increases to 1.1, nearly double the air leakage and at big delta T for that same structure If you have a leaky building, this can really increase heat load dramatically.
    Also, the other big error is the efficiency of equipment. A typical 80% gas efficiency atmospheric boiler without a damper that is 3 times oversized is running about 62% efficiency on a typical winter day ( which is about 1/2 of design load). A 3 times power burner boiler boiler tends to fare much better at about 68% efficiency.
    This is why I really like running staged boiler heating plants in larger buildings Sized and controlled properly, you can take the typical day 62% or 68% efficiency and bump that up to 80% to 85% with a properly sized heating plant with two smaller boilers. On the buildings I've done this, fuel usage reduction typically runs from about 20% to 60% and you still have very simple long lived equipment that is inexpensive to repair.
  • ratio
    ratio Posts: 4,344
    @The Steam Whisperer, I'm curious about the staging. Do you often (or ever) do more than two stages? Asymmetrical stages (like 1/3 & 2/3)? Pressure control vs temperature vs time?
  • I typically do 2 stages, unless I'm trying to stick with residential pre assembled boilers on larger loads. I have used asymmetrical stages, especially in unusual load situations like church structures that are in setback must of the time and only are heating a small space. For control on Hot water systems, I've used Tekmar for staging controls and reset, but its been quite awhile since I've done these. For steam, I use two stage thermostats quite often with orificed two pipe systems. On some steam systems you need both boilers to prime the system and then you can drop to one boiler. An aquastat at the end of the slow to heat main usually can take care of that. R&D controls makes a 2 stage steam control that will drop out the 2nd stage after the temp rises to about 60% of the differential. I probably will be trying one of these soon.
  • scatgo
    scatgo Posts: 102
    edited November 2025
    How dose this look for a more accurate information? What would be the width? Each room?
    Heat Loss Calculator | U.S. Boiler Company
    This particular U.S Boiler calc is looking at the home as a whole, measure outside walls, windows, doors. Follow the Procedure paragraph
    A more detailed load calc would be room by room. So use the same input data sheet and use the room dimension. A 10X 10' bedroom 8' tall for example.
    Screenshot 2025-11-28 at 8.17.49 AM.png Screenshot 2025-11-28 at 8.17.07 AM.png
  • The part I don't like about that is "select proper air change factor." In the end, you're just guessing. You could do a blower door test and actually measure the leakage.
  • In a house with significant solar gain this method will underestimate the design load.
  • MikeL_2
    MikeL_2 Posts: 561
    It's an interesting question. Design conditions may only occur for a few days or weeks a year. And many boilers, especially cast iron units, are oversized most of the heating season.
    At my house we're tolerant of 60° f indoors during design conditions so a boiler that's undersized for a few weeks a year is fine......
    Infiltration is always a guess and always was a guess without a blower door test.
    Hot water boilers have a built in 15% piping and pick up factor and steam is 33%. So if the boiler selected is the "perfect size" you would still have some extra capacity.
  • scatgo
    scatgo Posts: 102
    Can some one explain the math they want on windows? ft2? one window measures 41x51 inches. Just round off to feet? like 4ftx4ft
  • scatgo
    scatgo Posts: 102
    One problem. It just hit me. Going room by room will make all walls insulated. Including inside walls.
    pecmsg Posts: 7,634
    interior walls Insulated or not does not change the rooms load / loss.
    Intplm.hot_rod
  • psb75
    psb75 Posts: 1,181
    An overview of getting a "heat loss" number: You are expected to calculate the total cubic volume of the heated space of the dwelling, surrounded by the total insulated envelope of the walls, ceiling and floor. Calculate the entire area of windows and doors as a factor that detracts from the aforementioned. The air-change number is also important as a factor that measures the quality of "how well" all of the materials were "put together" (and any degradation of that). When you get The Number, imagine then…yourself in the house on the coldest day of the year in your region…on a windy day. IF your number falls between 65K and 97k , say its 75K…go with the 97K boiler model.
  • Intplm.
    Intplm. Posts: 3,162
    It depends on your mood. Do you want it cold, too hot, or as comfortable as possible? Hmm. I would hazard a guess that you want it as comfortable as possible. Crunching the numbers with more than one heat loss program is a good idea.
    Years ago, I had to do heat loss calculations by hand. ( Ok, I used a calculator too, I'm not that old.)
    Does anyone know where those calculation formulas can be found? Does Slant Fin still have theirs out there? Is there a calc? That can be reliably used?
    Here is another option, in an Excel sheet format, try several of the options offered on this thread to you find the one that works best for you.
    They are all based on a Manual J formula, some allow you to enter more details and get a more accurate number.
    The infiltration will be a guess unless you have a blower door test done. But easy enough with a spreadsheet to change ACH and see how it changes your load number.
    pecmsg Posts: 7,634
    Blower door tests are in the $250 - $500 range.
    Well worth the expense.
  • Of course even with a blower door test you're still guessing what the infiltration will be on a cold day, it's just a more informed guess.
    pecmsg Posts: 7,634
    it gives a starting point
  • neilc
    neilc Posts: 3,213
    how does infiltration change? cold day to hot day?
    known to beat dead horses
    I think some of the load calc programs allow you to enter wind speed. That could change the load numbers based on infiltration around doors and widows.
    Not many heat load programs take into account internal gains, passive solar gains either. So the load number is a best guess
    The maximum (heat loss) for a building will occur when it is unoccupied. Lighting, refrigeration, people add heat to the space which is not used as a credit to the heat loss.
    With air-conditioning these gains are considered in a heat gain calculation.
  • The temperature difference between the inside and the outside creates a pressure differential which drives infiltration. The greater the temperature difference the greater the infiltration.