I have a customer who had water sprayed on his boiler. Two of his taco control boards had water condensation inside the "ice cube relays" as can be seen from the pictures taken about a month ago. he let it dry a month and asked me to inspect. There is no more condensation and completely dry.. I tried all the zones and all respond properly. one of the boards shows some physical water damage to the board, but all functions properly.
Would you make him replace it or see if eventually starts to malfunction. do you think its a fire hazard.
(ps. There is another board that fried from the water which im replacing because its clearly not functioning properly)
Thanks
Joe
    109A_5 Member Posts: 3,691
    Since the best practice to 'Save' the water contaminated / damaged equipment was not implemented at the time when the damage happened, I would recommend that it should be replaced.
    Simply just letting it dry out is (was) not a good plan.
    The present problem is where is the corrosion hiding and what issues will it cause in the future ?
    It certainly could be cleaned up and the relays replaced (if needed), but it is probably not worth the cost (Vs. replacement) to have it professionally repaired. If the homeowner wants to assume the liability, get it in writing.
    EdTheHeaterManMad Dog_2
  • Joseph_4
    what IS the proper practice to save water contaminated equipment. Id like to know for the future if it occurs on my watch.
    thanks
    Joe
    CLamb
  • Intplm.
    Intplm. Member Posts: 2,910
    Usually, what I would do is wait and see. It's hard to gauge what is wrong until something shows that it is wrong/performing or not.
    Your pictures show a lot of water in and on the controls. You will have to decide what the best action to take is on a case-by-case basis.
  • GGross
    GGross Member Posts: 1,777
    I would try the same recommendation people give when a phone falls in the water. Do not power it on, bury it in rice for a day or 2. If there are covers, batteries, fuses anything reasonably meant to be removed from the device detach it and put it separately in the rice.
    hot_rod Member Posts: 27,082
    ask the relay manufacturer what they recommend.
    Prices are going up, replace them now.
    Did water run in the flex also? Into the wire nuts? Fresh water? Boiler water? Sea water?
    Mad Dog_2
    Jamie Hall Member Posts: 27,013
    Those relays will fail — the question is, when? If the equipment is properly fused and safetied, I doubt that there is a fire hazard, but check and make sure that the controlled equipment is properly safetied, as one of the failure modes is to lock something on which shouldn't be.
    Me, I'd replace the stuff.
    The rice trick is one what to handle electronics which have gotten wet. Another is freeze drying. Niether will help much if the water was salty or otherwise grundgy, not if the exposure was more than just a dunking.
    GGross
  • Joseph_4
    @Hvac Nut.. I appreciate the advice.. so Id have them sign a release with warnings on their accepting liabilty stating the possible risks. I told them i will send question here to help them decide for themselves based on what trade professionals across the country advise. They will read everyone's response to be better informed
    Thanks
    Joe
    EdTheHeaterMan Member Posts: 11,755
    edited May 2025
    How long ago was the water damage event?
    It may be too late but Water Damage from a leak is covered by homeowners insurance policy. Usually not the actual leak, but all the damage caused by the leak. With the cost of labor and the prices of electronics that you are already replacing and the suspected electrical controls, along with perhaps some other controls that operate the burner, like ignition equipment, there will be a pretty substantial claim. Should be well over a $500 or $1000 deductable.
    Replace all that you can in one large invoice and tell the customer to file a claim.
    If you are the last one there and something overheats and starts a fire, you may be filing a claim with your insurance company in the future. For a lot more!!!
    If you recommend replacing all the controls and wiring, and the customer declines the repair, then get a signature that the repairs are declined.  Keep the signed paper on file for your protection.  And Photographs are always good to keep on file.
    There are several Taco support staff that are on this forum and if they looked at those pictures they would cringe. Perhaps we can get the official response from @SteveSan or @Dave H_2 from Taco Tech Support
    SteveSanMad Dog_2
    pecmsg Member Posts: 6,894
    I wouldn’t accept the liability.
    Mad Dog_2
  • SteveSan
    SteveSan Member Posts: 295
    Water damage to electrical controls can lead to corrosion, short circuits, and electrical failures, posing safety hazards and reducing functionality. Water is a conductor of electricity, and its presence in electronic devices can create unintended electrical connections and damage components, especially if the device is powered on during contact.
    As others have suggested, I would replace any components with said water damage.
    EdTheHeaterManSTEAM DOCTORMad Dog_2
  • Intplm.
    Oh!? If it's a customer, I would change, swap things out. Who needs the headache of the maybe it will fail maybe it won't scenario? So, "When in doubt, change it out !"
    mattmia2 Member Posts: 16,036
    as mentioned above, i'd be more concerned with water that got in the 120v wiring than the board. the board itself is unlikely to be a hazard, the relays are likely to have problems. Since it isn't a safety control if it gets stuck you either get no heat or a heat call that won't end. If it were a primary control or gas ignition control or valve or part of the safety chain i would say you have to replace it.
    I wouldn't be super concerned about the mineral stains around the diodes for the relays, you can wipe it off, it isn't going to conduct unless it gets wet again. I would probably replace the relays if I can find an inexpensive source, otherwise I'd replace the whole control. I think the relays with the line voltage are the only place something might burn up as it fails. Electronic components are designed to be washed as part of the assembly process but those relays clearly got more than that.
    The way to try to salvage electronics that got wet is to rinse them out with fresh or ideally deionized or distilled water then let them dry completely, usually a few weeks, before energizing them. Even then it can sometimes go wrong.
    Long Beach EdSteveSanMad Dog_2
  • yellowdog
    yellowdog Member Posts: 287
    Electric code requires any electrical component that gets wet to be replaced, even romex wire. You are taking a risk that I would not.
    Intplm.Mad Dog_2
  • Joseph_4
    Thanks for the wealth of quality info
    I apppreciate everyones feedback. will print out and show to customer
    Joseph
    SteveSan
    Steamhead Member Posts: 18,324
    Here is one manufacturer's take on boilers and other components that got wet:
    Consulting
    Mad Dog_2JohnNY
    being immersed in water is quite different than a zone control being sprayed with fresh water.
    Intplm.CLamb
    Easy enough to look that up, abd in this case a manufacturer said to replace
    Mad Dog_2PC7060
  • yellowdog
    @mattmia2 get ahold of an electrical inspector and get his opinion. we have an electrical department and we deal with flooded houses. any electrical component that gets wet including wire, has to be replaced.
    Mad Dog_2
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,469
    As tempting as it is to "wait and see," recommend replacement of them. Unless you are a Licensed Electrician or a P.E. Electrical Engineer, you're getting yourself caught up in the red tape of potential litigation IF there's ever a fire. Mad Dog
  • PC7060
    PC7060 Member Posts: 1,762
    The liability risk extends to the engineer as well with expectation they can develop remediation plan in colaboration with OEM. Typical documentation includes details inspection / remediation steps taken to bring equipment back to OEM standard.
  • Mad Dog_2
    Of course, but they are actually qualified & licensed to take on that calculated risk...most of us, myself included, aren't. Mad Dog
    I think the OEM instructions and written opinion trumps all others. I doubt legally an engineer not employed and under the manufacturer’s insurance umbrella can override the manufacturers recommendation or liability.
    In this case the manufacturer is on record with the requirement.
    Unless the control was housed in a NEMA enclosure intended for under water, or wet locations and approved by UL, NEMA, et al, Allowing or putting that control in service is an expensive, maybe risky liability decision for all involved.
    Hopefully the licensed, insured pros on this list understand their due diligence🧐