finding a leak in a mini-split

have a mini split with small leak
havent been able to pinpoint
any tricks of the trade?
what is best electronic detector out there?
Comments
-
Isolate the linesets. Its probably somewhere in the middle of one.
0 -
-
Pressure test with high nitrogen pressure, 500-600 PSI and spray all lineset connections with with leak detector soap. If you happen to have the lineset with the white insulation it could be anywhere in between the indoor and outdoor units. Those linesets are notorious for leaks in the copper due to formicary corrosion. I usually add a little refrigerant in with the nitrogen so I use it as a trace gas for finding the leak with my electronic leak detector. I like to use the Infinicon D-Tek Stratus. I would never use any of the stop leak products that can be added with refrigerant, they do more harm than good. I only use dye as a last resort.
0 -
NEVER use dye in a mini split.
The dye isn't actually a liquid, it's finely powered fluorescent minerals. What happens is it settles out. I had a Mitsubishi that someone put dye in. I took the compressor out, dumped the oil, rinsed the compressor with denatured alcohol several times, & was still getting small flakes out. It was a total loss, we ended up replacing the outdoor and indoor units.
2 -
-
Have any of you ever experienced this? I had a leak in my self-installed mini split. I bought a sniffer and it detected a leak at one of the 2nd floor heads. I got a replacement under warranty after sending a video of the leak detector going off near the fins of the head unit.
I replaced it but the leak persisted.
I dug deeper and found it for real at a place where I had spliced the line set (I would not do that today).
I think the refrigerant migrated up the lineset insulation all the way to the head where the sniffer detected it. I have always felt guilty about that warranty replacement that probably was my fault.
Also, I swear I could smell it in the room when lying quietly, but it was VERY subtle
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
yeah if there is a leak in the lineset run and the leaky area is well covered by the insulation there is a pretty good chance the refrigerant will go out the end of the lineset insulation. I assume you had your splice pretty well taped and insulated and that's why you didn't check that first? Or put the sniffer near the splice but it wasn't showing up through the insulation?
1 -
yep is was buried in a line set run guard thing on the exterior wall but at least it was near the ground. Definitely a case of looking for my keys where the light is stronger
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
IDK if you were referring to my post re dye, but Mitsubishi will not warrant a unit that has dye in it. Perhaps other mfgrs allow it, I may have been too general.
I've seen dye work fine (well, messy as h#!!) in regular splits and automotive applications. IDK what it is about Mitsubishis, perhaps the metric oil (AB or something , I forget) is the cause, but it was something to see. It'll piss me off something fierce to get it in my manifold, though.
0 -
Copeland
Mitsubishi
Tecumseh
Reserve the right to refuse the warranty!
If overfilled with dye yes they will deny warranty!
I don’t believe any have tested the waters legally.
0 -
-
I would say six or seven out of 10 hvac contractors are more than thrilled to install a system, but when a problem pops up down the road they’re gone. I’m speaking in very general terms.
Leaks are a pain, and searching for them can be anywhere from pretty easy to extremely difficult. The more zones, the bigger the pain.Good luck I hope you get it all resolved
0 -
those #’s are conservative!
0 -
What will “Go out of balance”?
0 -
the wheatstone bridge in the refrigerant detector.
like it is alarming because i smacked it on the firewall next to the evaporator connection, not because it encountered refrigerant
0 -
my D-Tek does the same!
0 -
mine is a very old d-tek that i bought off ebay a decade or so ago.
0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 966 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements